How to latch an output with one input and unlatch with another input.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to latch an output with one input and unlatch with another input.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support
  • AdamSteele
    AdamSteele

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2928 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to latch an output with one input and unlatch with another input.

Picard Product_Support
‎2018-09-10 07:20 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:38 PM

Issue

If one Input is required to activate an Output and another Input to de-activate the Output, this Output can be defined by Input Types. The below is a simple scenario where when the first Input turns ON the Control Output turns ON, when the second Input turns ON the Control Output turns OFF.

In this scenario we are activating a Duress alarm when an Input goes on and resetting that Alarm when the reset Input is triggered.

Product Line

Security Expert

Environment

Security Expert

SP-C

Cause

Require detailed instructions on how to program a latching duress alarm scenario.

Resolution

Objects required:
 
1x Area - "Duress_Area"
2x Input Types - "Duress Enable", "Duress Reset"
2x Inputs - "VI Duress Trigger", "VI Duress Reset"
1x Output - "VO Duress Alarm"
 
Note: The above object names are what is used in this example, you can set these to whatever you require.
 
 
Instructions:
 
Creating the Area
1. Navigate to Programming > Areas. Add a new area (Duress Area), set the Entry and Exit Delay Times to 0. All other settings can be left default.
SX_DuressLatch_Area.jpg
 
Creating the Input Types
1. Navigate to Programming > Input Types. Create a new Input Type (Duress Enable)
2. Set the Control Output to your Output (VO Duress Alarm).
SX_DuressLatch_InputType_ControlOutput.jpg
3. Under Options 1 enable Generate Alarms.
4. Under Options 2 enable Activate Control Output on Alarm .
SX_DuressLatch_InputType_Activate.jpg
5. Set any other options that may be required.
6. Create a new Input Type (Duress Reset) and redo steps 2 - 5 above except under Options 2 enable Deactivate Control Output On Alarm.
SX_DuressLatch_InputType_Deactivate.jpg
 
Configuring the Inputs
1. Navigate to Programming > Inputs select the Input (VI Duress Trigger) and set the following:
2. Set the Area to the Dummy Area (Duress_Area) created earlier.
3. Set the Input Type to the Input Type (Duress Enable).
SX_DuressLatch_Input_Trigger.jpg
4. select the Input (VI Duress Reset) and set the following:
5. Set the Area to the Dummy Area (Duress_Area) created earlier.
6. Set the Input Type to the Input Type (Duress Reset).
SX_DuressLatch_Input_Reset.jpg
 
Testing
1. Arm both portions of the Area
2. Activate the Input (VI Duress Trigger) to confirm Alarm is generated and Output Activates.
3. Activate the Input (VI Duress Reset) to confirm Alarm is generated and Output Deactivates. 
SX_InputLatchOutput_2ndInputResetLatchOutput_AreaControl.jpg
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • 19820
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore