Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,838
  • TAC IA Series 1,821
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 327
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 254
    • 255
    • 256
    • …
    • 507
  • Next »

TS-8XXX and TS-9XXX 1,000 Ohm Balco sensor, Celsius temperature resistance table.

Issue TS-8XXX and TS-9XXX 1,000 Ohm Balco sensor, Celsius temperature resistance table. Environment TS-8XXX TS-9XXX 1,000 Ohm Balco sensor Cause Unknown Cause Resolution Temp (°C) Ohms -40 779.0 -39 782.3 -38 785.6 -37 788.9 -36 792.3 -35 795.6 -34 799.0 -33 802.3 -32 805.7 -31 809.1 -30 812.5 -29 815.9 -28 819.3 -27 822.7 -26 826.2 -25 829.6 -24 833.1 -23 836.5 -22 840.0 -21 843.5 -20 847.0 -19 850.5 -18 854.1 -17 857.6 -16 861.1 -15 864.7 -14 868.3 -13 871.8 -12 875.4 -11 879.0 -10 882.6 -9 886.2 -8 889.9 -7 893.5 -6 897.1 -5 900.8 -4 904.5 -3 908.1 -2 911.8 -1 915.5 0 919.2 1 923.0 2 926.7 3 930.4 4 934.2 5 937.9 6 941.7 7 945.5 8 949.3 9 953.1 10 956.9 11 960.7 12 964.6 13 968.4 14 972.3 15 976.1 16 980.0 17 983.9 18 987.8 19 991.7 20 995.6 21 999.6 22 1003.5 23 1007.5 24 1011.4 25 1015.4 26 1019.4 27 1023.4 28 1027.4 29 1031.4 30 1035.4 31 1039.4 32 1043.5 33 1047.5 34 1051.6 35 1055.7 36 1059.8 37 1063.8 38 1068.0 39 1072.1 40 1076.2 41 1080.3 42 1084.5 43 1088.6 44 1092.8 45 1097.0 46 1101.2 47 1105.4 48 1109.6 49 1113.8 50 1118.0 51 1122.3 52 1126.5 53 1130.8 54 1135.1 55 1139.4 56 1143.7 57 1148.0 58 1152.3 59 1156.6 60 1160.9 61 1165.3 62 1169.6 63 1174.0 64 1178.4 65 1182.8 66 1187.2 67 1191.6 68 1196.0 69 1200.4 70 1204.9 71 1209.3 72 1213.8 73 1218.3 74 1222.7 75 1227.2 76 1231.7 77 1236.2 78 1240.8 79 1245.3 80 1249.8 81 1254.4 82 1259.0 83 1263.5 84 1268.1 85 1272.7 86 1277.3 87 1282.0 88 1286.6 89 1291.2 90 1295.9 91 1300.5 92 1305.2 93 1309.9 94 1314.6 95 1319.3 96 1324.0 97 1328.7 98 1333.4 99 1338.2 100 1342.9 101 1347.7 102 1352.5 103 1357.3 104 1362.1 105 1366.9 106 1371.7 107 1376.5 108 1381.3 109 1386.2 110 1391.0 111 1395.9 112 1400.8 113 1405.7 114 1410.6 115 1415.5 116 1420.4 117 1425.3 118 1430.3 119 1435.2 120 1440.2 121 1445.2 122 1450.1
View full article
Picard Product_Support
‎2018-09-06 02:31 PM

Last Updated: Administrator CraigEl Administrator ‎2019-06-03 06:53 PM

Labels:
  • Field Devices
1473 Views

BACnet String and DateTime Value Object

Issue BACnet String Value Object or BACnet DateTime Value Object in EcoStruxure Building Operation cannot be created. Only the EcoStruxure Object is created. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium Building Operation Enterprise Server Building Operation Multi-purpose Controller (MP-X) Building Operation Room Controller (RP-C) Building Operation IP-IO Cause Only EcoStruxure String Value Object or DateTime Value Objects can be created under the Servers, even if created under the BACnet/Application Folder. There are no current plans to change this. MP-X, RP-C are native BACnet devices so BACnet String Value Object and BACnet DateTime Value Object can be created. Resolution BACnet String Value Object or BACnet DateTime Value Object can be read and hosted by all versions of EcoStruxure Building Operation, but not created in the Server
View full article
Picard Product_Support
‎2018-09-06 10:38 AM

Last Updated: Guinan RandyDavis Guinan ‎2019-06-03 01:45 PM

Labels:
  • EcoStruxure Building Operation
2543 Views

TGML Objects are no longer highlighted when dragging and dropping snippets to the graphic editing pane.

Issue TGML Objects are not highlighted when dragging and dropping snippets to the graphics editing pane. If a number of objects are close together, it can be difficult to see which object the snippet is being dropped on to. Product Line TAC Vista Environment TAC Vista 5.1.7 TGML editor 5.1.7 Cause Updates to the TGML Editor in 5.1.7 removed this feature. Resolution The item which the mouse-pointer is hovering over is highlighted in the TGML menu tree in later versions. An upgrade will restore this functionality. As a workaround in version 5.1.7, snippets can be dragged directly to the desired object in the Objects Pane as opposed to the editor workspace to ensure the proper object is selected.
View full article
Picard Product_Support
‎2018-09-10 06:16 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-06-03 06:53 AM

Labels:
  • TAC Vista
1511 Views

Restore MNB-1000 to factory default

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue Process to restore MNB-1000 to factory default. Product Line TAC IA Series Environment MNB-1000 Cause If the IP address has been lost or unit has been misconfigured how can this be restored the factory default. *This step should only be taken if the data on the unit is not to be maintained * Resolution On the DIP switch settings, set all of the switches (1-8) to the ON position. Cycle power on the controller. Unit will boot up in reset mode (red flashing status light) Once completed the status light will be solid green. The unit is now in factory default mode The IP address will be 10.1.10.2 with a 255.255.255.0 subnet mask. BACnet IP will be disabled by default and BACnet Ethernet will be active.
View full article
Picard Product_Support
‎2018-09-06 10:07 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-05-31 11:47 AM

Labels:
  • TAC IA Series
5501 Views

Security levels in TAC Vista Workstation

Issue What security levels are available in Vista? Product Line TAC Vista Environment TAC Vista Workstation User Administration Cause Different security levels can be set for different users to administrate what they can and cannot see or modify. Resolution Low security Low security is intended for TAC Vista systems not using a Windows NT/2k network. You usually log in as a TAC Vista user. Users from a Windows NT/2k network may be used at this level of security.  High security High security is intended for TAC Vista systems using a Win NT/2k Network. To set up a high security account in Vista: The user logs in as a user in a Win NT/2k network. TAC Vista users are not at this level of security. The user is verified by a domain controller in the Win network. To be able to log into the Vista system a Win NT/2k account must be defined in TAC Vista for each user/group who are authorized to access the TAC Vista system. When logging in the user is identified by TAC Vista via the domain controller in the Win network. 
View full article
Picard Product_Support
‎2018-09-06 03:15 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-05-31 11:41 AM

Labels:
  • TAC Vista
1259 Views

MESSAGE: Unmatched LonWorks response received! [LonCommReceive.run]

Issue LON bindings stop updating in a Niagara R2 UNC station. The following message also appears in the standard output window: MESSAGE: Unmatched LonWorks response received! [LonCommReceive.run] The LON bindings are re-bound but the problem re-occurs. Product Line TAC IA Series Environment  Niagara R2 UNC Cause This message indicates that a LON controller is sending a message to the UNC's subnet/node address that the UNC cannot match to its LON database. This happens when a controller has not had its binding table updated. Resolution Make sure the UNC is the only LON network management tool used on the associated controllers. Compare the UNC's LON database information to the data actually held in the associated controllers. Right click on the LonWorks Service and select Lon Utilities Manager. Leave the "device" to 'localLonDevice' and set the "Command" to 'reports' and the "SubCommand" to 'verify.' The resulting output will show any mismatches in the various tables. To correct, re-commission the localLonDevice, re-commission all other devices (which clears their tables), and then re-bind all listed bindings. Re-run a 'reports' > 'verify' to ensure all devices are up and running on the network.
View full article
Picard Product_Support
‎2018-09-06 02:50 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-05-31 09:36 AM

Labels:
  • TAC IA Series
1544 Views

Website linked by a Hyperlink in EBO Workstation does not log off when user logs off from Workstation

Issue When a user logs on to Workstation and accesses the hyperlink, the website is displayed without prompt for login credentials Product Line EcoStruxure Building Operation Environment Building Operation Workstation Microsoft Internet Explorer Cause EcoStruxure Building Operation software uses Microsoft Internet Explorer to present web pages. How the page logs on is an IE function and not a function of EBO Workstation Resolution  Log off from the web site before logging off from Workstation  Configure Internet Explorer to delete browsing history on exit Go to Internet Explorer settings and then the Internet Options On the General tab, under the Browsing history, enable the checkbox for 'Delete browsing history on exit' (computer restart may be required)
View full article
Admiral RyanSuar Admiral
‎2019-05-03 01:49 PM

Last Updated: Guinan RandyDavis Guinan ‎2019-05-31 05:44 AM

Labels:
  • EcoStruxure Building Operation
1981 Views

MNB-1000 COV links using "link builder" in WorkPlace Commissioning Tool do not work

Issue When using "link builder" in WorkPlace Commissioning Tool, MNB-V2s and MNB-300s link OK but links to MNB-1000s do not work. Product Line  TAC IA Series Environment WorkPlace Commissioning Tool I/A Series MNB VAV I/A Series MNB 70 I/A Series MNB 300 I/A Series MNB 1000 Cause An incorrect value set for APDU retries in the MNB-1000. Resolution Use WorkPlace Commissioning Tool to display the devices, and double click the MNB-1000 in question to display the Device Properties window. Select the Advanced tab and ensure APDU retries is not set to 0. If it is, set it to 3, reboot the controller and the links will function properly.
View full article
Picard Product_Support
‎2018-09-06 02:44 PM

Last Updated: Guinan RandyDavis Guinan ‎2019-05-31 05:41 AM

Labels:
  • TAC IA Series
1247 Views

Conversion of OGC to TGML graphic fail if OGC name is longer than 36 characters

Issue When an old OGC graphic is converted to a TGML graphic in TAC Vista the conversion will fail if the name of the OGC graphic is longer than 36 characters. The OGC to TGML converter will just close with no error message. Product Line TAC Vista Environment Vista Workstation Cause The OGC to TGML converter does not support OGC graphic names longer than 36 characters, but if you try converting with longer names, the converter just closes down without any error message indicating why the conversion failed. This is a defect in the OGC to TGML converter which is reported to R&D. Resolution Rename the OGC graphic to a name with 36 characters or less.
View full article
Janeway Jonas_Brissman Janeway
‎2019-05-13 12:12 AM

Last Updated: Janeway PeterEdvik Janeway ‎2019-05-31 05:29 AM

Labels:
  • TAC Vista
1253 Views

External binding to temperature input shows incorrect value

Issue A temperature input on one device is referenced in an external binding, e.g. a consumer value, in another (BACnet) device. The value on the consumer side is incorrect and seems to have been converted from Fahrenheit to Celsius although the units all show Fahrenheit. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Automation Server (Premium) Building Operation Enterprise Server / Enterprise Central BACnet Device(s) supporting external binding (e.g. MP-X or IP-IO) Cause The probable cause is that the value of the temperature input is not configured to a specific unit. This means that the unit is decided by the electrical type of the thermistor. In most cases this is Temperature °C, which means that the values are stored in °C, and this is the value being transferred in the consumer binding. If the measurement system in Workstation is set to United States Customary Units (US), the input value will be displayed in Fahrenheit (°F) and one might think that the unit of the temperature input value is also configured to Fahrenheit, when in reality it is in Celsius. In this situation the value on the consumer side is in Celsius as it has no information about units. Furthermore, if the consumer value unit is configured to Fahrenheit, then we have the situation shown in the screenshot above. Resolution Start by changing measurement system in Workstation to As configured in object. (Refer to the Webhelp for more information about how to do this.) By doing this the values will be displayed unconverted. It is now clear that the temperature input in reality is in Celsius. The next step is to configure the input unit to Fahrenheit. Open up Properties for the Temperature input and click the gear wheel next to Value to configure. Check the box to the left of Unit and click the button with the three dots to the right. Select °F and click Select Click OK to confirm the changes in both open windows. Both the temperature input and the consumer value will now be displaying the correct value in Fahrenheit.
View full article
Janeway PeterEdvik Janeway
‎2019-05-22 12:46 AM

Labels:
  • EcoStruxure Building Operation
3524 Views

PWM output in TAC Xenta 122

Issue How to set up PWM output in ZBuilder for TAC Xenta 121/122 devices. Product Line TAC Vista Environment Xenta 121 Xenta 122 ZBuilder Cause To be able to set up the PWM function for outputs, you need to understand each entry in the settings windows. Resolution   Activate at % TL The PWM output control starts when Terminal Load reaches this value. Fully active at % TL The PWM output control is fully active when Terminal Load reaches this value. Min control signal % The PWM output will not send out lower percentage of full stroke. Max control signal % The PWM output output will not send out higher percentage of full stroke. Period seconds The time for one full PWM period. This period will be cyclically repeated. Pulse change if change ≥ % Applicable only for actuators giving a position directly proportional to the pulse width and not dependent of cyclic updates (PWM with US terminology). This means the output will only activate when the Terminal Load has changed more than the set value, since last activation. Normally closed The TRIAC output is connected to ground (activated) when Terminal Load is zero, and the PWM output is not active. When the PWM output activates, the TRIAC output will not be connected to ground. Normally open The TRIAC output is open, not connected to ground, when Terminal Load is zero, and the PWM output is not active. When the PWM output activates, the TRIAC output will be connected to ground.
View full article
Kirk MikaelKrantz Kirk
‎2019-05-16 06:41 AM

Last Updated: Janeway PeterEdvik Janeway ‎2019-05-31 05:28 AM

Labels:
  • TAC Vista
1366 Views

Vista Workstation User Password Illegal Characters

Issue In Vista Workstation you can create a new user and password using all characters of a keyboard. Vista Workstation allows creation but when you try to login to Workstation you get a login error. Product Line TAC Vista Environment Vista Workstation Cause Using characters in the password field that Vista does not recognize. Resolution Don't use the following characters in a password for users: !   @   #   $   %   ^  &  *  (  )  -  =  +  ,  <  >  '  "  ?  \ The following special characters can be used in the password field: _  .  /  : 
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Last Updated: Janeway PeterEdvik Janeway ‎2019-05-31 05:27 AM

Labels:
  • TAC Vista
1600 Views

Trend logs in TAC Vista will not show any new values after upgrade to version 5.1.7

Issue After upgrading to TAC Vista version 5.1.7 no new values will be shown when a trendlog is opened.  Error message in Vista: System.Data.SqlClient.SqlException (0x80131904): Incorrect syntax near ')'. at System.Data.SqlClient.SqlConnection.OnError(SqlException exception, Boolean breakConnection) at System.Data.SqlClient.SqlInternalConnection.OnError(SqlException exception, Boolean breakConnection) at System.Data.SqlClient.TdsParser.ThrowExceptionAndWarning() at System.Data.SqlClient.TdsParser.Run(RunBehavior runBehavior, SqlCommand cmdHandler, SqlDataReader dataStream, BulkCopySimpleResultSet bulkCopyHandler, TdsParserStateObject stateObj) at System.Data.SqlClient.SqlDataReader.ConsumeMetaData() at System.Data.SqlClient.SqlDataReader.get_MetaData() at System.Data.SqlClient.SqlCommand.FinishExecuteReader(SqlDataReader ds, RunBehavior runBehavior, String resetOptionsString) at System.Data.SqlClient.SqlCommand.RunExecuteReaderTds(CommandBehavior cmdBehavior, RunBehavior runBehavior, Boolean returnStream, Boolean async) at System.Data.SqlClient.SqlCommand.RunExecuteReader(CommandBehavior cmdBehavior, RunBehavior runBehavior, Boolean returnStream, String method, DbAsyncResult result) at System.Data.SqlClient.SqlCommand.RunExecuteReader(CommandBehavior cmdBehavior, RunBehavior runBehavior, Boolean returnStream, String method) at System.Data.SqlClient.SqlCommand.ExecuteScalar() at TAC.DSS.DataAccess.SqlServer.SqlMaintenance.GetDatabaseFragmentationLevel(String tablename) at TAC.DSS.DataAccess.SqlServer.SqlMaintenance.GetDatabaseFragmentationLevel_TrendlogValue() at DssCliLib.Utility.GetDatabaseFragmentationLevel_TrendlogValue(SByte* pszConnectionString, Int32* plSize) Product Line TAC Vista Environment Vista Server version 5.1.7 Cause This issue occurs due to the use of an incompatible SQL server version. A number of new features were introduced in Vista 5.1.7, one of which was a check of the SQL database's fragmentation level. It is this check that fails as it uses a query that is not recognised in SQL 2000. Resolution Upgrade/run the database to/on SQL 2005 server or higher.
View full article
Picard Product_Support
‎2018-09-06 10:38 AM

Last Updated: Janeway PeterEdvik Janeway ‎2019-05-31 05:26 AM

Labels:
  • TAC Vista
1430 Views

Pin configuration of RJ10 for TAC Xenta OP

Issue Pin configuration of the RJ10 for TAC Xenta OP Product Line TAC Vista Environment Xenta OP Cause The Xenta OP has two connection methods, the 4 pin terminal blocks and an RJ10 port. Some users may have the need for making custom RJ10 cables. Resolution The pin order for the RJ10 port is the exact same as the order on the terminal block right next to it. From right to left they are: C1 (comms 1) C2 (comms 2) G+ (24 VAC power) G0 (24 VAC ground)
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Last Updated: Janeway PeterEdvik Janeway ‎2019-05-31 05:23 AM

Labels:
  • TAC Vista
1542 Views

Unable to send alarm generated emails via the Yahoo SMTP server in I/A Series G3.

Issue Unable to send alarm generated emails via the Yahoo’s SMTP server in I/A Series G3. The following error messages are displayed in the console output window when attempting to send a mail via Yahoo’s SMTP server. javax.mail.MessagingException: Could not connect to SMTP host: smtp.mail.yahoo.com, port: 465; Caused by: java.net.ConnectException: Connection refused: connect Product Line TAC I/A Series Environment Niagara G3 ENS ENC-520 ENC-410 Cause An incorrect STMP hostname was used in the “Hostname” of the OutgoingAccount. The correct Yahoo outgoing mail address, “smtp.mail.yahoo.com”, must be entered for in the OutgoingAccount “Hostname”. Resolution Procedure and properties settings required when using the Yahoo SMTP Server: Add the EmailService and CryptoService to the station's Services folder. If emails are to be sent from an ENC, ensure that the email and crypto modules (and their dependencies) are installed into the ENC. Add the OutgoingAccount to the EmailService. In the OutgoingAccount properties, configure the properties indicated below. Leave other properties as their default settings. Hostname: smtp.mail.yahoo.com Port: 465 (this is the TCP port SMTP over SSL uses) Account: example@yahoo.com (works without the “@yahoo.com” as well) Password: Your Yahoo account password Enabled: true Use SSL: true (Yahoo requires SSL) Transport: Smtp Use Authentication: true (Yahoo requires authentication when sending out emails) Reply to: example@yahoo.com (“The Reply To” must contain a valid Yahoo account) You can test the functionality by right-clicking on the EmailService and selecting 'Actions' > 'Send' to send out an email. Notes: CryptoService enables the SSL feature in the G3 station. The crypto module is included in the installation of I/A Series G3 version 3.6 but it was not included in earlier versions. You can download the crypto modules for earlier versions of G3 from The Exchange Download Center. Ensure that the station is licensed for crypto. You can look into your license file to check. Below is an example taken from a demo license. feature expiration="2012-03-31" name="crypto" parts="ENS-DEMO" ssl="true"
View full article
Picard Product_Support
‎2018-09-11 02:18 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2019-05-30 10:27 PM

Labels:
  • TAC IA Series
3131 Views

Generating a license for the Roam IO2 ethernet option

Issue A license is needed for using the Roam IO2 with ethernet Product Line Andover Continuum Environment Roam IO2 Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause A license is required to use the ethernet feature with the Roam IO2 Resolution Follow the instructions for Generating a License request in the BACnet Service Tool Generating a License manual, (PDF attached). Include your contact information, PO (purchase order) and RA numbers for the RoamIO2. Send that information to Upgrades.Continuum@schneider-electric.com to process the request.
View full article
Picard Product_Support
‎2018-09-10 04:25 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2019-05-30 10:23 PM

Labels:
  • Andover Continuum
1673 Views

Convert a Xenta 121-HP to a Xenta 121-FC

Issue Is it possible to convert a Xenta 121-HP to a Xenta 121-FC? Product Line TAC Vista Environment Xenta 121 Cause The hardware controller was purchased as a heat pump or fan coil unit, and the opposite is needed for the software application. Resolution As of August 2011, it is possible. Download the NXE file and XIF file for the desired application Download the files to the Xenta 121 using Lonmaker or NL220 This will be blocked in the future.
View full article
Picard Product_Support
‎2018-09-06 01:26 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2019-05-30 10:22 PM

Labels:
  • TAC Vista
1456 Views

Unable to connect to a G3 ENC or JACE after attempting to commission, downgrade or install a station.

Issue Unable to connect to a G3 ENC or JACE after attempting to downgrade or install a station. One of several different errors may be displayed in the serial shell console output.  The following are examples: Could not find library libcpp.so.3 Could not find library libcpp.so.4 Error occurred during initialization of VM - Java/Lang/ No Class Def found error: Java/Lang/object Product Line TAC I/A Series Environment I/A Series G3 ENC and JACE (all revisions), ENC-410, ENC-520, TRD-T-645, TRD-T-603, TRD-RB-645, TRD-RB-603, TRD-J-600E, TRD-T-700 Cause The issue is caused by downgrading the ENC / JACE without following the procedure to first install the clean distribution file. In addition, the ENC/JACE will fail if a station is copied into the ENC/JACE without first installing the OS and NRE software using the Workbench Commissioning Wizard. Note: With G3 release 3.3 and newer, the procedure for downgrading an ENC/JACE is included in the Niagara AX Platform Guide - Downgrading a JACE (Clean Dist). Resolution Tools needed: Null Modem Cable Serial Terminal (e.g. HyperTerminal or TeraTerm) Jumper Obtaining the files required to recover the ENC NOTE: If recovery of a Jace-700 is required, please contact Product Support for the recovery file. Download the appropriate OS image and gz file zip file for the ENC/JACE from the Exchange website - https://ecobuilding.schneider-electric.com ENC-410.zip ENC-410-1 standard memory - etfs512 ENC-410-EM.zip ENC-410-1 extended memory - etfs2048 ENC-520.zip ENC-520-2 standard memory - etfs512 ENC-520-EM.zip ENC-520-2 extended memory - etfs2048 NPM6E.zip JACE603/645, TRD-RB-603/645, JACE600E Note: The files used in the following procedure MUST correctly match the ENC/JACE hardware platform, otherwise permanent damage to the unit may occur. The serial shell can be used to determine the file system requirements (standard or extended memory). To find the exact image needed for an ENC (JACE 2/4/5) execute the following while connected to the unit with serial shell: Log into the unit's menu system using the platform username and password. Type sh to exit the menu system and enter the shell mode. At the # prompt, (type: cat sys/info/fs) and enter This will return the file system type of etfs512 or etfs2048. Extract the OS image and gz files from the downloaded zip to a suitable directory on the local computer (e.g. local hard drive such as: c:\temp). Enable ftp: By default, the ftp port is disabled on every ENC/JACE as shipped from the factory.  Enable the ftp as follows. Set the jumper on the ENC to serial shell mode and connect the null modem cable between the PC and the ENC/JACE. Connect to the ENC using the Serial Terminal program and the following port settings: Baud rate 57600 bps (Note: JACE-603/645 baud rate is 115200) 8 data bits, 1 stop bit, no parity After logging in to the menu system from the serial shell, do the following to enable ftp: Select option 4 from the menu Enter the port number (Normally 21). (type: 21) Press the Enter key to confirm the change Note: Leave the serial shell connection open while performing the next steps. FTP the OS image and gz files On the local system, open a command prompt window and change the directory to the location where the OS image and gz files were extracted (c:\temp). Connect to the ENC via ftp and put the OS image in the /tmp directory entering the following from the command line: Create a ftp connection to the ENC by typing: ftp and enter Type the username and password for the platform when prompted Change directory to /tmp (type: cd tmp) and enter Change to binary mode (type: bin) and enter Download the image to the ENC by using the put command. The image name must exactly match the image extracted from the downloaded zip file. ENC-410-1 standard memory (type: put york-etfs512.image) and enter ENC-410-1 extended memory (type: put york-etfs2048.image) and enter ENC-520-1 standard memory (type: put james-etfs512.image) and enter ENC-520-1 extended memory (type: put james-etfs2048.image) and enter JACE-600E, 603, 645 extended memory (type: put npm6xx-etfs2048.image) and enter Download the gz file to the ENC by using the put command. The name must exactly match the image extracted from the downloaded zip file. Change directory to the root (type: cd ../..) and enter Change directory to /ffs0/zip (type: cd ffs0/zip) and enter Download the gz file (type: put clean.tar.gz) and enter Exit ftp (type: quit) and enter Execute OS image update Return to the serial shell connection Type sh to exit the menu system and enter the shell mode At the # prompt, type: osupdate and enter After a short delay the # prompt will return. Shutdown to reboot the ENC (type: shutdown) and press enter. The ENC/JACE will reboot, install the clean distribution image and perform one additional reboot automatically. The ENC/JACE should now be recovered and allow connection to the platform. Connect and use the Workbench Commissioning Wizard to install the version of G3 required.
View full article
Picard Product_Support
‎2018-09-07 12:12 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2019-05-30 10:21 PM

Labels:
  • TAC IA Series
3358 Views

Failed to call pILiveData error when editing Schedule object in Continuum 1.94

Issue After upgrading to Continuum 1.94, Cyberstation throws the following error: Failed to call pILiveData -> GetLiveData().  ACDataServices has an error. Product Line Andover Continuum Environment Continuum 1.94 Schedule Error Cause This behaviour is due to a bug that was described in TPA-BOST-12-0002 00 Schedule Exception Errors. Resolution Install the CyberStation v1.94 SP1 - Software which can be found on the Exchange Extranet.
View full article
Picard Product_Support
‎2018-09-11 07:25 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-05-30 06:14 AM

Labels:
  • Andover Continuum
2008 Views

New graphic opens in a very small pane at the edge of the screen

Issue Most systems have an Overview Graphic of the whole building.  The user then navigates from this graphic to specific floors and rooms of interest. If the Workspace is configured incorrectly, navigating to a newly selected graphic does not work as expected. The overview graphic does not disappear and the new graphic is forced to open very small at the edge of the screen. Product Line Building Operation Enterprise Server Environment Workspaces Cause The standard Administration and Engineering Workspaces used in EBO contain a Work Area Window (WAW) which is necessary 'space' to show a selected graphic/trend/schedule If an Overview Graphic Pane is created in a Customer Workspace and this graphic takes up most of the screen, there is no space left to show the new object which the customer wishes to see Note: The Overview Graphic 'Building' is now shown in a Graphic Viewer only   When the system tries to open a new graphic, there is not space to open it in, The graphic is forced to open at the very edge of the screen and is therefore very small. Resolution General information about creating and using Graphic Panes, Work Area Windows and Panel Components can be found in the EBO webhelp, But for specific information on how to prevent a graphic opening at the edge of the screen see below.  Rather than adding a Graphic Pane to the Workspace to show the Overview Graphic add a Work Area Window (WAW) instead. Next, define the required Overview graphic as the initial path for the WAW on startup so the Overview graphic opens at user log on. Note: The Overview graphic 'Building' is now shown in the WAW rather than the Graphic Viewer. Graphics will always close themselves on navigation to the next object by default when used with a WAW (this can be changed). As soon as the user needs to navigate away from the overview page to a new graphic/schedule/trend, the system can use the WAW which will then use most of the screen as the 'space' to show it. In this case, as soon as the link to the next graphic 'Floor' is pressed, the first graphic 'Building' closes according to its default and the new object is shown in its place.
View full article
Admiral David_Kendrick Admiral
‎2019-01-17 03:02 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2019-05-30 05:17 AM

Labels:
  • EcoStruxure Building Operation
1684 Views
  • « Previous
    • 1
    • …
    • 254
    • 255
    • 256
    • …
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of