Issue
Reload fails during the programs portion with an error message similar to:
Unable to reload attributes. OMS database is currently unavailable, backing up.
Environment
- i2
- bCX
- NC2
Cause
A flash backup PE program is set to autostart. As soon as that program loads, it will start to perform a flash backup and any PE programs that have not loaded will not load and the reload will terminate.
Resolution
Make sure any programs set to automatically backup a controller cannot do so until after a reload is complete.