Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How to setup a Mantrap

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to setup a Mantrap
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4887 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to setup a Mantrap

Picard Product_Support
‎2018-09-10 05:08 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:03 AM

Issue

How to set up a Mantrap

Product Line

TAC INET

Environment

  • I/NET Access Control Site
  • Interlocked Doors
  • Person Trap
  • Anti-Passback (APB)

Cause

What is a mantrap? A mantrap is a security device that monitors and controls two or more interlocking doors to a small room that separates a non-secured area from a secured area. These interlocking doors allow only one door to be open at any time.

What are interlocking doors? “Interlocking doors” is a security term used to describe how two or more doors are interfaced with each other and locked. Doors that are interlocked cannot be opened at the same time. Either door can be unlocked and opened as long as the other door is locked and closed and no other alarm condition exists.
What types of locations require a mantrap? Mantraps are used at high-value or critical security areas where only authorized persons are allowed to enter. Typical areas include sensitive data processing areas, cash handling areas, critical research labs, security control rooms, and automated airline passenger entry portals.

Why would my company consider a mantrap? Typically, security personnel are posted in high-security locations to control access into the area. An automatic mantrap used in this same location would control the access to the area, allowing security personnel resources to be available for other tasks.

What is the difference between a mantrap and an interlocking door control system? Regarding controlling two doors within a vestibule, “mantrap” and “interlocking door controller” can be used interchangeably. Once the number of doors controlled by a single controller exceeds two, then the term interlocking door controller should be used.

Resolution

I/NET has three ways to do a mantrap:

  1. Event sequences and calculations -- limit to 5-7 SCUs per 7798C due to system loading
  2. Use a "standalone" third-party device that is wired to the door and is not attached to I/NET at all
  3. Use the interlock wiring diagram that uses relay logic to function. This is also part of the I/NET System.

I/NET Seven allows configuring a door to have both an entry and an exit reader and uses the selection of Anti-pass back/Anti-tailgate to set up Zones or areas with stricter control over access. However, even with the Anti-pass back option set to Hard, which denies access to successive reads at the same reader, it does not prevent multiple persons from entering and exiting together, and it does not provide real-time accounting for the number of people in a Zone. Besides having a guard at the door, the usual method of implementing Zones does not prevent violations.

 

The example below presents some thoughts about improving the Zone's security in an I/NET Seven system.

  1. There needs to be a way to restrict the number of people gaining access to the door.
  2. There needs to be a way to keep up with how many people are in the Zone.

One method to accomplish the first goal is to use a two-door egress system, as is often used in jails and similar security setups. For a medium security setup where the intent is not to prevent people from leaving, only one door needs a card reader. Such a design is illustrated below:


Notes:

  1. Electric strike normally energized.
  2. Low walls or fences. The area should be small enough to limit how many people or things are in it at one time.
  3. Gate with normally de-energized bolt. The gate could swing both ways, so one would only have to push it to open it. It should have a spring to close it.

The door “a” would have both an Entry and Exit reader, so an Anti-pass back/Anti-tailgate can be implemented. The strike on the door “a” would normally be energized and opened by a valid reader transaction.

 

The bolt on the gate would be normally de-energized, allowing the gate to open freely. When the strike on the door “a” is de-energized, the bolt on the gate would be energized, preventing the gate from opening. This is designed to allow only one person to simultaneously move into or out of the Zone.

 

An added level of security would be accomplished by mounting IR emitter/receiver pairs along the low wall or fence at regular intervals. A person would interrupt the light at a limited number of receivers, so if more than expected are interrupted, it would violate one person at a time, and necessary action could be taken.

 

If material needed to be moved through the door, the gated area could be made large enough to allow for a dolly or whatever might be needed. A different access level would be provided to those who are moving material, thus preventing the alarm for too many people going through the door.

 

This approach would restrict movement into and out of the Zone, and the example given in the AIC note could be implemented to allow real-time monitoring of occupancy levels in the Zone.

 

Design thoughts:

 

  • To calculate whether more than one person is in the gated area, sum the number of receivers that are detecting and compare it to a minimum, e.g., four of six must be detecting if only one person is in the area.
  • If material is in the gated area, generate an alarm if an authorized card is not read. Use the alarm delay for the point to give an individual time to make a card read before sounding the alarm.
  • The AIC scheme described in the AIC note would have to be duplicated for the material mover individuals to change the calculation of a person in the gated area. For material movers, the detection would be (sum of detectors < minimum), whereas for regular individuals, the detection would be (sum of detectors > minimum). Remember, the SLI connected to this door can have only 64 AIC’s and this door now has used 2 of them.
  • Use an inter-card delay long enough to let the person exit the gated area before another card can be read.
  • For personnel safety, there must be a way to de-energize the strike. One method would be to mount an emergency exit button located far enough away from the door so a single person could not reach it and a second emergency exit button on the outside of the Zone so someone could keep the strike de-energized until everyone is evacuated. Most codes probably require that all strikes be de-energized in case of smoke or similar emergency to provide another fail-safe.

 

Here is a pdf document which explains the setup using an SCU
Click here to download third-party ManTrap information.

Labels (1)
Labels:
  • TAC INET
Attachments
4900PLC Door Interlock.zip
Tags (2)
  • Find more articles tagged with:
  • 6880
  • RobertAndriolo23
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore