Issue
The data sheet states 2 different power consumptions:
Power consumption: average 6 VA
Transformer sizing: 30 VA
Which one should be used for calculating power supply?
Environment
Forta
Cause
There are different figures specified in the documentation for the Forta series actuator.
Resolution
Average consumption is 6VA, but the peak consumption is 30VA, and this is just before the valve reaches the fully closed position.