Issue
Is there a recommended repeater for BACnet MSTP networks?
Product Line
TAC I/A Series
Environment
- R2 G3 (Niagara)
- MNB-1000
Cause
MSTP repeaters may be required to extend trunk length or provide isolation in the smoke purge application.
Resolution
Consider B-Links which were actually used on the MSTP trunk during UL 864 testing.
- B-LINK-AC-S (AC powered)
- B-LINK-DC-S (DC powered)