Script program incorrectly calculates time differential
  • Script program incorrectly calculates time differential
  • RandyDavis
    RandyDavis
  • JohnBoehmer
    JohnBoehmer
JohnBoehmer Schneider Alumni (Retired)
‎2021-03-04 05:47 AM
on ‎2021-03-04 05:47 AM
A script program uses a calculation of the difference between event marker DateTime and the current time to trigger an alarm flag.
The alarm flag is initially set correctly but switches off again after 2147 seconds.
Building Operation Automation Server Premium Version 3.2.2
The result of the calculation Current Time - FailureTime returns a correct value until the difference exceeds 2147 seconds.
At that point the calculation returns a negative value and begins counting upward toward zero.
The Script program was broken.
Once the program was deleted and reimported the same script code consistently calculated an increased time differential.
This behaviour is identical to a defect which was fixed in the EBO 3.0.4 release.  In that case it was the controller rather than the program that was at fault.
Tags (5)
  • datetime
  • JohnBoehmer21
  • script
  • Time calculation
  • Time differential