Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1895 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 72
    • 73
    • 74
    • …
    • 95
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

MP-V upgrade from v1 firmware causes Box Flow to read zero

  Issue When upgrading a MP-V from v1.xx to a later release the Box Flow reading is zero when there is a velocity pressure. Product Line EcoStruxure Building Operation Environment SmarX IP controller MP-V   Cause When a MP-V-7A or MP-V-9A is upgraded from v1.xx to v3.xx firmware. The MP-V does not control and the Box Flow reading is zero. The damper will rotate to 100% with a Velocity Pressure reading.   The Balanced k-factor and the Balance flow correction are found to be at zero:       Resolution During the upgrade process the flow data is not retained.   Before the upgrade at v1.xx, backup the flow balance data under the Flow Balance Data object,     Continue and complete the upgrade process, re-hosting the controller and downloading the objects. Finally, restore the flow data.
View full article
Sisko DavidChild Sisko
‎2021-03-22 02:49 AM

on ‎2021-03-22 02:49 AM

Labels:
  • EcoStruxure Building Operation
1577 Views

All Custom Types disappear in an SmartX Server

Issue All Custom Types in an AS-P suddenly disappeared and it is not possible to create any new Custom Types. When trying to create a Custom Type it results in an invalid Custom Type object:   Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium Cause For an unknown reason, the Configuration database has become corrupt. Resolution Workaround 1: Do an upgrade of the AS-P to the same version which should fix this issue.   Workaround 2: Restore a backup taken before this issue appeared.
View full article
Janeway Jonas_Brissman Janeway
‎2021-03-10 05:52 PM

on ‎2021-03-10 05:52 PM

Labels:
  • EcoStruxure Building Operation
1141 Views

Restricting Workstation or WebStation login in EBO User Group Permissions

Issue How can specific users be restricted to logging into EcoStruxure Building Operation through Webstation and not through Workstation?   Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Webstation Cause There is a requirement that specific users be restricted from logging in to EcoStruxure Building Operation through Workstation but be allowed to log in through EBO WebStation. Resolution It is not possible today to restrict users' access to Workstation or WebStation individually. There is no more information available on user permissions than what is available today in WebHelp and technical guides.  
View full article
JohnBoehmer Schneider Alumni (Retired)
‎2021-03-05 07:58 AM

on ‎2021-03-05 07:58 AM

Labels:
  • EcoStruxure Building Operation
2101 Views

Script program incorrectly calculates time differential

Issue A script program uses a calculation of the difference between event marker DateTime and the current time to trigger an alarm flag. The alarm flag is initially set correctly but switches off again after 2147 seconds. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium Version 3.2.2 Cause The result of the calculation Current Time - FailureTime returns a correct value until the difference exceeds 2147 seconds. At that point the calculation returns a negative value and begins counting upward toward zero. Resolution The Script program was broken.   Once the program was deleted and reimported the same script code consistently calculated an increased time differential. This behaviour is identical to a defect which was fixed in the EBO 3.0.4 release.  In that case it was the controller rather than the program that was at fault.
View full article
JohnBoehmer Schneider Alumni (Retired)
‎2021-03-04 05:47 AM

on ‎2021-03-04 05:47 AM

Labels:
  • EcoStruxure Building Operation
1842 Views

Gathering PME Diagnostic Logs to troubleshoot PME/EBO Integration

Issue Integration issues between EcoStruxure Building Operation and Power Monitoring Expert/Energy Expert are often complex and may require more the one PSS Team to resolve.  Investigations may begin on the BMS side but then may move quickly to the EMS team so it would be helpful at that point to gather helpful Diagnostic Data on the PME/EE system Product Line EcoStruxure Building Operation, Power Monitoring Expert, Energy Expert Environment Building Operation Enterprise Server Integration Cause Existing KB articles on EBO and PME/EE integration generally focus on troubleshooting or investigating the EBO side and little data is available in KBs for direct PME/EE investigation. Resolution EMS Support have their own structure of useful FAQs rather than KBs and in this situation there is an FAQ article which details how to extract very useful Diagnostic Date from the PME/EE Server which can be obtained before the support case is escalated to the EMS Expert Team: https://www.se.com/ww/en/faqs/FA275753/   There is also a search function where you can browse through other potentially helpful FAQ articles.
View full article
Admiral David_Kendrick Admiral
‎2021-03-04 03:02 AM

on ‎2021-03-04 03:02 AM

Labels:
  • EcoStruxure Building Operation
1796 Views

"Server Error in '/ebo' Application" while registering a system

Issue When attempting to register a system, an error page is shown indicating a server error in the /ebo application   Error Text: Runtime Error An application error occurred on the server.  The current custom error settings for this application prevent the details of the application error from being viewed remotely (for security settings).  It could, however, be viewed by browsers running on the local server machine.  Product Line EcoStruxure Building Operation Environment WorkStation Registration Windows Server 2012 R2 and above Cause While the error message points to an error in the back end server, it is actually due to a setting on the client PC. Enhanced security configurations in Internet Explorer on Windows Server systems, is blocking required content from being run. EcoStruxure Building Operation WorkStation uses Internet Explorer as the built-in browser and is therefore affected by this. Resolution While the enhanced security measures can be disabled altogether, the resolution with the smallest impact is to add the URL of the registration portal to trusted sites in Internet Explorer. Open Internet Explorer Open Internet Options Select the Security tab Click Trusted Sites Click Sites Enter the registration portal URL: https://registration.smartstruxure.schneider-electric.com Click Add Click Close Click OK After doing so, restart WorkStation, and attempt the registration again. For more information, refer to the WebHelp topic EcoStruxure Building Operation Registration Page is not Displayed.
View full article
Administrator Benji Administrator
‎2019-07-18 05:11 PM

Last Updated: Picard RobertAndriolo Picard ‎2021-03-02 08:05 PM

Labels:
  • EcoStruxure Building Operation
4105 Views

Timestamp is in the middle of the month when viewing a Trend log

Issue When using a calculation method on a trend log list or trend chart with the period "Month" the timestamp is always on the 16th of each month. See the example below: Why is the time stamp always the 16th and is it possible to change the collection date Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause When doing a calculation in a trend log list or trend chart the timestamp will always be in the middle of the chosen period. Resolution This is currently not possible to change in EBO. Alternative ways of presenting the data are to use Dashboards or Notification reports
View full article
Janeway Jonas_Brissman Janeway
‎2021-02-25 09:19 AM

Last Updated: Janeway Omaelk ‎2021-03-01 11:35 PM

Labels:
  • EcoStruxure Building Operation
1736 Views

Continuum integration bindings made via Script IE (Import/Export) stop working

Issue Bindings made under the Infinet interface using Import/Export system (IE) stop updating. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium Continuum i2920 Controller Cause Objects under the Infinet interface sometimes lose their Object IDs for reasons that are not yet fully understood. The issue has been seen during up revision of the AS-P from 1.9x to 3.x Resolution Under the Infinet interface, right-click on the Application folder of the AS-P or Infinet device and select "Resolve object ids" The system automatically re-assigns the missing ids Download applicable i2 devices
View full article
Captain AbeMeran Captain
‎2021-02-25 09:13 AM

on ‎2021-02-25 09:13 AM

Labels:
  • EcoStruxure Building Operation
982 Views

Unable to import Infinet devices into AS-P

Issue Importing Infinet devices into AS-P fails with the following error "Invalid Data Error: Invalid_Data (0x10000) in module Coml(11). "Invalid cast from null": CreateObjectRequest".  Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium Cause Infinet devices have a space character within their names Resolution Remove the space character and use an underscore in its place.
View full article
Commander JonGreen Commander
‎2021-02-25 09:03 AM

on ‎2021-02-25 09:03 AM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1045 Views

Memory usage for ES increase until it finally hangs

Issue After starting the Enterprise Server(ES), the memory usage increase constantly until it finally hangs, which happens in a couple of days.  Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server version 3.2.x Building Operation Automation Server 3.2.x Cause Running a Notification report including many trend logs can take a long time to finish; for example, a report including 91 trend logs can take up to 10 minutes. If the Notification report is triggered more often than 10 minutes, reports will start to queue up, making the memory usage for the ES increase over time, and it will finally hang. Resolution When having a Notification report which includes many trend logs, make sure that it is not running too often as it is a rather slow process to create a report including many logs. Example: A Notification report which includes 91 trend logs with 168 log records takes 10 minutes to finish.
View full article
Janeway Jonas_Brissman Janeway
‎2021-02-23 02:55 PM

on ‎2021-02-23 02:55 PM

Labels:
  • EcoStruxure Building Operation
1574 Views

AS-P/B DHCP Server Configurability

Issue Webhelp and the Technical Reference Guide supply information for using the AS-P/B DHCP server option, however, a number of relevant questions have not been answered. Product Line EcoStruxture Building Operation Environment Building Operation Automation Server Premium (AS-P 0.62 hardware) Building Operation Automation Server Bundled (AS-B) Building Operation SmartX IP Multi-purpose Controller (MP-X) Building Operation SmartX IP Room Controller (RP-C) Building Operation SmartX Controller IP-IO Series Cause There are typically a number of options to configure DHCP servers, but since the DHCP server included with the AS-P/B is very basic and NOT configurable, it's important to understand which options are and are not available. Resolution Webhelp has some helpful information about the DHCP Server Options. The AS-P/Bs built-in DHCP server assigns unrouted IP addresses within the range of addresses from 10.110.210.2 to 10.110.210.254. This was developed to allow for a quick configuration of a private MP-X/RP-C network. The AS-P/B DHCP server can be disabled and another DHCP server can be used. Here is a list of other questions and answers that may come up based on typical options in other DHCP servers: Can the scope of the IP range be configured? There is no way to configure or limit the range of the standard IP address range or to have multiple scopes. Can IP exceptions be configured? There is no configuration option to prevent the AS-P/B DHCP server from assigning a specific IP address. The AS-P/B DHCP server is unaware of static IP addresses, so if a switch or other device has a static IP set in the 10.110.210.2 to 10.110.210.254 range, you run the risk of having the AS-P/B DHCP server assign an IP address twice which can cause a number of issues. Can a Default gateway be configured? Not configurable Can a Subnet mask be configured? Not configurable Is IP6 supported? No Can lease types be configured? No Can multiple DHCP servers be installed on the private LAN? No Should MP-X/RP-C IP level devices only be hosted within the private AS-P/B network? Most site IT departments prefer that the BAS networks be isolated, however, if the network switch (Not the AS-P/B) is used for assigning DHCP IP addresses, it could hand out addresses to the AS-P/B and the MP-X/RP-C devices if they are on the same subnet. A managed (RSTP Enabled) switch can reside as a client to the AS-P/B. This is due to how the Private DHCP option is advertised. On-site IT departments may not want the switch on the customer's LAN so it is placed in the private AS-P/B network. Does the AS-P/B DHCP server assign addresses to 3rd party devices? Yes, if the 3rd party device supports this. This would be a configurable option in the device.
View full article
Admiral Alan_Wood Admiral
‎2021-02-23 07:26 AM

on ‎2021-02-23 07:26 AM

Labels:
  • EcoStruxure Building Operation
5736 Views

PostgreSQL/Timescale filling up drive with error logs

Issue The hard drive fills up with logs generated by PostgreSQL/Timescale. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Cause Trend meta table missing information Resolution In the ES, go to the TimeScaleDB configuration. Set Trend and Event storage to false and click save. Set Trend and Event storage to true and click save.
View full article
Captain AbeMeran Captain
‎2021-02-04 06:31 AM

on ‎2021-02-04 06:31 AM

Labels:
  • EcoStruxure Building Operation
1516 Views

Some helpful basic IP commands.

Issue Some helpful basic IP commands. Product Line Other Environment Computer with IP NIC or Network Cause Need for basic IP configuration or IP address Resolution Go to start, click run and type in "cmd". This takes you to the command prompt. Type in: "ping xxx.xxx.xxx.xxx" to see if your device is online and its response time. Make sure you put the space between "ping" and "xxx". "ipconfig" and hit enter to get the info of the computer you are currently using. You'll get the IP address, subnet mask and the gateway. "ipconfig/all" and hit enter to get more info on the machine your using. It will give you all the above and then some including the DNS server addresses. "tracert xxx.xxx.xxx.xxx" and hit enter and you can see the servers that you are going through to get to your destination. This can be used when connecting to a Loytec or a iLon and the IP address is being presented to the L-IP or iLon is unknown. Connecting through a firewall/gateway/NAT server, you are not presenting the PC's address - when you do the tracert you will go through your gateway and the next address will be the IP you are presenting- Use this in the iLon as the LNS server address.
View full article
Picard Product_Support
‎2018-09-06 03:05 PM

Last Updated: Administrator CraigEl Administrator ‎2021-02-01 02:16 PM

Labels:
  • Andover Continuum
  • EcoStruxure Access Expert
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
2312 Views

Software permission on point level

Issue Is it possible to set software permissions for a Public Value in a Menta or Function Block program in EcoStruxure Building Operation (EBO)? Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause Public values in Function Block Programs (FBP) or Menta programs are not seen as objects but as attributes of the FBP or Menta object. Resolution It is not possible to set software permission on point level for a Menta program or Function Block Program, only on the Module level. One workaround is to create a Search or Watch View and add the signals the user should be able to change or add the points to a graphic. Set permissions to the Search, Watch window, or graphic.
View full article
Janeway Jonas_Brissman Janeway
‎2021-02-01 01:11 PM

on ‎2021-02-01 01:11 PM

Labels:
  • EcoStruxure Building Operation
1227 Views

Number of COV subscriptions supported by an RP-C

Issue What is the limitation on the number of COV subscriptions an RP-C can handle? Product Line EcoStruxure Building Operation Environment Building Operation Room Controller (RPC) Cause When setting up a binding to an RP-C to read a value from another device or transfer a value in the RP-C to another device COV subscriptions are often used.  Resolution The number of subscriptions an RP-C can support is limited primarily by the available resources of the controller. An RP-C with a single point can support thousands of subscriptions but that’s not a realistic configuration on a live site. If resources were allocated to support a defined number of COV subscriptions, this would lock down those resources (primarily memory), making less room for other applications. Since the maximum number of subscriptions depends on how many available resources the controller has at the moment when a subscription is made, there is no guaranteed number on how many subscriptions an RP-C can support.
View full article
Janeway Jonas_Brissman Janeway
‎2021-02-01 12:04 PM

on ‎2021-02-01 12:04 PM

Labels:
  • EcoStruxure Building Operation
1078 Views

How to connect a 4-wire PT100 on 3-wire RTD input

Issue How to connect a 4 wire PT100 or PT1000 sensor to a 3-wire RTD input. Product Line EcoStruxure Building Operation Environment Building Operation I/O Module 16 Ch RTD Cause Some PT100/PT1000 sensors have only 3 terminals to connect to. Resolution The wires to the sensor are often color marked in pair, like two red cables and two white cables. As we only have 3 terminals to connect to, the solution is to only connect 3 of the cables, and not connect the 4th cable.   As the RTD device also measure the resistance of the cables, to make a correct temperature reading, it is important that all three wires used do have the same length and resistance. Therefore, the fourth wire should NOT be connected in parallel, it has to be un-connected.
View full article
Guinan MikaelKrantz Guinan
‎2021-02-01 11:53 AM

on ‎2021-02-01 11:53 AM

Labels:
  • EcoStruxure Building Operation
4608 Views

Bitwise operations in script is not consistent regarding negative values

Issue Bitwise operations in script behave differently in the AS-P compare to ES regarding negative values. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Enterprise Server Building Operation Automation Server Premium Cause Bitwise operations in the script only defined for positive Integers. Resolution Enterprise Server processes negative operands as twos complement whereas Automation Server Premium does not handle negative operands. Behavior with negative integers is undefined.
View full article
Guinan MikaelKrantz Guinan
‎2021-02-01 11:44 AM

on ‎2021-02-01 11:44 AM

Labels:
  • EcoStruxure Building Operation
810 Views

Could not save TAC Xenta application due to Save Error

Issue When importing and saving an application from TAC Vista into Building Operation Workstation, an Error message shows up. Product Line TAC Vista, EcoStruxure Building Operation Environment Building Operation Workstation TAC Xenta Control Device Cause In the application, there were two trend log entries with the same name. Resolution Rename one of the duplicate trend log names.
View full article
Guinan MikaelKrantz Guinan
‎2021-02-01 11:27 AM

on ‎2021-02-01 11:27 AM

Labels:
  • EcoStruxure Building Operation
709 Views

Continuum X-Driver upgrade path in EcoStruxure Building Operation

Issue For integration purposes, it is important to clarify exactly what Andover Continuum X-Driver protocols have a prescribed upgrade path and remain supported in EcoStruxure Building Operation (EBO) Product Line Andover Continuum, EcoStruxure Building Operation Environment Andover Continuum Building Operation Enterprise Server Building Operation Automation Server Premium Cause As more and more systems Transition from Andover Continuum to EBO, customers need to know how existing Continuum X-Drivers can be supported and upgraded to maintain data connectivity in their new EcoStruxure Building Operation architecture. Resolution Product Announcement PA-00789 available on EcoExpert Exchange details all those X-Drivers which are supported going forward into EBO
View full article
Admiral David_Kendrick Admiral
‎2021-02-01 10:11 AM

on ‎2021-02-01 10:11 AM

Labels:
  • EcoStruxure Building Operation
1103 Views

Supplemental Documentation on the Menta/Function Block PID blocks

Issue Supplemental Documentation on the Menta/Function Block PID simple blocks Product Line TAC Vista, EcoStruxure Building Operation Environment Menta/Function Block editor Cause The document below is intended to clarify some of the more subtle aspects of the Menta/Function Block PID blocks and when/how to use them. Resolution A Brief Overview of PID Control Proportional-integral-derivative (PID) control is a generic feedback control loop algorithm. A PID controller calculates the error from the desired setpoint of a measured variable. It then adjusts the control output accordingly to try and minimize this error. Parameters used in the calculation must be tuned according to the system they are employed to control. The three prominent parameters are the proportional, integral, and derivative values. The proportional value affects the change in the output signal based upon the current error from setpoint. The integral value works based on the sum of the most recent errors. The derivative value reacts based on the rate at which the error has been changing. The weighted sum of these three actions is used to adjust the control output. The most typical application used in HVAC controls is actually a proportional-integral control with no derivative influence (PI). Derivative action is very sensitive to measurement noise, and generally considered too complex for the relatively limited benefit to slower, more easily controlled loops.   Three Types of PID Blocks in Menta Menta has three different simple blocks for PID control. They are: PIDI, PIDP, and PIDA (links to Web Help). PIDI PIDI is a PID controller with an incremental output. It is designed to be used together with two digital pulse output (DOPU) blocks in control loops with increase/decrease actuators. Input parameters to the PIDI will influence the operation of the controlled output in the same way as the analog PID blocks. The output, however, will not show a percentage. The end user will only be able to force an “open” or “close” command to the actuator – not set it to a desired percentage. Examples of how to use PIDI are explored later in the document. PIDP PIDP is the newer of the two analog output PID controllers in Menta. Because of this, it can only be used in Xenta controllers with a system program version of 3.6 or later. In Menta, under Options > Device Specification, it may be necessary to set the file to system version 3.6 or later during the programming phase. PIDP differs from PIDA in 4 distinct ways: PIDP will remain in saturation for a longer time than PIDA. The integral portion of the calculation keeps a running sum of previous error adjustments. Because of this, it can “wind up” a stored integral response. There is an anti-wind up mechanism to combat the effect, but PIDA has no wind up at all. In PIDP, a change in the setpoint value will not cause a step change when using PI or PID control. The measured error is not from the setpoint input, but rather from the last sampled measured value. The PID block samples a measured variable any time it is inside the deadzone. The allows for the calculation’s setpoint to equal the edge of the deadzone and have a less dramatic response to exiting the deadzone. The other time it will sample a new measured variable is any time a control coefficient is changed. This is an important distinction to be aware of during tuning operations. It may be useful to force the measured variable equal to setpoint after altering tuning parameters. The tracking of the tracking signal is not instantaneous in PIDP, as opposed to PIDA. Looping back the output to the TSg tracking signal feedback input will not cause the PID to stay synched with an overridden output. Additional logic is needed to switch the Mode to 0 for one program cycle in order to lock in the feedback signal any time it does not equal the output signal. The D-part is not as sensitive to measurement noise in PIDP as in PIDA. PIDA PIDA uses the following equation to calculate its output: where e is the control error, y is the measured value (MV), G is the controller Gain, Ti is the integral time, Td is the derivative time and h is the Control Interval (ControlInt), i.e. the time between two successive updates of the controller output signal. While analyzing and understanding this formula is beneficial to fully understanding the PID simple block, do not get too mired in the details. This document will help to demystify input parameters to make the PID work in a number of situations. For the purpose of this document, a PIDA will be assumed for all applications.   Inputs to the PIDA Block MV Measured value is the process variable for the PID controller. It is an input value of type Real. Examples of this would be a room temperature, a return air CO2 level, or a hot water differential pressure. SP Setpoint is the desired value of the measured value. It is an input value of type Real. It could be a static value (Operator “Real const”), adjustable from the front end (Simple Block “PVR”), a stepping value, or a modulating value. If the setpoint is likely to change often, it is recommended to use the PIDA block as opposed to PIDP. Mod The mode input to the PID block will control its action and enable or disable the control output. It is an input value of type Integer. There are four possible modes: Mode = 0 Web Help lists this mode as, “Off, controller stopped.” A more accurate description would be, “The value present at the TSg input will pass through to the output.” If the looped back output value is not changing, then the PID output will freeze. Mode = 1 Normal control. A new output value will be calculated on every Control Interval. Mode = 2 Controller output forced to UMax. This could be used on a hot water valve when freeze protection is enabled. Mode = 3 Controller output forced to UMin. This typically represents the “off” position of a PID. G Gain is the proportional parameter of the PID control. It is an input value of type Real. It is represented by the following equation: To arrive at an appropriate default value for Gain, three parameters must be considered: UMax, UMin, and proportional band. In typical applications, UMin and UMax will be 0% and 100%, respectively. This is because most valve or damper actuators are going to control between 0-100%. For the following examples, this will be assumed, but do not discount the effect it will have on default Gain parameters if these values change (such as in a cascade control application). Appropriate default parameters are merely in the same mathematical order of magnitude as the final tuned value. Rarely will the default parameter result in perfect operation of the control loop. It is only intended to get close enough to provide decently steady control until proper tuning can take place. It is usually easier to think in terms of proportional band than proportional Gain. Consider a room temperature. What would be an appropriate band around the setpoint to maintain? Perhaps ±5°F. If ±5°F is selected, that would result in a 10°F proportional band. Plug that into the equation along with the assumed UMin and UMax values: This would result in a default Gain of 10. It is important to remember that Gain is a unit-less value. A Gain of 10 is neither large nor small – merely relative to the process variable and anticipated error from setpoint. Consider a PID controlling an outside air damper to maintain an outside air flow of 1000cfm. Would a proportional band of 10cfm make sense in this situation? Probably not. A more appropriate value might be a band of 500cfm. Plug this into the same equation as before: In the case of air flow control, because the process variable and anticipated error from setpoint are so much larger than in temperature control, a more appropriate default Gain would be 0.2. In a third situation, consider a PID controlling static air pressure in a supply duct by modulating a variable speed fan. A proportional band of 500”wc would not make sense. A band of 0.8”wc might be more appropriate. In the instance of static air pressure, a default Gain of 125 would be suitable. Comparing these three situations with Gains of 0.2, 10, and 125, they will all have relatively similar speeds in the control loop. Just by glancing at these values alone, it cannot be said that any of them are “bigger” or “faster” than the others without a more in depth mathematical analysis. In addition to the value of the Gain, the sign is also important. Positive values represent reverse acting PIDs like a hot water valve where the signal to the valve will decrease as the room temperature increases. Negative values represent direct acting PIDs like a chilled water valve where the signal to the valve will increase as the room temperature increases. To avoid confusion at the front end, and reduce the possibility that end users will accidentally reverse the action of a PID, it is best practice to always use a positive value PVR to represent the value of the Gain. Then use an Expression absolute value operator “ABS()” to remove any sign and apply a negative value when necessary. Using this method, the Gain from the front end will always appear as a positive value and no consideration for the proper action of the PID will need to be taken after the programming phase is complete. Ti Ti is the integral time, or the integral portion of the PID control. It is an input value of type Real. Adding integral control to a straight proportional algorithm helps to avoid “controlling to an offset.” It is theoretically possible that a chilled water valve at 40% is exactly the amount of chilled water required to maintain a supply air temperature of 58°F, even if the setpoint is 55°F. If the error in the signal never changes, then the proportional algorithm will not change the output signal. And an offset has been achieved and will now be maintained indefinitely. Integral time will eliminate this possibility. Every Control Interval that the temperature remains above the setpoint, integral control will add a little more to the control output. This will cause the measured variable to always approach the setpoint. Because this value does have units (seconds) it is possible to compare one integral time value to the next. Ti is inversely proportional to the integral effect in the formulation of the next control output. In general, the smaller the Ti value, the more integral control will affect the control output. A value of 50 seconds would have a very large impact on the output. A value of 2500 seconds would hardly affect the control output at all. The exception to this rule is that a value of 0 seconds will disable integral control. Typical default values fall anywhere between 250-1000 seconds. Some PID solutions may be susceptible to “integral wind up” where the internal calculation desires and integral response beyond the output limits. When the control signal reverses, the integral wind up must be reversed before the output sees the change. In the PIDA algorithm, integral wind up is not a concern. Td Derivative time is also measured in seconds and represents the D portion of the PID. It is an input value of type Real. Derivative control is generally considered too complex and sensitive to measurement noise to be of sufficient benefit to HVAC control. A Simple Block “PVR” set to a value of 0 seconds will disable derivative control, but allow the tuner to add derivative control if desired. DZ Dead zone refers to the amount above and below the desired setpoint that will result in no change to the control output. It is an input value of type Real. This differs from the concept of a proportional band in that it is not centered around the value. While a proportional band of 10°F represents ±5°F around setpoint, a dead zone of 10°F would represent ±10°F around setpoint. A dead zone is helpful to reduce “hunting” of the control output where it repeatedly rises and falls when a steady output would cause the control variable to steady out. Typical values depend on the process variable. For a supply air temperature, anywhere from 0.25°F to 0.5°F would suffice. For outside air flow, anywhere from 50cfm to 100cfm might be appropriate. In a supply air static pressure control loop, limiting the dead zone to 0.1”wc would suffice. TSg TSg is short for tracking signal. It is an input value of type Real. The internal equation uses this as the value of the previous control signal. It should be looped back to the PID from the output signal. This might be directly from the output of the PID, or it may be after some external logic. The TSg input can be used in another way as well. When the PID is in Mode 0, the TSg value passes directly through to the output signal. By setting the PID to Mode 0 for the first second of a control period, initial positions other than UMin or UMax can be achieved. It can also be used to keep a PID in synch with an output that has been overridden by the front end. If the PID is controlling a physical output AO, then the output of the AO should be looped back to the PID.   Configuration Parameters of the PIDA Block ControlInt The Control Interval represents the number of seconds in between each successive calculation of outputs. If this value is set to 0 seconds, then the Control Interval will match the cycle time of the application. The Control Interval should be thought of in terms of how long a change in the control output will take before the impact is realized on the measured variable. Consider three scenarios: Scenario 1: A variable speed drive modulates a pump speed to maintain chilled water differential pressure. Because water is incompressible, a change in the pump speed results in an almost immediate change in the pressure. A Control Interval of 1 second is appropriate in this scenario. Scenario 2: A chilled water valve modulates to maintain a supply air temperature setpoint. The supply air temperature sensor is a few feet down the duct from the chilled water coil. A PID controller moves the chilled water valve from 0% to 10%. How long will it take before the supply air temperature starts to fall? Granted, there are several X factors in this equation, but a good guess might be around 20 seconds. A Control Interval of 20 seconds is appropriate in this scenario. Scenario 3: A supply air temperature setpoint modulates to maintain a large auditorium's temperature setpoint in a classic cascade control configuration. A chilled water valve then modulates to maintain the supply air temperature setpoint. Room temperature dictates that the supply air temperature setpoint should drop from 60°F to 55°F. How long will it take before this change in setpoint causes the room temperature to fall? It may take a full minute, perhaps even several minutes before that change has an affect at the room temperature sensor. A Control Interval of 80 seconds, while seeming very slow, is perfectly appropriate here. Correctly configured Control Intervals will allow one change in position to have an effect on the measured variable before a second (or third, or fourth...) change is made. A proper Control Interval will stop the valve from overshooting unnecessarily. UMin UMin is the minimum possible output of a PID controller. In most applications (valve and damper actuators) this will be set to 0%. In the case of a cascade control supply air setpoint PID, it might be set to 50°F. If the hardware output has a minimum position (say on an outside air damper), it is best to accomplish this with secondary logic as opposed to using the PID UMin. Otherwise if the PID is made public to the front end, the user will never see this value drop to 0, even if the control output is at 0. UMax UMax is the maximum possible output of a PID controller. In most applications (valve and damper actuators) this will be set to 100%. In the case of a cascade control supply air setpoint PID, it might be set to 90°F. StrokeTime The name Stroke Time refers to the manufacturer specified stroke time of a physical actuator. By setting the PID to the same stroke time as the valve it is controlling, it is guaranteed not to “wind up” faster than it is possible for the valve to react. Whenever possible, set the stroke time to match the physical stroke time of the actuator it is controlling. However, stroke time can be thought of in another way. It is used to calculate DuMax, the maximum rate of change of the controller output during one Control Interval. In the case of a chilled water valve that modulates between 0% and 100% with a Control Interval of 20 seconds, see how a stroke time of 180 seconds affects the DuMax: A stroke time of 0 seconds will not limit the rate of change at all in the controller. Based on the error and the Gain, it could potentially jump the full 100% stroke at once. By setting the stroke time to 180 seconds, the amount that the control signal can move every 20 seconds is now limited to 11.11%. It is not proper practice to employ stroke time as a tuning mechanism of a PID. It should be set prior to and independent from the tuning process.   Output of a PIDA Block The output of a PIDA block will usually control a hardware output from a Xenta controller. Because of this, it is typically connected to a Menta Simple Block “AO.” In Function Block it may be output to an analog value or hardware output.   Output of a PIDI Block A PIDI controls a floating actuator using two Simple Block “DOPU” digital pulse outputs. The PIDI will output a value between -1 and 1, which the DOPU block converts into the appropriate pulse lengths. Inverting the decrease signal will pulse the actuator closed when the output of the PIDI is negative.   The downside to PIDI control is that there is no percentage value to report to the front end about the position of the actuator. This is why use of the PIDI is somewhat rare. The same control can be accomplished using a PIDA with some external logic to pulse the floating actuator open and closed. Using a “virtual feedback” signal to mathematically monitor the assumed position of the floating actuator allows the end-user to view a percentage open signal for the actuator. It also allows them to override the Not-Connected AO to a certain position and have the floating actuator travel to that position just as an analog output would. The following example converts a Not-Connected AO from a PIDA into pulse output DOs from the controller. Public Signals and Public Constants All of the parameters that go into the operation of a PID need to be considered when tuning its operation. Eventually, one will come to the question of what parameters need to be made available from the front end. While some thoughts might end up on the well-meaning, under-trained end-user who could potentially wreak havoc by adjusting values, it is more important to consider the startup technician. If a value is not public from the front end, then a download must be performed to make any changes to any values. By making every parameters public by default (and only selectively removing certain parameters during exceptions) less time will be spent in the field during start up. After the PIDs have been tuned, it is always possible to remove certain values from being public. The exceptions are UMin and UMax, which when controlling a valve or a damper are almost always 0% and 100%. If desired, these can usually be hard-coded into the PID with little consideration. However, they can also be made available from the front end with little or no ill effects. Floating, PID, or Cascade Control There are three main control loop algorithms to consider when programming. Which one best suits the application is really a factor of the control loop speed. Consider the three options: Floating Floating control (also called bump control) involves making small, measured adjustments to the control signal on specified intervals. This is usually the best option any time a variable speed drive is involved. This is because these drives typically control supply fan static pressure or hot/cold water pump differential pressure. Both of these are very fast control loops. A slight change in the speed of the drive results in an almost instantaneous change in the measured variable. Floating control reacts more gradually to these quick changes. It compares the measured variable to the setpoint, and if it is too high, it bumps the control signal down a little bit. If the measured variable is too low, it bumps the control signal up a little bit. PIDs can (and often have been) used successfully to control very fast control loops. However, they are typically tuned to closely resemble floating control – low Control Interval, very little proportional control, very high integral control. In the end, it may be easier for a technician to understand and adjust “1% every 5 seconds” than “a Gain of 125 and an integral time of 175 seconds.” The other advantage to floating control is its adaptability. When tuning a PID, it is tuned to one exact set of circumstances – a certain load on the building, a certain volume of piping, etc. If enough of those conditions change by enough, the PID can be sent into oscillations. Floating control will not be affected by these changes. Consider a PID tuned to control a chilled water pump, which maintains differential pressure during the winter when loads are low. During the summer, a manual valve is opened to provide cooling to the athletics storage shed that was unoccupied all winter. This will increase both the demand for cooling and the volume of the pipe. This could potentially render the PID useless. However, a floating control will not react any differently. It will simply increase and decrease the speed as needed. See an example of floating control: The downside to floating control is that there is no proportional control. It will not take a bigger step size when the error is high. To combat this, and especially to aid during startup of equipment, this floating control macro utilizes two different step sizes – one for when error is low, and one for when error is high. By setting the threshold sufficiently high, this will cause more rapid acceleration during startup, and then quickly revert back to normal control during normal operation. This same code will also work relatively well for any size or nature of supply fan or supply pump. Minor adjustment of the parameters may be needed, but it will give a very decent starting point. PID PID control is for control loops of moderate speed. It can be thought of as the "valves and dampers" control method. A chilled water valve modulating to control supply air temperature or a damper modulating to control outside air flow are two examples of when PID control is appropriate. It is a source of debate whether PID control is appropriate in different situations. Some attest that a PID loop can be tuned to accurately control in any situation, including those where this document recommends either floating or cascade control. While this is certainly true, just because a PID can be used, does not mean that it is always the most appropriate solution, or that it will continue to work even as conditions change. Cascade Control Cascade control is used in very slow control loops. It is called cascade because two PIDs are used in a cascading arrangement – the output of the first is the setpoint of the second. An example of when to use cascade control is to modulate a chilled water valve to maintain the space temperature in a very large gym or auditorium. A small change in the chilled water valve position could take a very long time to have an effect at the sensor. If a regular PID is used, it is likely that the PID will wind up all the way to 100% output before the sensor ever experiences the first adjustment's effect. Then it will stay at 100% until it over-cools the space and starts decreasing the call for cooling. The same thing will happen on the reverse side as it modulates all the way to 0% and under-cools the space. And the cycle will continue indefinitely. In this cascade configuration, the supply air temperature setpoint is modulated based on the room temperature and setpoint. The chilled water valve PID then maintains the supply temperature. This will allow control that is more accurate and prevent the oscillation sometimes seen by inappropriate use of a single PID.   Putting It Into Practice There are college courses devoted entirely to the subject of PID control. The subjects covered in this document have barely scratched the surface of the topic. The intent is to give the average Menta/Function Block programmer and field technician the information needed to get a system up and running in as little time as possible with the most satisfied customer possible. Understanding when and why to use PID control will increase accuracy and efficiency of control loops and decrease wasteful overshoot, hunting, and oscillation. Tuning efforts will also be accelerated when the default parameters only require minor tweaking instead of calculation and trial and error. Using the hints and tips suggested will allow not only for proper programming techniques, but also for creation of macro libraries that can be reused and shared to improve effectiveness across business units.
View full article
Picard Product_Support
‎2018-09-07 03:05 AM

Last Updated: Administrator DavidFisher Administrator ‎2021-01-11 10:30 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
31849 Views
  • « Previous
    • 1
    • …
    • 72
    • 73
    • 74
    • …
    • 95
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore