Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

I/NET physical layer issues

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/NET physical layer issues
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2065 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/NET physical layer issues

Picard Product_Support
‎2018-09-07 02:09 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:09 AM

Issue

I/NET Physical Layer Issues, Lan Reconfigure, and/or Controllers going on or offline 1 at a time.

Product Line

TAC INET

Environment

I/NET

Cause

Physical Layer Issue

Resolution

Some or all of the following may indicate a physical layer issue.

  1. Abnormally large number of Lan Reconfigure messages
  2. Controllers going offline individually or in groups and sometimes all together
  3. Large numbers of Station Lost/Restore Messages
  4. Frequent problems connecting to controllers and data interruption

To Troubleshoot a suspected Physical Layer error:

  1. Determine if this is a Controller LAN layer issue by direct connection to the Controller LAN using a tap.  If you continue to experience the same errors, as while connected via TCP/IP then the issue is on the Controller LAN
  2. Verify that you are using the correct wire gage (22 or 24) and that you controller LAN is less than 4000 feet for 24 AWG and less than 5000 feet for 22 AWG.
  3. Verify shield drain wire. Shield drain wire continuity must be maintained as the LAN cable passes through each controller. Shield drain wires from each controller LAN cable must be twisted together, insulated, and tied back such that wires do not come in contact with ground or any conductive surface within a controller. Shield drain wire must be directly connected to Electrical Service Earth Ground at only one end of the cable.
  4. The issue at this point can either be a wiring fault or a controller that is broken.
  5. Disconnect all controllers from the controller LAN by removing the LAN terminal strip from each controller
  6. Reconnect each controller one at a time and watch for the original errors. During this process a LAN Reconfigure is expected each time a device comes online
  7. While at each controller watch for any frayed wire, unusual/unneeded splices and if needed re-seat each wire into the terminal block
  8. When a controller is brought online and the error returns, examine that leg of the LAN wire for shorts or replace that section of wire
  9. Replace the suspect controller with a different device to ensure that the controller is not the source of the problem. (On critical systems you can plug in a spare controller at the location for testing without taking the existing controller offline) Typically if a controller is causing the error it will display alarms or LAN reconfigure on it's LEDs. Consult the TCON for the specific controller for more details (TCON Cross Reference available in TCON Number and Title Cross Reference (with links)).
  10. If it is not feasible to replace long sections of wire, or if it is determine that the controller LAN exceeds the specified length, then you may want to consider using Distributed Link Architecture.
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 4899
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore