How to add a calibration factor or offset value to an input using automatic scaling.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to add a calibration factor or offset value to an input using automatic scaling.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • AdamSteele
    AdamSteele
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2406 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to add a calibration factor or offset value to an input using automatic scaling.

Picard Product_Support
‎2018-09-07 02:09 AM

Last Updated: Administrator CraigEl Administrator ‎2023-09-26 08:48 PM

Issue

How to add a calibration factor or offset value to an input using automatic scaling.

Product Line

Andover Continuum

Environment

Continuum Universal Input

Cause

If using the Conversion field to offset the ElecValue on an input that is using an automatic scale, the resulting value will not be calculated properly.

Resolution

For this to function with an input using an automatic scale we need to setup an InfinityFunction to do the scaling for us and then add/subtract our offset from this result.

 

1. Create a new InfinityFunction in the controller called “IPConvert”

2. Paste the below code (between the lines) into the function and save it.


========
'This InfinityFunction must be called from the conversion line of the input
'This InfinityFunction will allow an offset to be applied to a universal input

'Example Conversion line in the Input - IPConvert(EngScaleTop, ElecScaleTop, EngScaleBot, ElecScaleBot, -1)

Arg 1 EngTop 'Engineering Units -  Top of Scale
Arg 2 VltTop 'Voltage -  Top of Scale
Arg 3 EngBot 'Engineering Units -  Bottom of Scale
Arg 4 VltBot 'Voltage - Bottom of Scale
Arg 5 Offset 'Amount to Offset returned value

Numeric Slope, C

Slope = ((EngTop - EngBot) / (VltTop - VltBot))
C = EngBot + (Slope * (minimum(VltTop, maximum(ElecValue, VltBot)) - VltBot))
Return C + Offset
==========

3. Go to your inputs on that controller that need to use this function.

4. confirm that the auto conversion fields have been set to the scale range you require.

5. type the below into the conversion field, replacing the “-0” at the end with whatever offset is required.

IPConvert(EngScaleTop, ElecScaleTop, EngScaleBot, ElecScaleBot, -0)

Labels (1)
Labels:
  • Andover Continuum
Tags (5)
  • Find more articles tagged with:
  • 12458
  • airflow
  • CraigEllis23
  • humidity
  • pressure
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore