Issue
A Cyberstation program will not transfer the value of an AnalogValue in a third party device to an AnalogValue point in Continuum.
The Cyberstation program consistently errors out and disables.
Product Line
Andover Continuum
Environment
- Continuum Cyberstation
Cause
Using a Cyberstation program to set the value of a point in a BCX controller to equal the value of a point in a third party device without an intermediate step.
Resolution
- Create AnalogValues in the Cyberstation.
- Point values should first be transferred from the third party device to the Cyberstation points.