Issue
During step 9 of How to replace a Xenta controller in a LNS network it is possible to receive a warning with the following information:
Warning: The device has no application file (MTA file) thus disabling the
possibility
of a download of application and parameters to the device.
Please download via serial port any application file (MTA file) of your
choice
by using Menta before attempting to download to this device again.
Product Line
TAC Vista
Environment
- Programmable Controllers
- 281, 282, 283, 301, 302, 401 & 401:B
Cause
Attempting to install a Xenta programmable device that does not have a Menta Application loaded into controller.
NOTE: A new controller out of the box should have a simple MTA Application already loaded. However, if you receive the warning above your controller may not have any Menta file and loading any simple Menta file (i.e. one PVR block) will suffice.
Resolution
You will need to direct connect to the new controller with a RS-232 cable to upload any simple Menta application (i.e. one PVR block) before the Vista System Plug-In will properly communicate and download the new controller. The System Plug-In will not communicate with an applicationless device.