Setting up a custom Wiegand format access card

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Setting up a custom Wiegand format access card
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
7040 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Setting up a custom Wiegand format access card

Picard Product_Support
‎2018-09-07 01:58 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-07-11 09:08 AM

Issue

Using access card types not natively supported by Continuum system

Product Line

Andover Continuum

Environment

  • CyberStation
  • CX9900/9940
  • CX9702
  • CX9680
  • ACX5740/5720
  • ACX701
  • ACX781

Cause

Continuum has built in support for the most widely used Wiegand card types, occasionally a site might be using a card type for which Continuum has not built in support. In such cases the system must be configured using custom card functionality.

Resolution

Setting Up a Custom Wiegand Format

A custom format must be used when the card format is not one of the standard pre-defined formats. Only one custom format can be used in an ACX7xx controller and NC1(CX99xx), NC2(CX968x) using AC1 modules, up to four custom formats can be used with the ACX57xx and NC1/NC2 using AC1Plus modules.

  1. In each ACX700 and ACX780/781, NC1, NC2, ACX57xx create an InfinityNumeric point called AccessFormat (use this spelling exactly!). During the creation process, attach a manual array (log) with 22 entries to the point. If using more than one custom card definitions create InfinityNumeric points called AccessFormat2, AccessFormat3 and AccessFormat4
  2. Create the following InfinityProgram in each controller. The program should be type FallThru, and AutoStart. This program basically saves you from having to set each array value individually for each controller. The program, once created, can be copied to all other access controllers that need it.

    In the following example the AccessFormat array is setup to allow the system to read the HID Corporate 1000, 35 bit card.

    Program Name: SetCustCrdArray
    FlowType: FallThru
    AutoStart: True
    
    Code:
    Set AccessFormat[1] to 35      ‘overall number of bits
    Set AccessFormat[2] to 0        ‘control mask
    Set AccessFormat[3] to 0        ‘ manufacturer’s code
    Set AccessFormat[4] to 0       ‘ start bit of man. Code (first bit is 0, not 1)
    Set AccessFormat[5] to 0       ‘ end bit of man. code
    Set AccessFormat[6] to 2       ‘ start bit of site code (NOTE: If the card has no site code set this field to 0)
    Set AccessFormat[7] to 13      ‘ end bit of site code (NOTE: If the card has no site code set this field to 0)
    Set AccessFormat[8] to 14      ‘ start bit of card number
    Set AccessFormat[9] to 33      ‘ end bit of card number
    Set AccessFormat[10] to 0      ‘ odd parity mask, first 16 bits
    Set AccessFormat[11] to 0      ‘ odd parity, next 16
    Set AccessFormat[12] to 0      ‘ odd parity, next 16
    Set AccessFormat[13] to 0      ‘ odd parity, next 16
    Set AccessFormat[14] to 0      ‘ even parity, first 16
    Set AccessFormat[15] to 0      ‘ even parity, next 16
    Set AccessFormat[16] to 0      ‘ even parity, next 16
    Set AccessFormat[17] to 0      ‘ even parity, next 16
    Set AccessFormat[18] to 0      ‘ card number multiplier
    Set AccessFormat[19] to 0      ‘ card number divisor
    Set AccessFormat[20] to 0      ‘ start bit of issue code
    Set AccessFormat[21] to 0      ‘ end bit of issue code
    Set AccessFormat[22] to 0      ‘ decimal shift of issue code​

     
  3. In each Door Configuration, select the Custom Wiegand card type. Other card types may also be selected.
  4. For each Personnel, select the Custom Wiegand card type, and enter the correct card number and site code.

If the card is not working, check the Event Log and determine the cause. For Invalid Card Parity errors, set all the parity masks to 0 and try again. For proximity cards, the parity check may be eliminated with little consequence.

NOTE: In controllers that support the HID Corporate 1000, 35 bit card natively (NC2 – CX968x and ACX2 – ACX57xx) the AccessFormat numeric is internally used by the system, any other custom card definitions must use AccessFormat2 – AccessFormat4

Control mask

Some Wiegand cards are encoded with the bits in one or more fields reversed and/or complemented. It is then necessary to operate on the fields when decoding the data in order to obtain the correct data.

In the AccessFormat array a control field is provided to configure the system so that the bits in a field in the access card data can be reversed and/or complemented.

The control mask is located at AccessFormat[2]

Control Mask

The bits of the control mask are used by the parsing routine in the controller to reverse or complement selected fields. Setting the appropriate bit to a 1 will enable the special action:

controlMask.png

Example: To reverse the bits in the site code field set AccessFormat[2] = 8

Parity mask calculation

The table below shows the card format information provided by the manufacturer of a 32 bit Wiegand card. From the information provided by the manufacturer we can deduct the flowing about the format of the data on the card:

  1. The card data is comprised of the following 3 fields
    A = Customer Code
    B = Facility Code
    C = Card Number
  2. Bits 0 through 16 make up the even parity field. (The ‘X’ indicates that the bit is part of the even parity field)
  3. Bits 15 through 31 make up the odd parity field.

Note the overlap in the fields (bits 15 and 16 are members of both the even and odd parity fields), this is common as the fields are arbitrarily assigned by the card manufacturers.

parityMask.png

Armed with the information provided by the manufactures we can calculate the parity mask which Continuum will need to use in order to perform the necessary parity check upon receipt of the card data transmitted by the card reader.

First, calculate the EVEN parity mask.

To better illustrate how the calculation is done we have added a new row to our table, in this row we are going to enter the even parity mask as a binary number.
What we do is write a 1 (one) in each bit that is a member of the even parity field and a 0 (zero) for bits that are not part of the even parity field.

evenParitMask.png

The second step is to divide the bits that make up the field into groups of 4 which will make it easier to convert the binary number in the previous row to a hexadecimal number.

evenParityHex.png

The even parity mask for this card is 0xFFFF8000

It should now be obvious how Continuum uses the mask when checking for even parity.

Upon receipt of the card data transmitted from the reader, Continuum applies the mask to the full 32 bit stream of data received, (a logical AND operation is performed) the mask acts like a filer that allows only the set bits in the even parity field to pass through, now all Continuum has to do is count the bits that passed through the filter and make sure the count is an even number, if the count is not an even number Continuum sends a parity error.

The Odd parity mask is calculated using the same procedure.
Here is an example for the calculation of the parity masks for a 35 bit card

oddParityMask.png

A = Company ID Code
B = Card Number

P= EVEN PARITY

Even Parity Mask

0x76DB (30427)
0x6DB6 (28086)
0xC000 (49152)
0x0000 (0)

P = ODD PARITY

Odd Parity Mask

0x6DB6 (28086)
0xDB6D (56173)
0xA000 (40960)
0x0000 (0)

After calculating the parity masks you enter the decimal numbers into the appropriate fields in the AccessFormat array.

accessFormatArray.png

S = Site Code
C = Card Number

P= EVEN PARITY

Even Parity Mask

0xFFFF (65535)
0XE000 (57344)
0x0000 (0)
0x0000 (0)

P = ODD PARITY

Odd Parity Mask

0xFFFF (65535)
0xFFFF (65535)
0xF000 (61440)
0x0000 (0)

IMPORTANT:

If a custom card is configured with a bit count that is the same as the bit count of one of the cards that are supported natively, the parity masks MUST be entered in the AccessFormat array in order for the controller to be able to parse the custom card correctly, if not parity masks information is entered, the controller will generate an 'Invalid attempt, bad parity' event when the custom card is presented at the reader.

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 4857
  • CraigEllis19
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore