SE 7300 override/°C-°F button choice.
  • SE 7300 override/°C-°F button choice.
  • SESA150559
    SESA150559
‎2018-09-06 12:51 PM
When defining configuration on SE7300 part no, your choice is between "0" (override) and "5" (possibility to change between °C and °F in interface).
SE7300
its not possible to have both override and °C/°F feature
When defining the part number, you will have to choose. The override feature is usually the preferred choice in industrial applications, while the °C/°F feature is used for Hotels and similar, where users are given the possibility to change unit of desired temperature.
Labels (2)
  • EcoStruxure Building Expert
  • Field Devices
Tags (4)
  • 7004
  • celsius
  • degrees
  • fahrenheit
100% helpful (1/1)