"Failed to Connect to Server" During Sigma Data Import to EBO

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • "Failed to Connect to Server" During Sigma Data Import to EBO
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • DavidChild
    DavidChild
  • Gary
    Gary

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2103 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

"Failed to Connect to Server" During Sigma Data Import to EBO

Picard Product_Support
‎2018-09-10 07:18 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-05 08:13 PM

Issue

When performing a Sigma data import into Building Operation, the following error appears on the Enterprise Server (ES) machine:
"Failed to connect to server"

01 SBO Screens.jpg

Simultaneously, the Sigma Server service on the Sigma machine has stopped unexpectedly.

02 Sigma Server.jpg

Product Line

EcoStruxure Building Operation

Environment

  • Sigma 4.08
  • Building Operation Workstation
  • Building Operation Enterprise Server

Cause

The Sigma database contains a longtext.rec file with unsupported characters, which causes the Sigma Server service to crash during the import process.

Resolution

Option 1: Longtext Not Required

If the Sigma longtext entries are no longer needed:

On the Sigma Server:

  1. Stop the Sigma Server service.
  2. Navigate to C:\Sigma\Data\ and delete the longtext.rec file.
  3. Restart the Sigma Server service.
  4. On the SBO ES: Retry the Sigma data import.

Option 2: Longtext Required

If longtext entries are still needed:

On the Sigma Server:

  1. Start the Sigma Server service.
  2. Open a Sigma client (can be on the Sigma server, SBO ES, or another machine).
  3. Log into the Sigma Operator Panel.
  4. Go to System Alarm Manager → Configure → Longtext.

    03 Sigma Alarm Manager1.jpg

  5. Review each longtext entry and remove unsupported characters.

    04 Longtext Characters1.jpg

  6. Re-enter the required longtext messages.
    • You may find backup copies in C:\Sigma\Data\Longtext.
  7. On the SBO ES: Retry the Sigma data import.

Once the unsupported characters are removed or the file is deleted, the Sigma Server service remains stable, and the data import completes successfully.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
Tags (3)
  • Find more articles tagged with:
  • 19845
  • CraigEllis25
  • DavidChild20
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore