Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

AS-P/B DHCP Server Configurability

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • AS-P/B DHCP Server Configurability
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • JohnBoehmer
    JohnBoehmer
  • Alan_Wood
    Alan_Wood
  • Dave_Shore
    Dave_Shore
  • DavidChild
    DavidChild

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
6087 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

AS-P/B DHCP Server Configurability

Alan_Wood Leader
‎2021-02-23 07:26 AM

on ‎2021-02-23 07:26 AM

Issue

Webhelp and the Technical Reference Guide supply information for using the AS-P/B DHCP server option, however, a number of relevant questions have not been answered.

Product Line

EcoStruxture Building Operation

Environment

  • Building Operation Automation Server Premium (AS-P 0.62 hardware)
  • Building Operation Automation Server Bundled (AS-B)
  • Building Operation SmartX IP Multi-purpose Controller (MP-X)
  • Building Operation SmartX IP Room Controller (RP-C)
  • Building Operation SmartX Controller IP-IO Series

Cause

There are typically a number of options to configure DHCP servers, but since the DHCP server included with the AS-P/B is very basic and NOT configurable, it's important to understand which options are and are not available.

Resolution

Webhelp has some helpful information about the DHCP Server Options.

The AS-P/Bs built-in DHCP server assigns unrouted IP addresses within the range of addresses from 10.110.210.2 to 10.110.210.254. This was developed to allow for a quick configuration of a private MP-X/RP-C network.

The AS-P/B DHCP server can be disabled and another DHCP server can be used.

Here is a list of other questions and answers that may come up based on typical options in other DHCP servers:

  • Can the scope of the IP range be configured?
    There is no way to configure or limit the range of the standard IP address range or to have multiple scopes.
  • Can IP exceptions be configured?
    There is no configuration option to prevent the AS-P/B DHCP server from assigning a specific IP address. The AS-P/B DHCP server is unaware of static IP addresses, so if a switch or other device has a static IP set in the 10.110.210.2 to 10.110.210.254 range, you run the risk of having the AS-P/B DHCP server assign an IP address twice which can cause a number of issues.
  • Can a Default gateway be configured?
    Not configurable
  • Can a Subnet mask be configured?
    Not configurable
  • Is IP6 supported?
    No
  • Can lease types be configured?
    No
  • Can multiple DHCP servers be installed on the private LAN?
    No
  • Should MP-X/RP-C IP level devices only be hosted within the private AS-P/B network?
    Most site IT departments prefer that the BAS networks be isolated, however, if the network switch (Not the AS-P/B) is used for assigning DHCP IP addresses, it could hand out addresses to the AS-P/B and the MP-X/RP-C devices if they are on the same subnet.
    A managed (RSTP Enabled) switch can reside as a client to the AS-P/B. This is due to how the Private DHCP option is advertised. On-site IT departments may not want the switch on the customer's LAN so it is placed in the private AS-P/B network.
  • Does the AS-P/B DHCP server assign addresses to 3rd party devices?
    Yes, if the 3rd party device supports this. This would be a configurable option in the device.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • AlanWood20
  • as-b
  • DavidShore21
  • DHCP Server
  • mp-x
Was this article helpful? Yes No
88% helpful (7/8)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore