Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,854
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 11
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 41
    • 42
    • 43
    • …
    • 509
  • Next »

Using Modbus Register Group to batch read registers

Issue Modbus Register Groups feature can overcome some Modbus communication problems. It has been seen before where the Modbus controller falls offline for a few seconds then comes back online. This cycle will repeat every few seconds. When register groups are not used, there may also be issues with the amount of time it takes for a Modbus points to update. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Enterprise Server Building Operation Automation Server Premium (AS-P) Building Operation Automation Server Bundled (AS-B) Cause In a normal Modbus network, a Modbus polling device obtains data from a polled device by sending a query message to the device and then waiting for the response message that contains the requested value from the selected register. If data from another register is required, the polling device sends out a new query message and awaits the response message. This process is repeated until all subscribed points values have been read. The Modbus Register Groups are a batch read function to poll Modbus devices. Instead of reading each register individually, the batch read function reads registers in manually created groups. When all registers in a group have been read, the response message returns subscribed register values for the whole group. Register grouping provides a dramatic saving in the time taken to poll your devices. For more guidance and tips on this topic, see Section "Batch Read Function" in the EcoStruxure Building Operation Technical Reference Guide.  Note: When viewing a graphic containing Modbus values, those values will update at the same interval as their Modbus register group. Resolution When grouping Modbus points, it is important to keep in mind some of the following points. Try to ensure that as many Modbus points as possible are contained in as few groups as possible. This will reduce the overall time it takes the Enterprise Server or Automation Server to read all the subscribed points in each Modbus device. Network performance can be enhanced by choosing the method of grouping that is most suitable for each device in the Modbus network.  Network performance can be enhanced by selecting a different default poll time for each register group. Network performance can also be enhanced by grouping points that have the same or similar polls. Start with higher group poll times to ensure a stable system before reducing the poll time. Make sure to delete Modbus points out of a register group individually before deleting the group. If this is not done, it can cause system delays. See article Modbus Batch Read Multiple Registers Groups Creating a Modbus Register Group In Workstation, in the System Tree pane, right-click on a Modbus device and select New Object (1).  In the create object window select Modbus Register Group (2), provide a name and select Create (3). Now that the group has been created, existing Modbus points can be dragged and dropped into the group. New Modbus points can also be created in the group.  Right-click on the Modbus Register Group and select New Object (1).  In the create object window expand Modbus Point (2), select a point type (3), provide a name and select Create (4).
View full article
Picard Product_Support
‎2018-09-11 04:22 AM

Last Updated: Sisko GavinHe Sisko ‎2023-03-31 03:35 AM

Labels:
  • EcoStruxure Building Operation
6300 Views

Unable to transfer values from third party device in a Cyberstation Program.

Issue A Cyberstation program will not transfer the value of an AnalogValue in a third party device to an AnalogValue point in Continuum. The Cyberstation program consistently errors out and disables. Product Line Andover Continuum Environment Continuum Cyberstation Cause Using a Cyberstation program to set the value of a point in a BCX controller to equal the value of a point in a third party device without an intermediate step. Resolution Create AnalogValues in the Cyberstation.  Point values should first be transferred from the third party device to the Cyberstation points.
View full article
Picard Product_Support
‎2018-09-06 09:56 AM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-31 11:14 AM

Labels:
  • Andover Continuum
1170 Views

Quickly delete 100,000 alarms and a lot of old trend data

Issue My Server has a 100,000 alarms and a lot of old trend data.  How can I delete them quickly? Product Line TAC IA Series Environment I/A Series R2 Niagara Cause The APP folder under the station holds all alarm and trended data.  When this folder gets too big, i.e. >500 MB the Server functionality can slow down while working with this large database file. Resolution Stop the Server station Rename the existing APP folder to something other than APP Restart the Server station.  When the Server station restarts it will check for the presence of a folder called APP and when none is found it will create a new one and use that one to archive alarms and trend data. 
View full article
Picard Product_Support
‎2018-09-06 12:42 PM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-31 11:29 AM

Labels:
  • TAC IA Series
1271 Views

Having a mix of Cyberstation versions on the same system

Issue Is it possible to have different software versions on the Cyberstation workstations? Product Line Andover Continuum Environment Continuum Cyberstation Cause When adding an extra workstation to a system does it have to match the version of existing workstations? Resolution All workstations on the same system must be exactly the same version including any service packs. This also includes Web Client servers. You will either need to install the same version as the rest of the system or upgrade all other workstations to the latest version, although this may need an upgrade of the security keys. Cyberstation software can be downloaded from The Exchange Download Center.  
View full article
Picard Product_Support
‎2018-09-09 09:46 PM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-31 10:53 AM

Labels:
  • Andover Continuum
1324 Views

Viconics VT7600x1000x exceeding the set 3 Cool Cycles Per Hour (CPH)

Issue Tested the Viconics VT7600x1000x for Cool CPH set to 3.  Manually heated the thermostat and let it cool to cycle the cool stages and it cycled on and off 7 times before stopping the test.  According to the documentation it should have stopped after 3 on/off cycles. Product Line Field Devices Environment SSL SE7000 Cause Cooling/heating has to be within 15-85% of the proportional band. Resolution With the Viconics VT7600x1000x series products, the CPH only works when the cooling/heating demand is within 15 to 85% of the proportional band. The thermostat has a 2 degree proportional band (fixed) so at a setpoint of 72 and CPH of 3 (cooling CPH adjustable 3-4), if the temperature stays between 72.3 and 73.7 the CPH is at 3. Outside of that band the cooling/heating is allowed to cycle as often as needed.
View full article
Picard Product_Support
‎2018-09-06 02:33 PM

Last Updated: Administrator CraigEl Administrator ‎2023-03-31 07:45 PM

Labels:
  • Field Devices
1169 Views

BACnet/IP port supported with EcoStruxure Building Operation

Issue BACnet/IP port supported with EcoStruxure Building Operation Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Edge Server - Standard Cause Which BACnet/IP ports are supported with EcoStruxure Building Operation, and can there be more than one port? Resolution By default, the BACnet/IP network uses UDP port 47808 (0xBAC0), this is adjustable higher or lower. The BACnet/IP network supports a single BACnet UDP port, Additional IP networks can be created in the BACnet system as long as each network has a unique identifier (network Id and name) and UDP/IP port number. Refer to: Creating an Additional BACnet IP Network (se.com) and Best Practices When Configuring BACnet IP Networks and BBMDs for EcoStruxure BMS Servers Please note that BACnet/IP uses UDP as its transmission protocol. For more information read the BACnet/IP basic design criteria.
View full article
Picard Product_Support
‎2018-09-10 12:44 PM

Last Updated: Administrator CraigEl Administrator ‎2023-03-31 07:41 PM

Labels:
  • EcoStruxure Building Operation
2880 Views

Can J Bus devices be used with an Automation Server?

Issue Will J-Bus operate with Modbus RTU devices on the same bus? Product Line EcoStruxure Building Operation  Environment Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause Compatibility of J Bus required. Resolution The J Bus protocol is supported by the Autimation Server, it runs on an RS485 network and uses a subset of the Modbus RTU protocol function codes. The J Bus devices addressing usually has an offset of 1 compared to the Modbus RTU standard, to apply this offset select "J-Bus Mode" = Yes in the Modbus Master Network Properties.   Verify that the devices to be used have a standard RS485 electrical connection and do not require any special electrical biasing, also ensure that all units connected on the bus have a unique ID/ address number. If this is the case then you should be able to connect both Modbus RTU and J Bus devices on the same Automation Server port connection but in the Modbus Master Network select the J Bus Mode setting to No. In J-Bus mode, the Automation Server will automatically reduce the polled register addresses by one, so if the AS is set to Modbus mode, you may need to manually set the register addresses of any J-Bus devices by minus one. With J Bus as with Modbus sometimes the point addressing needs to be offset by +1 or -1, but check with the 3rd party device supplier/ documentation to determine its specific point addressing requirements.  
View full article
Picard Product_Support
‎2018-09-11 03:56 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2023-03-30 01:37 AM

Labels:
  • EcoStruxure Building Operation
3253 Views

Imported BACnet/IP device does not communicate

Issue Import of BACnet/IP device is missing Device ID value. The device is indicated as offline and will not communicate. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Edge Server - Standard Cause A device instance number is not preserved in an export. An imported BACnet device must be associated with a device.  Resolution Use the Associate with Device option on the BACnet/IP device object, refer to: Associating a BACnet Instance Number with a Device (se.com). Specify the device instance number.
View full article
Picard Product_Support
‎2018-09-07 08:56 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2023-03-30 02:32 AM

Labels:
  • EcoStruxure Building Operation
1767 Views

Setting default BACnet priority levels in EcoStruxure Building Operation

Issue Setting the default BACnet priority levels for different applications avoids priority conflicts by normalizing which priority gets used for a specific action or within a specific application Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Edge Server - Standard Cause Different EcoStruxure applications may act upon BACnet objects utilizing different BACnet priority levels. This may cause confusion and can keep the system from operating as expected. Resolution BACnet objects created with EBO (1.4 and higher) will have a default BACnet Priority of 16 unless specified otherwise. The default BACnet Priority can be changed to the customer's needs.   As a best practice, define the Default priority level prior to configuring the system. In addition, consider maintaining the same default priority level for multiple active systems at your site. For example, configure the same default priority level for the EcoStruxure Building Operation and fire protection system. In a multi-server system, you can only configure the Default priority level from the Interface Manager of the Enterprise Server. If you set a new priority level, the system propagates the change to the other automation servers in the network. Refer to: Default Priority Level (se.com) and Configuring the Default Priority Level (se.com)  
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2023-03-30 02:52 AM

Labels:
  • EcoStruxure Building Operation
1754 Views

TGML Graphics Editor Error: Could not load file or assembly vjslib

Issue Error: "Could not load file or assembly 'vjslib, Version=2.0.0.0, Culture=neutral, PublicKeyToken=b03f5f7f11d50a3a' or one of its dependencies. The system cannot find the file specified." when starting TGML editor    Can not start TGML editor. Product Line TAC Vista Environment TAC Graphics TGML editor Cause TGML editor needs Microsoft Visual J#® 2.0 Redistributable Package to be installed on the machine for the TGML editor to run. If this for some reason is missing it needs to be installed. Resolution Go to the following link http://www.microsoft.com/downloads/en/confirmation.aspx?FamilyID=e9d87f37-2adc-4c32-95b3-b5e3a21bab2c Download and install the program
View full article
Picard Product_Support
‎2018-09-09 09:44 PM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-30 12:48 PM

Labels:
  • TAC Vista
2094 Views

Is there a touch-screen display that can be used to display BACnet objects directly from other I/A Series BACnet controllers?

Issue Customer wants a customizable permanently installed touch-screen display instead of a computer and web based graphics for display of points from their network of I/A Series BACnet controllers.  They would like to accomplish this without having to create shadow objects in a UNC or ENC. Product Line TAC IA Series Environment I/A Series MNB family of controllers Optional ENC or UNC Cause Customer does not want to deploy computers that would be easily stolen but instead wants to have permanently installed touch-screen displays. Resolution The LoyTec LVIS-ME212 or LVIS-ME215 touch panels can be directly connected to any BACnet-IP or BACnet-MS/TP network and can be linked to any BACnet object on the interconnected BACnet networks including those objects accessible over attached BACnet routers such as an ENC or MNB-1000. Available through the Schneider Electric iPortal online ordering system as LOY-LVIS-ME212 and LOY-LVIS-ME215  
View full article
Picard Product_Support
‎2018-09-06 01:41 PM

Last Updated: Administrator CraigEl Administrator ‎2023-03-30 05:58 PM

Labels:
  • TAC IA Series
2182 Views

A floating-point value is displayed incorrectly in a TGML graphic.

Issue A floating-point value is displayed incorrectly in a TGML graphic. The presentation field appears to show random numbers. The example shows how the value 11.60 is represented in a TGML graphic. 11.60 is actually stored as 11.600000381469727. In format presentation mode: In none presentation mode: The last 6 digits of the stored floating-point value are seen! Product Line TAC Vista Environment TAC Vista 5.1.X TGML editor 5.1.X A presentation text bound to a floating-point value. Cause Vista uses the PC's default settings for number of decimals, when presenting values in TGML graphics. Resolution To resolve the issue, either set the format property to "Presentation" for the binding object or change the PC's settings to view fewer decimal places eg. 2.
View full article
Picard Product_Support
‎2018-09-10 05:02 AM

Last Updated: Administrator CraigEl Administrator ‎2023-03-30 05:56 PM

Labels:
  • TAC Vista
2032 Views

Access Expert exception error adding a downstream device to an SSC

  Issue When attempting to add a downstream device to an SSC the error "exception of type \'Feenics.Keep.DomainModel.KeepException\' was thrown" Product Line EcoStruxure Access Expert Environment  Access Expert V3 Cause The SSC has a limitation of 32 downstream devices no matter what port(s) are being used either RS485 or virtual.  Resolution The SSC specification data sheet indicates the SSC can manage up to 64 downstream devices. However, R&D has corrected our understanding of this limitation which is only 32 downstream devices. Attempting to add a 33rd downstream device will result in the   \'Feenics.Keep.DomainModel.KeepException\' error. An additional SSC or Mercury upstream controller will be necessary to commission greater than 32  downstream devices.   From R&D: "The SSC can support a Total of 32 downstream devices no matter what port they are connected to either RS485 or Virtual. The SSC can also support 64 doors total." SSC data specification sheet  *Note: The specification sheet will be corrected in the future by the Product Owner.
View full article
Admiral Alan_Wood Admiral
‎2023-03-30 05:53 PM

on ‎2023-03-30 05:53 PM

Labels:
  • EcoStruxure Access Expert
986 Views

The procedure to follow for upgrading or downgrading the I/A Series G3 software in an I/A Series ENC

Issue What is the procedure for upgrading the I/A Series G3 software in an I/A Series ENC? Product Line TAC IA Series Environment I/A Series G3 Workbench software on computer (both the old version and new version need to be installed on the computer) I/A Series G3 ENC-520 or ENC-410 Cause Need to upgrade the software that is installed in the ENC. Resolution With the old version of Workbench running on the computer, backup the station running in the ENC.  All required graphic files, etc., stored in the ENC should also be backed up.  Note the station folder name for use in step 5, below. Verify that the license in the ENC is compatible with the new release to be installed. If not, use the License Manager (under the Platform) to install an updated license. If the correct version of the license is not currently available, it must be obtained and installed prior to beginning step 6, below. If the new release of the I/A Series G3 software has not already been installed on the computer, install it now. Verify that the Workbench computer has a license that is version compatible with the new release of the I/A Series software to be installed.  If the license is not version compatible, acquire a new license for the Workbench computer before continuing. Copy the entire named station folder (used in step 1) from the old release Stations folder to the new release Stations folder.  See NOTE below regarding the installation of a version downgrade. Run the "Install Platform Daemon" command from the Windows Start Menu folder for the new version of the software. Open the Workbench in the new version of the I/A Series G3 software and connect to the platform of the ENC to be upgraded. From the Platform menu, open the License Manager and verify that the ENC license has been updated to allow use with the new version of the I/A Series G3 software. Right-Click on the ENC platform in the Workbench tree and select Commissioning Wizard. Complete the commissioning process as documented in the Niagara AX Install and Startup Guide . On the first screen, select the operations to be performed.  The required minimum operations will normally be checked and shown in grey.  The "Install a station..." option needs to be checked if not already checked. Click [Next] to begin the commissioning process.  Continue through the various steps, as required.   When prompted, select the station copied in step 5. When prompted, verify that all required modules are available and are selected for installation. Allow the commissioning process to complete, following the prompts as required. The upgrade is now complete.  Start the station as required. NOTE: Do not use the process to directly downgrade the version of software installed in an ENC.  You must use the Platform "Distribution File Installer" to install the appropriate clean distribution (from the cleanDist folder under the software version to be installed.  Typically, only one clean distribution file will be available to be installed.  Select that file then click the [-> Install] button to downgrade the ENC software.  This process needs to be done as noted in step 5, above, after backing up the station but before beginning the commissioning of the device with the older I/A Series G3 software version.
View full article
Picard Product_Support
‎2018-09-10 09:04 PM

Last Updated: Administrator CraigEl Administrator ‎2023-03-30 05:51 PM

Labels:
  • TAC IA Series
4559 Views

Trend log limitations in SmartX IP Controllers

Issue What is the maximum number of trend logs in a SmartX IP Controller? What is the maximum number of trend log records in a SmartX IP Controller? Product Line EcoStruxure Building Operation Environment Building Operation Multi-purpose Controller Cause SmartX IP controller free object system memory is shared between objects and data in your application. There are no specific limits on the number of objects and/or trend logs that you can create. Several factors impact memory consumption: Every object added consumes a fixed amount of memory Memory is shared between objects and data. Adjustments to description fields or trend log buffer sizes will also impact the amount of memory consumed. Different controllers have different amounts of memory to start from. RPC controllers have roughly half of the memory of an MPC. Changes to EBO 3.X will also change the memory consumption, so upgrading your system may skew the memory consumption larger than it was in previous versions. Resolution After adding trend logs to the device consult the Free object system memory entry in the device report since this will help determine how much free memory is available. Trend log buffers are pre-allocated on creation of the trend object. The other place to find how much free memory the device have is in the device property page. This value can be put in a watch window, trended, or even bound to a low-limit alarm.     If the amount of free memory drops below 50 Kbytes, that is critically low available memory. A better target is to try to preserve 50% of available memory. Based on empirical testing, estimates of memory available inside a blank controller are: MP-C: 1890 Kbytes MP-V: 1780 Kbytes RP-C: 1115 Kbytes It is important to not overload the controller because the remaining memory can also be used for COV subscriptions (the last line in the table above). If there is no memory available, then opening a graphic which creates COV subscriptions could overrun memory or operate very slowly
View full article
Janeway Jonas_Brissman Janeway
‎2019-05-02 06:15 AM

Labels:
  • EcoStruxure Building Operation
3441 Views

Alarm Pane not shown in Webstation

Issue Alarm Pane not shown in Webstation Product Line EcoStruxure Building Operation Environment Building Operation Webstation Cause The User is viewing a Workspace which does not contain the Alarm Pane Resolution In the Top Left hand corner of the screen click View>Workspaces Select Engineering (or other applicable workspace)
View full article
Picard Product_Support
‎2018-09-07 07:15 AM

Last Updated: Administrator CraigEl Administrator ‎2023-03-29 05:23 PM

Labels:
  • EcoStruxure Building Operation
1284 Views

Locking down access to WebStation.

Issue Unable to lock down access to AS WebStation to all clients Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium Building Operation Webstation Cause Required to forbid accessing AS via http or https.. Resolution Https is the default workstation communication channel to an SBO server and therefore cannot be locked down. 
View full article
Picard Product_Support
‎2018-09-06 08:46 AM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-29 06:09 AM

Labels:
  • EcoStruxure Building Operation
1203 Views

Difference between "Workstation" and "Workstation Professional" licenses

Issue Information is needed regarding the content of the various license types Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause If a standard Workstation license and a Workstation Pro. license are purchased, and are loaded on to a License server, when is the professional license used? Resolution The difference between the standard Workstation license and the Workstation Pro. license is that the professional license allows the usage of the editors (Graphics Editor, Function Block Editor, Script Editor, Menta Editor, WorkPlace Tech Editor). The licenses can be seen as a bundle of license features that can be checked in and checked out separately from each other. When a workstation attempts to use any of these editors the license server is asked to check out the license feature for that editor and if successful, that feature is "taken" and cannot be used by any other Workstation until the first workstation leaves the editor. This means that if you have one professional license, only one Workstation can use the same editor at the same time, if you e.g. have 2 professional licenses you can have 2 Workstations using the same editor at the same time. However, any Workstation can use any editor as long as there is a free license feature for it on the license server.
View full article
Picard Product_Support
‎2018-09-06 09:22 AM

Last Updated: Administrator CraigEl Administrator ‎2023-03-29 05:20 PM

Labels:
  • EcoStruxure Building Operation
1541 Views

Script program does not execute correctly.

Issue The script program always executes the first condition, whatever the condition is. The code is shown below: Numeric Input AirFlowMin,AirFlowMax,AirFlowRead Numeric OutPut FlowFactor Line Judging if AirFlowMin<AirFlowRead<(AirFlowMax-AirFlowMin)/3 then goto 1 if (AirFlowMax-AirFlowMin)/3<AirFlowRead<(AirFlowMax-AirFlowMin)*2/3 then goto 2 if (AirFlowMax-AirFlowMin)*2/3<AirFlowRead line 1 FlowFactor=1 goto judging line 2 FlowFactor=2 goto judging line 3 FlowFactor=3 goto judging After the above program saves successfully, whatever the value of AirFlowRead is, the program only goes to line 1 and sets the value of FlowFactor to 1, and never goes to the other two lines. Product Line EcoStruxure Building Operation Environment B3s Script Program Cause Some expressions are supported in Continuum Plain English but are not supported in b3 Script programs Resolution Change the expression as shown below: Line Judging if AirFlowMin<AirFlowRead and AirFlowRead<(AirFlowMax-AirFlowMin)/3 then goto 1 if (AirFlowMax-AirFlowMin)/3<AirFlowRead and AirFlowRead<(AirFlowMax-AirFlowMin)*2/3 then goto 2 if (AirFlowMax-AirFlowMin)*2/3<AirFlowRead and AirFlowRead  
View full article
Picard Product_Support
‎2018-09-06 09:44 AM

Last Updated: Administrator CraigEl Administrator ‎2023-03-29 05:16 PM

Labels:
  • EcoStruxure Building Operation
1318 Views

Alarm email failure.

Issue Microsoft Outlook is not emailing alarms. Product Line Andover Continuum Environment Continuum 1.XXX Microsoft Outlook 2XXX Cause The created Contact folder used by Continuum Alarms to send emails was not being shown first.. Resolution Open Microsoft Outlook Select Tools > Address Book Select Tools > Options Once opened, select  "Show this address list first:" (It defaults to the Global Address List) Ensure the contact folder with the distribution list created for Continuum Alarms has been selected (Contact) Also see online help: Email, Creating an Event Notification List
View full article
Picard Product_Support
‎2018-09-06 02:14 PM

Last Updated: Administrator CraigEl Administrator ‎2023-03-29 05:10 PM

Labels:
  • Andover Continuum
2300 Views
  • « Previous
    • 1
    • …
    • 41
    • 42
    • 43
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of