Can Plain English interact with the Continuum Alarm Engine?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Can Plain English interact with the Continuum Alarm Engine?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • David_Kendrick
    David_Kendrick
  • PaulFr
    PaulFr
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2482 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Can Plain English interact with the Continuum Alarm Engine?

Picard Product_Support
‎2018-09-10 11:14 AM

Last Updated: Admiral David_Kendrick Admiral ‎2023-10-06 07:07 AM

Issue

How to setup and use the Plain English Alarm function?

 

Product Line

Andover Continuum

 

Environment

  • PEAlmFunction, PERtnFunction
  • CyberStation Alarm
  • Workstation PE function

Cause

Manual configuration is required to create the Plain English alarm function and set certain registry keys.

 

Resolution

As a function of Continuum CyberStation Alarm Engine, user written Plain English functions are automatically invoked at a workstation

  • when an alarm occurs
  • when an alarm is acknowledged
  • when a return-to-normal condition occurs.

The user optionally specifies the names of those functions in the Windows registry, and they will be called appropriately.

Registry keys used for calling Plain English Alarm function

  • PEAlmFunction : The name of the user-defined PE Alarm Function. (Ex. “AlmProcess”)
  • PERtnfunction : The name of the user-defined PE Return-to-Normal Function. (Ex. ”AlmProcess”)

Example of the Plain English Alarm function is as follows:

Arg 1 A ' Network AliasName(16)
Arg 2 B ' Controller AliasName(16)
Arg 3 C ' Infinet Controller AliasName(16)
Arg 4 D ' Object name(32)
Arg 5 E ' Object AliasName(16)
Arg 6 F ' Object Description(32)
Arg 7 G ' Object Value(Numeric)
Arg 8 H ' Alarm State(3) ALM,RTN,ACK 
Arg 9 I ' Graphic Object AliasName(16) 
Arg 10 J ' Alarm Enrollment Alarm Message(String) 
Arg 11 K ' Alarm Enrollment AliasName(16)
Arg 12 L ' EventNotification AliasName(16)  
Arg 13 M ' EventNotification Priority (Numeric 1~255)
Arg 14 N ' TimeStamp(16)
Arg 15 O 'Logging Flag (1~255) 
'
String 1 Q
String 80 AlmDir, Fnam
File AlmF
'
If M < 100 then
  AlmDir = "C:\"
  Q = chr(96)
  Fnam = NumToStr(random(Second))
  OpenFile(AlmDir ; Fnam ; ".alm", WriteOnly, AlmF)
   Print L ;", " ; K ; ", " ; A , B , C , D , ", " ; G  to AlmF
  CloseFile(AlmF)
Endif
Return Success
  1. Create the following registry keys in HKEY_LOCAL_MACHINE\SOFTWARE\Andover Controls \Continuum\Settings:
    • PEAckFunction (REG_SZ)
    • PEAlmFunction (REG_SZ)
    • PERtnFunction (REG_SZ)
    • PEMaxBufferedAlarms (REG_DWORD)
    • PEPopAlarm (REG_DWORD)
  2. Set PEAlmFunction to “AlmProcess”
  3. Set PERtnFunction to “RtnProcess”
  4. Restart Continuum.
  5. Create PE programs in the workstation called AlmProcess, and RtnProcess with source code similar to the example function.
  6. Files will be created in the specified directory containing the alarm and return to normal information.
Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 7658
  • DavidKendrick23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore