Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,856
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • ESMI Fire Detection 13
  • EcoStruxure Building Advisor 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Helpfulness
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 21
    • 22
    • 23
    • …
    • 509
  • Next »

How to latch an output with one input and unlatch with another input.

Issue If one Input is required to activate an Output and another Input to de-activate the Output, this Output can be defined by Input Types. The below is a simple scenario where when the first Input turns ON the Control Output turns ON, when the second Input turns ON the Control Output turns OFF. In this scenario we are activating a Duress alarm when an Input goes on and resetting that Alarm when the reset Input is triggered. Product Line Security Expert Environment Security Expert SP-C Cause Require detailed instructions on how to program a latching duress alarm scenario. Resolution Objects required:   1x Area - "Duress_Area" 2x Input Types - "Duress Enable", "Duress Reset" 2x Inputs - "VI Duress Trigger", "VI Duress Reset" 1x Output - "VO Duress Alarm"   Note: The above object names are what is used in this example, you can set these to whatever you require.     Instructions:   Creating the Area 1. Navigate to Programming > Areas. Add a new area (Duress Area), set the Entry and Exit Delay Times to 0. All other settings can be left default.   Creating the Input Types 1. Navigate to Programming > Input Types. Create a new Input Type (Duress Enable) 2. Set the Control Output to your Output (VO Duress Alarm). 3. Under Options 1 enable Generate Alarms. 4. Under Options 2 enable Activate Control Output on Alarm . 5. Set any other options that may be required. 6. Create a new Input Type (Duress Reset) and redo steps 2 - 5 above except under Options 2 enable Deactivate Control Output On Alarm.   Configuring the Inputs 1. Navigate to Programming > Inputs select the Input (VI Duress Trigger) and set the following: 2. Set the Area to the Dummy Area (Duress_Area) created earlier. 3. Set the Input Type to the Input Type (Duress Enable). 4. select the Input (VI Duress Reset) and set the following: 5. Set the Area to the Dummy Area (Duress_Area) created earlier. 6. Set the Input Type to the Input Type (Duress Reset).   Testing 1. Arm both portions of the Area 2. Activate the Input (VI Duress Trigger) to confirm Alarm is generated and Output Activates. 3. Activate the Input (VI Duress Reset) to confirm Alarm is generated and Output Deactivates. 
View full article
Picard Product_Support
‎2018-09-10 07:20 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:38 PM

Labels:
  • EcoStruxure Security Expert
2901 Views

Backup and Restore MongoDB for Windows for Access Expert On-Premise

Issue Access Expert On-Premise setup needs procedures and tools to backup and restore the database Product Line Access Expert Environment Access Expert Premise Software V3 MongoDB Cause The procedures for backing up and restoring the MongoDB is documented online at the link below. https://docs.mongodb.com/manual/tutorial/backup-and-restore-tools/ However, these instructions do not outline how to use the commands (mongodump and mongorestore) within the Windows OS environment using specific examples. Resolution The following procedures are designed to fill in the gap for Access Expert administrators who need to do manual MongoDB Backup and Restore. These procedures assume that Access Expert V3 has been installed and is functioning normally. You will need 2 separate Command Prompts, run as Administrator, open for these procedures. Mongo DOS Shell to attach to and run commands within MongoDB environment Standard DOS Shell to run the Mongo backup and restore commands MongoDB Backup Ensure MongoDB service is running (Start> Run> services.msc) Open a Command Prompt as Administrator (referred to as the Mongo DOS Shell) Type mongo(command) Type show dbs (command) - shown above, to give a list of the dbs available) If the MongoDB service is "Running," but the client cannot connect when typing mongo, it's probably because the path to the mongo bin folder hasn't been added to the PC's environment. To Add a local path locations variable to a PC environment https://docs.microsoft.com/en-us/previous-versions/office/developer/sharepoint-2010/ee537574(v%3Doffice.14) Ex. C:\Program Files\MongoDB\Server\3.6\bin (This will vary based on the version of Mongo) Open another Command Prompt as Administrator (Standard DOS Shell) Use the CD command to navigate to where you would like the backup files to be created Ex. C:\Data mongodump (command) The mongodump command creates the dump folder with admin, Keep, Signalr subfolders MongoDB Restore In the (Mongo DOS Shell) Prompt show dbs (command) use Keep (command) (Case sensitive) db.dropDatabase() (command) Use the Command Prompt as Administrator (Standard DOS Shell) mongorestore (command) The window should indicate "Finished Restoring Keep.Events," "done" and RESTORE COMPLETE If there are “E11000 duplicate key error collection” Keep.Events errors, it’s because the collection events are already in the folder and need to be deleted first.   Steps to correct the E11000 duplicate issue: (Stop the service, delete and recreate the DB folder, restart service) Right-click on the MongoDB service and Stop (you can’t delete files while the service is running) Delete C:\Data\db folder (not the Data, only DB) MANUALLY CREATE THE DB FOLDER - Right Click > New Folder and name it DB Restart the MongoDB service - this creates the necessary files in the DB folder Once these steps have been done, rerun the mongorestore command mongorestore (command) Verify that users can log into Access Expert with this database
View full article
Picard Product_Support
‎2018-09-10 07:56 AM

Last Updated: Administrator DavidFisher Administrator ‎2023-09-11 01:50 AM

Labels:
  • EcoStruxure Access Expert
4416 Views

Is there an I/A Series BACnet IP to BACnet MS/TP converter?

Issue Wants to be able to access a remotely located group of BACnet MS/TP controllers via BACnet IP or BACnet-Ethernet.  Do you sell any routers or converters of this type? Environment MNB series BACnet controllers using MS/TP communications. Cause Customer wants to use BACnetIP to connect to a group of BACnet MS/TP controllers. Resolution The UNC-520-2 or ENC-520-2, with the BACnet driver installed, can operate as a BACnet IP to BACnet MS/TP router.  These devices allow routing between BACnet-IP or BACnet Ethernet to BACnet MS/TP.  This approach allows for up to four separate MS/TP networks to be routed to the BACnet-IP or BACnet-Ethernet network. The MNB-1000 provides a single MS/TP bus along with the BACnet IP or BACnet Ethernet capability. We have not tested and cannot support any third party BACnetIP to BACnet MS/TP converters.
View full article
Picard Product_Support
‎2018-09-06 12:55 PM

Labels:
  • TAC IA Series
1973 Views

How to setup a Mantrap

Issue How to set up a Mantrap Product Line TAC INET Environment I/NET Access Control Site Interlocked Doors Person Trap Anti-Passback (APB) Cause What is a mantrap? A mantrap is a security device that monitors and controls two or more interlocking doors to a small room that separates a non-secured area from a secured area. These interlocking doors allow only one door to be open at any time. What are interlocking doors? “Interlocking doors” is a security term used to describe how two or more doors are interfaced with each other and locked. Doors that are interlocked cannot be opened at the same time. Either door can be unlocked and opened as long as the other door is locked and closed and no other alarm condition exists. What types of locations require a mantrap? Mantraps are used at high-value or critical security areas where only authorized persons are allowed to enter. Typical areas include sensitive data processing areas, cash handling areas, critical research labs, security control rooms, and automated airline passenger entry portals. Why would my company consider a mantrap? Typically, security personnel are posted in high-security locations to control access into the area. An automatic mantrap used in this same location would control the access to the area, allowing security personnel resources to be available for other tasks. What is the difference between a mantrap and an interlocking door control system? Regarding controlling two doors within a vestibule, “mantrap” and “interlocking door controller” can be used interchangeably. Once the number of doors controlled by a single controller exceeds two, then the term interlocking door controller should be used. Resolution I/NET has three ways to do a mantrap: Event sequences and calculations -- limit to 5-7 SCUs per 7798C due to system loading Use a "standalone" third-party device that is wired to the door and is not attached to I/NET at all Use the interlock wiring diagram that uses relay logic to function. This is also part of the I/NET System. I/NET Seven allows configuring a door to have both an entry and an exit reader and uses the selection of Anti-pass back/Anti-tailgate to set up Zones or areas with stricter control over access. However, even with the Anti-pass back option set to Hard, which denies access to successive reads at the same reader, it does not prevent multiple persons from entering and exiting together, and it does not provide real-time accounting for the number of people in a Zone. Besides having a guard at the door, the usual method of implementing Zones does not prevent violations.   The example below presents some thoughts about improving the Zone's security in an I/NET Seven system. There needs to be a way to restrict the number of people gaining access to the door. There needs to be a way to keep up with how many people are in the Zone. One method to accomplish the first goal is to use a two-door egress system, as is often used in jails and similar security setups. For a medium security setup where the intent is not to prevent people from leaving, only one door needs a card reader. Such a design is illustrated below: Notes: Electric strike normally energized. Low walls or fences. The area should be small enough to limit how many people or things are in it at one time. Gate with normally de-energized bolt. The gate could swing both ways, so one would only have to push it to open it. It should have a spring to close it. The door “a” would have both an Entry and Exit reader, so an Anti-pass back/Anti-tailgate can be implemented. The strike on the door “a” would normally be energized and opened by a valid reader transaction.   The bolt on the gate would be normally de-energized, allowing the gate to open freely. When the strike on the door “a” is de-energized, the bolt on the gate would be energized, preventing the gate from opening. This is designed to allow only one person to simultaneously move into or out of the Zone.   An added level of security would be accomplished by mounting IR emitter/receiver pairs along the low wall or fence at regular intervals. A person would interrupt the light at a limited number of receivers, so if more than expected are interrupted, it would violate one person at a time, and necessary action could be taken.   If material needed to be moved through the door, the gated area could be made large enough to allow for a dolly or whatever might be needed. A different access level would be provided to those who are moving material, thus preventing the alarm for too many people going through the door.   This approach would restrict movement into and out of the Zone, and the example given in the AIC note could be implemented to allow real-time monitoring of occupancy levels in the Zone.   Design thoughts:   To calculate whether more than one person is in the gated area, sum the number of receivers that are detecting and compare it to a minimum, e.g., four of six must be detecting if only one person is in the area. If material is in the gated area, generate an alarm if an authorized card is not read. Use the alarm delay for the point to give an individual time to make a card read before sounding the alarm. The AIC scheme described in the AIC note would have to be duplicated for the material mover individuals to change the calculation of a person in the gated area. For material movers, the detection would be (sum of detectors < minimum), whereas for regular individuals, the detection would be (sum of detectors > minimum). Remember, the SLI connected to this door can have only 64 AIC’s and this door now has used 2 of them. Use an inter-card delay long enough to let the person exit the gated area before another card can be read. For personnel safety, there must be a way to de-energize the strike. One method would be to mount an emergency exit button located far enough away from the door so a single person could not reach it and a second emergency exit button on the outside of the Zone so someone could keep the strike de-energized until everyone is evacuated. Most codes probably require that all strikes be de-energized in case of smoke or similar emergency to provide another fail-safe.   Here is a pdf document which explains the setup using an SCU Click here to download third-party ManTrap information.
View full article
Picard Product_Support
‎2018-09-10 05:08 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:03 AM

Labels:
  • TAC INET
4437 Views

Controlli S300 Actuator

Issue Controlli S300 Actuator Environment Controlli S300 Actuator Cause Controlli S300 Actuator terminal details. Resolution L=Neutral L'=230Vac B=Close signal from thermostat or control device R=230V to thermostat or control device V=Open signal from thermostat or control device To test: Place a wire link between R and B, the valve actuator will close, place a wire link between R and V, the valve actuator will open. If a auxiliary switch kit D22 is fitted, this can be used to signal the boiler/pump to start if the installation was a domestic. For the actuator datasheet click here.
View full article
Picard Product_Support
‎2018-09-10 05:15 AM

Labels:
  • Field Devices
2144 Views

Unable to reload attributes. OMS database is currently unavailable, backing up.

Issue Reload fails during the programs portion with an error message similar to: Unable to reload attributes. OMS database is currently unavailable, backing up. Environment i2 bCX NC2 Cause A flash backup PE program is set to autostart. As soon as that program loads, it will start to perform a flash backup and any PE programs that have not loaded will not load and the reload will terminate. Resolution Make sure any programs set to automatically backup a controller cannot do so until after a reload is complete.
View full article
Picard Product_Support
‎2018-09-06 12:54 PM

Labels:
  • Andover Continuum
1568 Views

Can Continuum operate over a NAT Ethernet connection?

Issue Can a workstation communicate to a controller using Ethernet Network Address Translation (NAT) Product Line Andover Continuum Environment Cyberstation All Ethernet level CX and bCX controllers. Cause Some IT Departments may want to use Network Address Translation to connect between different sections of their network. Resolution Continuum does not support Network Address Translation (NAT) the IP address entered in the Cyberstation database must match the address entered locally in the controller.
View full article
Picard Product_Support
‎2018-09-06 12:53 PM

Labels:
  • Andover Continuum
1484 Views

Can Modbus TCP and Modbus Serial (EIA/TIA-485) be used on an AS together?

Issue Using Modbus TCP and Modbus Serial (EIA/TIA-485) on an AS together? Product Line EcoStruxure Building Operation. Environment AS-P Modbus TPC Modbus Serial Cause Communicating with two third party devices simultaneously. Both are using the Modbus communication protocol. One is Modbus TCP, the other Modbus Serial (EIA/TIA-485). Resolution Modbus TCP and Modbus Serial (EIA/TIA-485) can be used together on an AS-P. This configuration is supported and has been used many times.
View full article
Picard Product_Support
‎2018-09-06 12:53 PM

Last Updated: Administrator CraigEl Administrator ‎2023-03-07 04:56 PM

Labels:
  • EcoStruxure Building Operation
1316 Views

Maximum number of reader expansion modules and doors per controller

Issue Maximum number of expansion modules and doors per controller Product Line EcoStruxure Security Expert Environment SP-C Security Expert Security Expert Controller SP-RDM2 Security Expert Security Expert Door Expansion Module Cause Documentation states that one SP-C supports up to 128 doors but this is dependent on the communications.  Resolution The current recommendation from Product Management is a maximum of 24 to 34 doors per SP-C. This equates to about 10 to 17 reader expansion modules.  
View full article
Picard Product_Support
‎2018-09-06 07:29 AM

Last Updated: Guinan AdamSteele Guinan ‎2025-07-06 10:38 PM

Labels:
  • EcoStruxure Security Expert
2098 Views

Continuum webClient DCOM permissions resetting with a batch file

Issue After the successful installation of Continuum 1.9x, users are receiving a DCOM Permission error when logging on to Continuum webClient. The error is intermittent. Product Line Andover Continuum Environment Microsoft Server 2008 Standard Microsoft Windows 7 Continuum 1.9x and 2.0 Continuum webClient Server Remote Desktop Cause When a remote desktop connection is made on Windows 7 or Windows 2008 Server the console occasionally gets locked. It stays locked until the local session is restored with a logon. Resolution Create a .bat file. **************************************************************************************** @echo off REM Restores session 0 to the "console".  Thus allows local machine REM to return to the service accounts desktop without being locked. REM ------------------------------------------------------ tscon.exe 0 /dest:console @%windir%\System32\tscon.exe 0 /dest:console @%windir%\System32\tscon.exe 1 /dest:console @%windir%\System32\tscon.exe 2 /dest:console **************************************************************************************** Place this file on the desktop of the Continuum webClient Server system. When you disconnect from the remote session run this Bat file. Do not just disconnect. This must be run "As an Administrator." This will disconnect the session and restore the console.
View full article
Picard Product_Support
‎2018-09-06 12:53 PM

Last Updated: Guinan RandyDavis Guinan ‎2022-05-03 10:04 AM

Labels:
  • Andover Continuum
3195 Views

SE 7300 override/&deg;C-&deg;F button choice.

Issue When defining configuration on SE7300 part no, your choice is between "0" (override) and "5" (possibility to change between °C and °F in interface). Environment SE7300 Cause its not possible to have both override and °C/°F feature Resolution When defining the part number, you will have to choose. The override feature is usually the preferred choice in industrial applications, while the °C/°F feature is used for Hotels and similar, where users are given the possibility to change unit of desired temperature.
View full article
Picard Product_Support
‎2018-09-06 12:51 PM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
1867 Views

SBO reports "Failed to connect to server" when carrying out a Sigma data import.

Issue When a Sigma data import is carried out, the following messages are displayed on the SBO ES computer. On the Sigma server computer, the Sigma server service has stopped. Product Line EcoStruxure Building Operation Environment Sigma 4.08 Building Operation Workstation Building Operation Enterprise Server Cause The Sigma database’s longtext file contains unsupported characters. Resolution Option 1: If Sigma longtext is no longer required: On the Sigma computer. 1)      Stop the Sigma server service. 2)      Delete the longtext.rec file from the Sigma Data folder (C:\Sigma\Data\longtext.rec). 3)      Start the Sigma server service. On the SBO computer Carry out the data import again. Option 2: If Sigma longtext is required: On the Sigma server computer. 1)      Start the Sigma server service. Open a Sigma client, either on the Sigma server computer or the SBO ES computer or other. 1)      Log into Sigma’s operator panel 2)      Go to the System Alarm manager 3)      Under the menu “Configure” select Longtext 4)      Open each longtext entry and remove the unsupported characters 5)      Add the longtext message your require. (You may find copies of the original longtext messages you can copy the text from, under “C:\Sigma\Data\Longtext” used by Sigma before the system was upgraded. On the SBO computer 6)      Carry out the data import again.   The data import should now complete.
View full article
Picard Product_Support
‎2018-09-10 07:18 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 07:37 PM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
1922 Views

Sigma - Changing the IP address of, or moving the Sigma server.

Issue What needs to be changed in the Sigma configuration? Environment Sigma IP Address Moving Different network. Cause Are any changes required to the Sigma configuration, when a Sigma server is moved or the IP address is changed? Resolution Changes required when moving the Sigma server PC to another location or re-installing the Sigma server software onto another PC in a different location. Locate the PC in the new area and give it an appropriate IP address. Start the Sigma server and local client. Enter Sigma "System setup" and select "Networks and Devices" Select the zone that the server is in. In the "Networks" option, does the network already exist, if not then create it. In the "Servers" option select the Sigma server and select the correct network and IP Address. In the "Clients" option check that all clients are attached to the correct servers. In "Controller Items / Routesets" confirm that the routesets are correctly matched to the clients. Download the "Node Configuration" to all devices Download the Att.set and the Routeset.rec files to all controllers.
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • Satchwell BAS & Sigma
1977 Views

Reason Code 12 error during Send to Database.

Issue Continuum displays Reason Code 12 error During Send to Database on BACnet/IP device. Environment 3rd party BACnet Continuum BCX4040 BACnet over IP Cause Third party device is not accessible to Continuum following configuration change by vendor. Resolution Restore communication to 3rd party device.
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • Andover Continuum
1151 Views

What is the resolution of our various controllers Inputs and Outputs?

Issue Need to know the smallest change that an Input can measure or that an Output can provide. Environment All Continuum controllers. Cause Need to know for specification compliance or to determine the smallest measurable change in an Input. Resolution Some of our controllers support inputs with a 10 bit resolution and some support 12 bit resolution. As a rule, all 5.115v inputs are 10 bit and all 10v inputs are 12 bit. You can see which resolution each controller supports by viewing the Datasheet for each controller and noting the value of the "Input Resolution" and voltage range of the inputs (normally 0-10VDC). As an example, the b3920 shows an input resolution of 2.5mV on its 0-10VDC inputs. This equates to a 12 bit resolution as shown below.      2 x = 10VDC / 0.0025 VDC      2 x = 4000      x * log(2) = log(4000)      x = log(4000) / log(2)      x = 11.96578 or 12 bit   Further, a b3800 has an input resolution of 10 bits on its 0-5.115VDC inputs.      5VDC / 2 10 = 0.00499V or 5 mV You can find the individual controller Datasheets on Ecobuildings. Navigate to the Download Center and search the controller model number. Then narrow results by Asset Type = 'Specification Sheet'.  Most of the new Datasheets now note both the Input and Output resolutions.
View full article
Picard Product_Support
‎2018-09-10 06:34 AM

Labels:
  • Andover Continuum
1666 Views

Can we integrate 3rd party LON devices

Issue Can we integrate 3rd party LON devices Environment StruxureWare Building Operation AS or Enterprise Server Cause Integrating third part LON devices allows the system to take full advantage of the open protocol. Resolution We currently support 3rd party Lon devices in Version 1.0 and 1.1, but some large devices are too big to be configured in quantities according to specifications. No major change regarding this is scheduled until earliest 1.4. In 1.3 we will change the numbers that we support to configure but this will mainly be runtime improvements. Some devices can only be configured with Lonmaker which is an extra step during the engineering process.
View full article
Picard Product_Support
‎2018-09-06 12:49 PM

Labels:
  • EcoStruxure Building Operation
1467 Views

Difference between valves V211 and V211T

Issue Please define the difference between the V211 and V211T Environment V211 V211T Cause There are 2 different valves with similar characteristics, what differences are there, and why should I choose one or the other? Resolution V211 is equipped with flanged connections, while the V211T has internal threaded connections.
View full article
Picard Product_Support
‎2018-09-06 12:49 PM

Labels:
  • Field Devices
1239 Views

How to replace a Xenta controller in a LNS network

Issue In the event of a hardware failure on a Xenta controller you may need to perform a proper replacement procedure in the TAC Plug-In to install the new device. Product Line TAC Vista Environment Vista Xenta Programmable Controllers Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B Cause Hardware failure in an LNS network Resolution In the event you have a piece of hardware fail on your LNS network you will want to follow the steps below to properly replace the device. Remove the bad controller and Install the new controller in its place Open your LNS network in LonMaker or NL220 Select to open the TAC System Plug-In in your network management tool In the Plug-In, locate the bad controller in the tree under the LNS Network pane and right click Select Replace... (the Replace TAC Xenta Device Wizard will open) Click Next Select the service pin button and press the service pin on the new controller Then click Next In the next window, click Next to update your Vista Database (NOTE: If you receive a warning during this process, see Warning about application file replacing a programmable controller in Vista System Plug-In) Once this process of updating your Vista Database is complete you will see the screen below confirming that the update was completed successfully Close the TAC Vista Load window Return to the Replace TAC Device Wizard and click Finish. This will complete the replacement process for your new device In some rare cases not all I/O modules will come online after this procedure. If this occurs a power cycle of the Xenta 400/300 will solve this issue.
View full article
Picard Product_Support
‎2018-09-10 05:36 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:01 PM

Labels:
  • TAC Vista
2523 Views

Power consumption Forta M400

Issue The data sheet states 2 different power consumptions: Power consumption: average 6 VA Transformer sizing: 30 VA Which one should be used for calculating power supply? Environment Forta Cause There are different figures specified in the documentation for the Forta series actuator. Resolution Average consumption is 6VA, but the peak consumption is 30VA, and this is just before the valve reaches the fully closed position.
View full article
Picard Product_Support
‎2018-09-06 12:48 PM

Labels:
  • Field Devices
1173 Views

Warning about application file replacing a programmable controller in Vista System Plug-In

Issue During step 9 of How to replace a Xenta controller in a LNS network it is possible to receive a warning with the following information: Warning: The device has no application file (MTA file) thus disabling the possibility of a download of application and parameters to the device. Please download via serial port any application file (MTA file) of your choice by using Menta before attempting to download to this device again. Product Line TAC Vista Environment Programmable Controllers 281, 282, 283, 301, 302, 401 & 401:B Cause Attempting to install a Xenta programmable device that does not have a Menta Application loaded into controller. NOTE: A new controller out of the box should have a simple MTA Application already loaded.  However, if you receive the warning above your controller may not have any Menta file and loading any simple Menta file (i.e. one PVR block) will suffice. Resolution You will need to direct connect to the new controller with a RS-232 cable to upload any simple Menta application (i.e. one PVR block) before the Vista System Plug-In will properly communicate and download the new controller.  The System Plug-In will not communicate with an applicationless device.
View full article
Picard Product_Support
‎2018-09-10 05:37 AM

Last Updated: Spock PeterLarsen Spock ‎2023-07-18 10:29 PM

Labels:
  • TAC Vista
1923 Views
  • « Previous
    • 1
    • …
    • 21
    • 22
    • 23
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of