Trend log limitations in SmartX IP Controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Trend log limitations in SmartX IP Controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterEdvik
    PeterEdvik
  • RobertAndriolo
    RobertAndriolo
  • Jonas_Brissman
    Jonas_Brissman

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3214 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Trend log limitations in SmartX IP Controllers

Janeway Jonas_Brissman Janeway
‎2019-05-02 06:15 AM

Issue

What is the maximum number of trend logs in a SmartX IP Controller?
What is the maximum number of trend log records in a SmartX IP Controller?

Product Line

EcoStruxure Building Operation

Environment

Building Operation Multi-purpose Controller

Cause

SmartX IP controller free object system memory is shared between objects and data in your application. There are no specific limits on the number of objects and/or trend logs that you can create.

Several factors impact memory consumption:

  • Every object added consumes a fixed amount of memory
  • Memory is shared between objects and data. Adjustments to description fields or trend log buffer sizes will also impact the amount of memory consumed.
  • Different controllers have different amounts of memory to start from. RPC controllers have roughly half of the memory of an MPC.
  • Changes to EBO 3.X will also change the memory consumption, so upgrading your system may skew the memory consumption larger than it was in previous versions.

Resolution

After adding trend logs to the device consult the Free object system memory entry in the device report since this will help determine how much free memory is available.

Trend log buffers are pre-allocated on creation of the trend object.

2019-04-15_14-07-13.png

2019-04-15_14-08-46.png

The other place to find how much free memory the device have is in the device property page. This value can be put in a watch window, trended, or even bound to a low-limit alarm.

 

Jonas_Brissman_0-1679895312156.png

 

If the amount of free memory drops below 50 Kbytes, that is critically low available memory. A better target is to try to preserve 50% of available memory. Based on empirical testing, estimates of memory available inside a blank controller are:

  • MP-C: 1890 Kbytes
  • MP-V: 1780 Kbytes
  • RP-C: 1115 Kbytes

It is important to not overload the controller because the remaining memory can also be used for COV subscriptions (the last line in the table above). If there is no memory available, then opening a graphic which creates COV subscriptions could overrun memory or operate very slowly

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • JonasBrissman19
  • JonasBrissman23
  • mp-c
  • mp-v
  • RP-C Memory
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of