Upgrading Power Manager 1.0 to EcoStruxure Energy Expert 2.0 (PME 7.0 to PME 9.0)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Upgrading Power Manager 1.0 to EcoStruxure Energy Expert 2.0 (PME 7.0 to PME 9.0)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3760 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Upgrading Power Manager 1.0 to EcoStruxure Energy Expert 2.0 (PME 7.0 to PME 9.0)

Lieutenant JG Robert_Davis Lieutenant JG
‎2020-12-17 06:03 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:22 AM

Issue

When upgrading EcoStruxure Building Operation to version 2.0 or newer, the existing Power Manager software should also be upgraded to EcoStruxure Energy Expert to maintain compatibility

Product Line

EcoStruxure Building Operation

EcoStruxure Energy Expert

Environment

  • Power Monitoring Expert (PME)
  • Power Manager

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

The proper procedure is required when upgrading from older versions of Power Manager to the latest Energy Expert version. Guidance and best practices are needed for upgrading a PME server from PME 7.2 to PME 9.0.

Resolution

A Power Manager 1.0 site should be taken to 1.1 first, then upgraded to Energy Expert 2.0
Below are the recommendations for a side-by-side upgrade from PME 7.2 to PME 9.0:

On the old server:
  1. Run the PME_8.2.iso file to do an in-place upgrade from PME 7.2.3 to PME 8.2
  2. After completing that upgrade, the system will default to using a PME 8.2 trial license
  3. Install and run the PME 8.2 CM 2.1.0 Tool which will perform necessary actions for the side-by-side upgrade; we will use it to create a .zip file containing configuration components such as reports, dashboards, diagrams, users, devices, etc.
  4. Transfer this .zip file from the CM Tool to the new server
On the new server:
  1. Run the PME_8.2.iso file to install PME 8.2 (this can be done while the above steps are performed on the old server)
  2. After transferring the .zip file from the old server, install and run the PME 8.2 CM 2.1.0 Tool on the new server and have it load the archived data from the .zip file into the program, and then write it to the system (essentially performing a PME 8.2 server to server migration)
  3. After that finishes, we can run the PME_9.0.iso file to upgrade from PME 8.2 to PME 9.0
  4. After PME 9.0 is installed, we can activate the PME 9.0 license(s) in the Floating License Manager using the activation ID(s) that were already acquired, then remove the PME 9.0 trial license using License Manager (different from Floating License Manager)

Running into issues with the install? Receiving error messages related to PME? Check out the Technical FAQ for a solution to your problem. 

Links to relevant documentation and files:
  • Where can I find documentation for Power Monitoring Expert 8.2 (PME 8.2)?
  • Where can I download Power Monitoring Expert 8.2 installation files?
  • Where can I find documentation for Power Monitoring Expert 9.0 (PME 9.0)?
  • Where can I download Power Monitoring Expert 9 installation file?
  • PME 8.2 CM Tool Exchange Community post 
  • PME 9.0 CM Tool Exchange Community link
 
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • DavidKendrick20
  • RobertDavis19
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore