Number of COV subscriptions supported by an RP-C
  • Number of COV subscriptions supported by an RP-C
  • RandyDavis
    RandyDavis
  • Jonas_Brissman
    Jonas_Brissman
Janeway Jonas_Brissman Janeway
‎2021-02-01 12:04 PM
on ‎2021-02-01 12:04 PM
What is the limitation on the number of COV subscriptions an RP-C can handle?
Building Operation Room Controller (RPC)
When setting up a binding to an RP-C to read a value from another device or transfer a value in the RP-C to another device COV subscriptions are often used.
The number of subscriptions an RP-C can support is limited primarily by the available resources of the controller.
An RP-C with a single point can support thousands of subscriptions but that’s not a realistic configuration on a live site. If resources were allocated to support a defined number of COV subscriptions, this would lock down those resources (primarily memory), making less room for other applications.
Since the maximum number of subscriptions depends on how many available resources the controller has at the moment when a subscription is made, there is no guaranteed number on how many subscriptions an RP-C can support.