Script program does not execute correctly.
  • Script program does not execute correctly.
  • Ramaaly
    Ramaaly
  • sesa242211
    sesa242211
  • YangboLIU
    YangboLIU
‎2018-09-06 09:44 AM
Last Updated: Administrator CraigEl Administrator ‎2023-03-29 05:16 PM
The script program always executes the first condition, whatever the condition is. The code is shown below:
Numeric Input AirFlowMin,AirFlowMax,AirFlowRead
Numeric OutPut  FlowFactor
Line Judging
if AirFlowMin<AirFlowRead<(AirFlowMax-AirFlowMin)/3 then goto 1
if (AirFlowMax-AirFlowMin)/3<AirFlowRead<(AirFlowMax-AirFlowMin)*2/3 then goto 2
if (AirFlowMax-AirFlowMin)*2/3<AirFlowRead
line 1
FlowFactor=1
goto judging
line 2
FlowFactor=2
goto judging
line 3
FlowFactor=3
goto judging
After the above program saves successfully, whatever the value of AirFlowRead is, the program only goes to line 1 and sets the value of FlowFactor to 1, and never goes to the other two lines.
  • B3s
  • Script Program
Some expressions are supported in Continuum Plain English but are not supported in b3 Script programs
Change the expression as shown below:
Line Judging
if AirFlowMin<AirFlowRead and AirFlowRead<(AirFlowMax-AirFlowMin)/3 then goto 1
if (AirFlowMax-AirFlowMin)/3<AirFlowRead and AirFlowRead<(AirFlowMax-AirFlowMin)*2/3 then goto 2
if (AirFlowMax-AirFlowMin)*2/3<AirFlowRead and AirFlowRead
Tags (2)
  • 15438
  • RamaAly23