Issue
Bindings made under the Infinet interface using Import/Export system (IE) stop updating.
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Automation Server Premium
- Continuum i2920 Controller
Cause
Objects under the Infinet interface sometimes lose their Object IDs for reasons that are not yet fully understood.
The issue has been seen during up revision of the AS-P from 1.9x to 3.x
Resolution
Under the Infinet interface, right-click on the Application folder of the AS-P or Infinet device and select "Resolve object ids"
The system automatically re-assigns the missing ids
Download applicable i2 devices