Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 45
    • 46
    • 47
    • …
    • 508
  • Next »

Double feature values for Entitlements

Issue Sometimes the availability count for license features are displayed as double the actual available count for Entitlements. The problem has no functional effect on the system other than that the visual indication of the feature count is wrong. Issue seen in Entitlement View - Features inside a License Product are doubled. Issue seen in Server View. -The issue can be seen temporarily during activation on the server line. -The number of features inside the License Products available for activation under the server are doubled permanently. Server line view after activation. - After the license product has been activated the features on the server are shown correctly. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium (AS-P) Secure Boot Building Operation Automation Server Bundled (AS-B) Scalable Cause AS-P Classic and AS-B Classic licenses are NOT affected. None of the Windows licenses are affected.   EBO releases affected: All EBO versions up to and including 4.0.3. The EBO systems that are already running licenses are Not affected. Customers that for any reason reinstall an Entitlement in DA will be affected by the issue. EBO 5.0.1 Resolution This issue is planed to be resolved in the following EBO versions: EBO 4.0.4 EBO 5.0.2
View full article
Janeway Jonas_Brissman Janeway
‎2023-01-25 03:50 AM

Last Updated: Janeway PeterEdvik Janeway ‎2023-01-25 04:17 AM

Labels:
  • EcoStruxure Building Operation
822 Views

1.8 kOhm thermistor on the RTD-16 I/O module

Issue Is it possible to use a TAC Xenta 1.8 kOhm thermistor on an RTD-16 Central I/O module? Product Line EcoStruxure Building Operation. Environment Building Operation I/O Module 16 Ch RTD Cause Wants to use existing modules instead of adding new modules. Resolution The RTD-16 module is designed to interface with linear resistive inputs such as PT100, PT1000. Thermistors generally have logarithmic scales, therefore it will be hard to program a correct curve function to get an acceptable sensor accuracy. Using a universal input that is made for thermistor readings will give a more accurate reading without additional programming.
View full article
Kirk MikaelKrantz Kirk
‎2023-01-18 04:51 PM

Last Updated: Administrator CraigEl Administrator ‎2023-01-18 04:54 PM

Labels:
  • EcoStruxure Building Operation
959 Views

Controlling command priorities with Continuum workstation programs or Infinity controller programs.

Issue What is required to control command priorities in 3rd party controllers using Plain English? Product Line Andover Continuum Environment Continuum Cyberstation BACnet Controller (BCX, B4920, B3) BACnet command priority Plain English Cause Need to understand how to control command priorities and point values with Continuum workstation programs or controller infinity programs. Resolution Command Priority is a BACnet mechanism to decide the control hierarchy of a point, with 1 being the highest priority and 16 being the lowest.  Consider the following:   Default setting for a workstation program priority level is ManualOperator priority 8 Programs located in the workstation default command priorities can be controlled through Bacnet Preferences Controller InfinityPrograms will need to use the WriteProperty function to set a different priority other than priority 10 To relinquish a priority level use Relinquish(pointname, priority level)   The WriteProperty function is written in the format: WriteProperty (object_name, value, priority, index) object_name  Includes a full pathname, followed by a property name. The object identifier and property identifier are combined as one argument value   This actual value to which the property is set. This is optional.  If it is not present, then the next argument, priority, must be present to perform a Relinquish command.  (See the example in Relinquish.)  priority  The priority  number, ranging from 1 (highest) to 16 (lowest).This is optional.  It applies only to a set commandable property.  For controllers:  If it is not present, priority 10, if applicable, is used.  For CyberStation: The value, based on the priority in the BACnet Preferences dialog, is used.  index  This is optional.  It applies only to an array-type BACnet property.  The index is ignored whenever it is not applicable.   Infinity controller samples: This line will write the value of 22 to priority 10 BACnetDevices\BNet_4444\B3_885\B3Num1 = 22 This line will write the value of 33 to priority level 4 WriteProperty(BACnetDevices\BNet_4444\B3_885\B3Num1, 33 , 4 ) This line will relinquish the value for priority level 4 setting the value back to NULL Relinquish(BACnetDevices\BNet_4444\B3_885\B3Num1 , 4 )
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Last Updated: Sisko GavinHe Sisko ‎2023-01-13 02:23 AM

Labels:
  • Andover Continuum
2148 Views

Modbus/IP and BACnet/IP on AS-P Ethernet Port 2

Issue Is it possible to use both Modbus/IP and BACnet/IP on the same AS-P Ethernet Port 2? Product Line EcoStruxure Building Operation. Environment Building Operation Automation Server Premium Cause There is a need to have both Modbus TCP as well as BACnet/IP devices on the same AS-P secondary Ethernet port. Resolution This is not a common configuration so it has not been tested extensively. With regards to the architectural guidelines, consider the Modbus/IP as BACnet/IP devices. For example, where the maximum number of SpaceLogic BACnet/IP devices per private IP field-bus is 200, adjust this limit to 190 if you have 10 Modbus/IP devices on the secondary Ethernet port.
View full article
Kirk MikaelKrantz Kirk
‎2023-01-16 11:37 PM

Labels:
  • EcoStruxure Building Operation
3992 Views

Max network length when using daisy chain MP-C devices

Issue When connecting MP-C controllers in a daisy chain, do they act as a repeater and boost the signal thus allowing total network distances of greater than 90 meters. Product Line EcoStruxure Building Operation. Environment Building Operation Multi-purpose Controller. Cause Each MP-C acts as a switch and decodes and generates a new fresh packet. Resolution Maximum 100 meters between each device when using daisy chain when connecting MP-C.
View full article
Kirk MikaelKrantz Kirk
‎2023-01-16 04:57 AM

Labels:
  • EcoStruxure Building Operation
1386 Views

Ensuring the SSL Host Certificate and key file are a matching pair

Issue After configuring SSL certificates manually, having an incompatible Host Certificate and Key file can cause the import to EBO to fail. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Central Building Operation Enterprise Server Building Operation Automation Server Cause Host Certificate provides the public key for which the private key is paired. An unmatched Host Certificate and private key will cause the certificate import to fail. Resolution While managing certificates manually, it is recommended to check that the Host Certificate and Key files are a matching pair.   Using the provided Host Certificate (.pem) file and private key (.key or .prv) file Download OpenSSL v1.1.1 Light choosing the EXE file type and correct version (Win64 or Win32), as the latest version letter will be posted to Win32/Win64 OpenSSL Installer for Windows - Shining Light Productions (slproweb.com) or OpenSSL installed with EBO If using Shining Light installer, it is recommended to open command prompt from where certificates are stored on the desktop and substitute openssl with "C:\Program Files\OpenSSL-Win64\bin\openssl.exe". Working with certificate files on the Windows desktop ensures the user will have the correct permission to run the commands, unlike putting certificate files in the Program Files directory where openssl.exe resides. Open PowerShell or Command Prompt Obtain the host certificate md5 hash with this command: openssl x509 -noout -modulus -in filename.pem | openssl md5 Obtain the private key md5 hash using the command below. Use the correct command based on the key file file type openssl rsa -noout -modulus -in filename.prv | openssl md5 openssl rsa -noout -modulus -in filename.key | openssl md5   In this example, the Host Certificate is HostCert.pem and the private key is EcoStruxure.key. The private key was converted to EcoStructure.prv using Step 12 of Installing an SSL Certificate from an External CA - Communities (se.com) These commands make the hash more readable to human eye. We use openssl to inspect the x509 for Certificate and encryption type rsa for the key to produce the modulus (-modulus), which is a long string. You then use (-noout) to prevent the full modulus from printing to the screen. You then create a shorter md5 hash so the human eye can easily compare them. If the md5 hashes match, that indicates that the modulus is a match and proves that the certificate/key is a pair.
View full article
Picard David_Purser Picard
‎2022-12-02 09:46 AM

Labels:
  • EcoStruxure Building Operation
2762 Views

Forcing deletion of personnel objects

Issue By design, the Continuum system cannot delete personnel objects until all the distributed copies can be first removed from the controller(s). In some cases the distributed copies cannot be removed from the controllers, such as when a controller is permanently offline or has been deleted. Product Line Andover Continuum Environment CyberStation Cause Communication failure between CyberStation and controllers. Resolution Starting in CyberStation version 1.94 a new feature has been added that allows the user to force a delete of personnel objects even if the distributed copies cannot be removed. In CyberStation 'Delay Distribution' dialog, a new button has been added; the button is only enabled when CyberStation is in offline edit mode. Make a backup of the Continuum database as a precaution. Close ALL CyberStation workstations. Put CyberStation in Offline edit mode to enable the 'Clean up failed personnel delete distribution' button Click on the button, the system will provide the following warning Click OK to force all personnel deletions that are pending or have failed distribution to complete; any distributed copies in the controllers will be left orphaned. If offline controller returns online orphan distributed personnel records in controller can be removed by one of the following methods: Cool start the controller.  (For controllers that support access control and backup to flash such as the CX9680, ACX5720, ACX5740 . Note that personnel objects ARE NOT saved to flash memory, the controller requests a personnel distribution from CyberStation on cool start). See Restart modes of the second generation Infinity controllers for more information on cool start. Reload the controller from the CyberStation, this will perform a cold start and re-send all objects to the controller followed by a personnel distribution.
View full article
Picard Product_Support
‎2018-09-10 11:20 AM

Last Updated: Admiral Alan_Wood Admiral ‎2023-01-11 10:54 AM

Labels:
  • Andover Continuum
3262 Views

Guidelines for combining multiple Continuum databases into one.

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue How to combine multiple Continuum DBs into one DB Product Line Andover Continuum Environment Continuum Cyberstation Cause Multiple Continuum site databases need to be combined into a single site database Resolution Guideline for combining Multiple sites to one Database Executing this procedure requires a technician who thoroughly understands Continuum and how it works with SQL Server. This procedure does not encompass BACnet controllers. There is a multitude of decisions related to efficiencies and site preferences that are not documented here. The following procedure is intended for use as a guideline for combining multiple databases. This work must be done offline on a development database and validated on a test bench before Note:Before proceeding with this procedure you must do the following. Backup the Continuum database in SQL. Backup all the files and folder structure under New Graphic Files. Note that these files may be on the SQL Server or elsewhere on a mapped drive. Back all Cyberstation Profiles. Steps 1 – 11 must be done before any of the site exports are done. Preparation All sites must have the same revision software and CX firmware. NO EXCEPTIONS! Make sure that all the Alarm Enrollments and Event Notifications have unique names between all sites as these will wind up together in a single database. Make sure that all the Graphics in the Root directory have unique names between all sites. Make sure each Schedules in the Root directory has a unique name across all sites. Make sure each Custom ListViews in the Root directory has a unique name across all sites. Make sure each Groups in the Root directory has a unique name across all sites. Make sure each Reports in the Root directory has a unique name across all sites. Once steps 1-5 are completed, export each class in the root individually. Import files from step 6 into the new site The Local Site name on all the sites that will be combined must be named LocalSite. All workstations must have unique names and ACC IDs between the sites. All CX, ACX and BCX controllers must have unique names and ACC IDs between the sites. Note: The safest way to do steps 9 & 10 is to create a new controller in offline mode with the changed ID, then drag and drop copy from the original controller to the new controller. Panels, reports, and programs then must be edited to bind to the new controller. Another way to merge the panel, reports, and programs that are in the root is to copy all the panels, programs, and reports to their corresponding controller then export the controller. Doing this will keep all the bindings linked. Then once the controller is imported into the merged database they can be copied back up to the root. All Commports on all controllers and workstations must be named Comm1, Comm2, etc… Each site must have the default “ACC” user and password. All graphic files (.pin) under the New Graphic Files folder must have unique names between the sites. Merging the databases Install a standard multi-user Continuum system being sure to size the database big enough to accept all the other databases combined into one database.  After a clean installation is done, shut down the new workstation and the SQL server. Copy the empty database files to an area where they won’t get corrupted. Do a complete site export from each of the sites that will be combined. Back up all the Graphic files (.Pin) files from the site so that they can be transferred to the new server. Copy all the backed up Graphic files (.Pin) from each site onto a New Graphics Files folder in the location of choice. Note these files can reside on the SQL server or elsewhere on a mapped drive. Import each of the site text exports from the old systems into the new system. After each import check to make sure that each import went cleanly. Check all the Graphics, Programs, Alarm Enrollments, and Event Notifications to make sure that all the links were made during the import process.
View full article
Picard Product_Support
‎2018-09-07 01:49 PM

Last Updated: Administrator CraigEl Administrator ‎2023-01-11 07:34 PM

Labels:
  • Andover Continuum
819 Views

Configure the Flexnet License Administrator web portal to use HTTPS

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue Cybersecurity vulnerability scans are flagging the Building Operation License Server because it is using HTTP rather than HTTPS Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation License Server Cause The Building Operation License Server contains a web portal for diagnostics and administration. By default, the Building Operation License Server Administration web portal is configured to use HTTP Resolution It is possible from the Administration area of the Building Operation License Server Administration web portal to configure HTTPS communications. Note: this does not change how Ecostruxure Building Operation connects to the license server.   The following process configures the Building Operation License Server Administration web portal to use HTTPS   From a web browser open the Building Operation License Server Administration web portal by typing http://localhost:8888 Once the web portal opens, select Administration at the top right. You will be prompted to log on, use "admin" as the user name. If you have logged in before, use the password you have defined. If not, enter "admin" as the password, and you will then be prompted to create a password. Once signed in Select the Server Configuration tab. Under the Secure Web Server Configuration section, select Enable HTTPS Change HTTPS Port to a unique number e.g. 8443 Select Redirect Non-Secure Web Access to Secure Web Access At the bottom of the page click the Save button and close the web browser tab. Restart the Building Operation X.X License Server from the Windows Services app (services.msc) If the license server is opened using http://localhost:8888 it will now redirect to HTTPS using the port specified in step 4 above
View full article
Administrator CraigEl Administrator
‎2023-01-11 04:50 PM

on ‎2023-01-11 04:50 PM

Labels:
  • EcoStruxure Building Operation
3073 Views

Does EBO 2022 support multi-verson for AS classic (part number - SXWAUTSVR10001)?

Issue How can I find out whether the EBO 2022 multi-version support applies to AS Classic module?  Does it apply to all the AS, AS-P, and AS-B modules? Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Cause The EBO 2022 Release Note describes that the EBO 2022 Device Administrator software is not supported on the original AS classic (part number SXWAUTSVR10001) but there is no description of the software backward compatibility of the EBO on AS classic. Resolution An AS classic can continue to exist in a multi-version system; the maximum version an AS classic can operate at is 3.1.2. It is nowhere implied that it is not supported under a multi-version setup. The statement “EBO 2022 does not support AS classic” in the EBO 2022 Release Note is misunderstood. It simply means that one cannot install EBO 2022 on an AS Classic, the same as the previous EBO 3.2 version. Note that the AS Classic will not inherit any features introduced in later EBO releases when operating in a multi-version system.
View full article
Lieutenant | EcoXpert Master SangKim Lieutenant | EcoXpert Master
‎2023-01-09 04:11 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2023-01-10 03:42 PM

Labels:
  • EcoStruxure Building Operation
2186 Views

Enterprise Server Backup Failed - File is Corrupt

Issue When performing a backup of all Servers and All Data on an Enterprise Server the backup fails and generates an error in Software Administrator indicating the backup is corrupt although the backup is not corrupt. Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Workstation EcoStruxure Building Operation Enterprise Server Cause There is not enough free disk space on the Enterprise Server to save the backup file created.  The error generated in Software Administrator is a generic error. Resolution Check the Trace Log for Internal Server Error: Insufficient_Space_For_Backup If this is evident free up additional space on the Enterprise Server and re-try saving the backup.
View full article
Sisko GavinHe Sisko
‎2023-01-09 04:33 PM

on ‎2023-01-09 04:33 PM

Labels:
  • EcoStruxure Building Operation
911 Views

SP-ACX on board inputs randomly activate/open on their own

Issue One or more inputs on the SP-ACX will randomly report as open for a brief moment (a second or less), This can result in unauthorized door access if for example the input is associated with a door Exit Request. Product Line EcoStruxure Security Expert Environment SP-ACX Cause Electrical noise in wiring Resolution Increase the Alarm input speed, issue has been seen with Alarm input speed set to 0, increasing the input speed to 1 second typically resolves the problem.
View full article
Captain AbeMeran Captain
‎2023-01-09 04:30 PM

on ‎2023-01-09 04:30 PM

Labels:
  • EcoStruxure Security Expert
907 Views

WebRequest malfunction after upgrading to EBO 2022

Issue A system with multiple WebRequest calls appears to become erratic after upgrading the AS-P to EBO 2022 and above. After a reboot, multiple scripts execution are hanging.   In previous EBO versions, the script would be stopped and return an Unknown Exception error message.   Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Enterprise Server Cause The Architectural Guidelines always recommended a maximum of 5 concurrent WebRequest calls. In EBO 2022, this limitation is enforced to limit the impact on the system resources and prevent scripts stopping due to Unknown Exception errors.   Architectural Guidelines    Web requests exceeding this number will be queued, and the scripts doing these calls will hang on that function as the queue is emptied. This will directly impact the execution of other scripts.   Resolution 1. Enforce a good scripting practice to prevent more than 5 concurrent Web Request calls. 2. Cascade the execution of scripts to make sure that after a reboot, the scripts are executed in a sequence to prevent simultaneous calls filling the queue and causing scripts to be stopped.  
View full article
Ensign PierreOlivierJean Ensign
‎2023-01-09 04:17 PM

on ‎2023-01-09 04:17 PM

Labels:
  • EcoStruxure Building Operation
611 Views

Disable a program from another program with Script

Issue At times it is necessary to programmatically disable a program from another program Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Workstation EcoStruxure Building Operation Server (ES/ASP/ASB) Cause A program will not just stop another program without some additional steps. In Continuum there was an ability to just name another program stop it. Resolution A program can stop itself,  however, here is a way for one program to stop another program. The user can declare an input variable in a program, check it and stop the program, based on the value of that variable. That input variable would be set from outside the program. Example: Prog1 stops Prog2 ======================== ‘Prog1 Numeric Output OutStopProg    ‘bound to the input variable InStopProg of prog2 ‘Stop program Prog2 OutStopProg = true        ‘this statement sets the input variable InStopProg  of Prog2 to true ======================== ‘Prog2 Numeric Input InStopProg     ‘bound to the OutStopProg variable of Prog1 If InStopProg = true then Stop   ‘this statement stops prog2 if InStopProg  is true  
View full article
Picard Product_Support
‎2018-09-06 09:51 AM

Last Updated: Sisko GavinHe Sisko ‎2022-12-06 02:00 AM

Labels:
  • EcoStruxure Building Operation
1359 Views

Holidays in Access Expert

Issue A site configured a schedule to have 2 different holiday durations during a spring break holiday week. The schedule is not working as expected. The Holiday week is set up as a range for Monday - Friday and assigned to a single Holiday group.   Two new schedule durations have been added with the respective days selected that they would like the durations to activate on. On the 2 new durations, they added the Holiday group in the "Always Active On" area.   Product Line EcoStruxure Access Expert Environment Access Expert V3 Hosted Access Expert V3 Premise Cause Holiday and special date durations will activate on the holiday dates regardless of the day(s) of the week selected in the scheduled duration. The day(s) of week checkboxes in each duration is only used for setting a recurring weekly activation on those days and are not required for Holidays. For durations that will only be used during holidays, do not select any day(s) of the week. Resolution In this case, since you need two different durations during your holiday week, you will need two new durations but with different holiday groups for each duration. Set the M, W, and F duration as holiday group A and T, R for holiday group B. Now apply the Holiday Groups to the right dates via the Holidays Menu.      
View full article
Commander JonGreen Commander
‎2022-12-29 09:26 AM

on ‎2022-12-29 09:26 AM

Labels:
  • EcoStruxure Access Expert
2075 Views

Creating a report of visitors using the Visitor Management System

Issue When configuring the in-built Visitor Management System (VMS) there is no report mechanism under the Visitor tab to show visitor access. Product Line EcoStruxure Security Expert Environment Security Expert Client Visitor Management System Cause Reports for visitors are part of the list of the Report types under the more general User reports Resolution Visitor reports for visitors using the in-built VMS can be generated with a User Report by selecting one of the following Report Type options: All current visitors All overdue visitors All visitors by date Visitor user report setup This can then be further configured to your requirements by editing the report filter. Launch the event report view in a new window by pressing the Edit in report view button. The report can be run and filters can then be configured as required and saved as the default report filter.
View full article
Kirk AdamSteele Kirk
‎2022-12-22 07:40 PM

on ‎2022-12-22 07:40 PM

Labels:
  • EcoStruxure Security Expert
1374 Views

Security Expert: Updating site: Preferred order of installation

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue What is the best order to update software and firmware from very outdated sites? Should we update the controller's firmware or Security Expert client/Server software first? Product Line EcoStruxure Security Expert Environment Security Expert Controller Cause Controller, firmware, Client, Server, Software Resolution Update the controller's OS to 2.0.27 Then update the controller's firmware to the "interim-build" v2.08.1287 Then update to release build 2.08.1295. Firmware is located on the EcoExpert Extranet  There is no importance of installation order between controller firmware and Client/Server software
View full article
Lieutenant JG JamesMorgan Lieutenant JG
‎2022-12-13 08:52 AM

Last Updated: Kirk AdamSteele Kirk ‎2022-12-21 04:16 AM

Labels:
  • EcoStruxure Security Expert
1089 Views

EBO WorkStation freezes and crashes

Issue Building Operation WorkStation freezes and crashes. The stack trace shows: System.ComponentModel.Win32Exception: Not enough quota is available to process this command Product Line EcoStruxure Building Operation Environment Building Operation WorkStation Cause This is an error from Windows system: Not enough quota is available to process this command There are two potential causes for this error: Windows does not have enough virtual memory for all of the processes that are currently running on the machine or Windows is running out of other resources such as: disk space, handles, GDI resources, process message queue or something else. This error turns up on a lot of programs in Windows intermittently, such as Windows File Explorer. WorkStation freezes (usually because its waiting on the server) and the user tries to do a 'soft' shutdown (not a kill process) of WorkStation in the Task Manager. The Windows OS then sends instructions via the message queue (to simulate a user press on the "red cross" button on upper right in caption bar) which in turn leads to this quota error. Resolution If this error is seen, Microsoft recommends closing some applications and trying again. If you still get this message, increase the size of your paging file.   In the Taskbar Search, type “Advanced System“. You will see View Advanced System Settings. Click on it. Or you can navigate to it via Control Panel In System Properties, click the Advanced tab In the Performance section click the Settings button Performance Options will open. Click the Advanced tab Here, under Virtual memory, select Change Uncheck Automatically manage paging file size for all drives Highlight your Windows system drive Select Custom size Change the Initial size value and the Maximum size value to a higher value Click Set Finally, Click Apply/OK all the way  
View full article
Administrator CraigEl Administrator
‎2022-12-20 04:12 PM

on ‎2022-12-20 04:12 PM

Labels:
  • EcoStruxure Building Operation
1947 Views

No more threads can be created error.

Issue TAC Vista reports an error in the Alarm view that no more threads can be created and remote workstations cannot connect to the Vista server. Product Line TAC Vista Environment TAC Vista Workstation Cause This issue occurs when the TAC Vista remote computer that connects to the TAC Vista Server computer is left logged in and the Remote computer goes into hibernation. This causes the TCP/IP Thread between the TAC Vista remote computer and the TAC Vista server PC's to remain in use. Then once the TAC Vista remote computer is taken out of hibernation another TCP/IP Thread is created. Eventually this will use up the allocated thread count and generate an error. Resolution Restarting the TAC Vista Server PC will fix the issue until the TCP/IP Thread count increase to the limit again. The TAC Vista Remote Workstation computer can be setup so it doesn't go into hibernation and remains on, then the TAC Vista log off function works correctly and closes down the TCP/IP Thread. Alternatively change the TAC Vista Remote Workstations to TAC Vista Servers and configure them to look at the mastern TAC Vista server. This configuration uses a different communication setup for Server to Server communications. See the Creating TAC Vista multi-server network Knowledge Base article for further information on this configuration
View full article
Spock PeterLarsen Spock
‎2022-12-19 05:59 PM

on ‎2022-12-19 05:59 PM

Labels:
  • TAC Vista
1153 Views

Bypassing and Clearing the Bypass of Inputs and Trouble Inputs on Security Expert Keypad

Issue There are some differences between Bypassing/Clearing the Bypasses of Inputs and Trouble Inputs when Arming Security Expert Areas Product Line EcoStruxure Security Expert Environment Security Expert Controller Security Expert Keypad Arming Areas Cause Both Inputs and Trouble Inputs can be easily Bypassed when attempting to Arm an Area in Security Expert.  However, while Input Bypasses can also be cleared from the Keypad, Bypasses of Trouble Inputs cannot. Resolution The Bypassing and Clearing of Bypasses on Inputs can be carried out from the keypad.  However, whilst a Trouble Input can be Bypassed from the keypad the Bypass can only be cleared by restarting the controller from the web interface.   The following video will illustrate how to: Bypass and Clear the Bypass on an Input via the keypad Bypass a Trouble Input via the keypad Clear the Trouble Input Bypass via the Web Interface  
View full article
Admiral David_Kendrick Admiral
‎2022-12-19 03:11 AM

on ‎2022-12-19 03:11 AM

Labels:
  • EcoStruxure Security Expert
1096 Views
  • « Previous
    • 1
    • …
    • 45
    • 46
    • 47
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login