Issue
The Runtime tab of an Infinet controller editor shows the maximum number of 255 for both the Infinet Error Count (InfinetErrCount) and Reconfigs. What is the command to reset them to 0?
Product Line
Andover Continuum
Environment
- Infinet controller
- NetController (CX9200, CX9400, Cx9702, CX99xx)
- NetController II (CX9680)
- bCX9640
Cause
Having an unstable Infinet can cause both Infinet errors and Reconfigs to occur. An engineer may want to reset the Infinet Error Count (InfinetErrCount) and Reconfigs to 0 and check how fast they both reoccur.
Resolution
Either execute the command from the Command Line of Continuum Explorer or create an InfinityProgram in the CX controller to reset them as below:
* Set Comm2 Reconfigs = 0
* Set InfnetCtrlName InfinetErrCount = 0
NB Make sure the whole path is specified!!