Use a PE Program to grant/deny access to areas dynamically based on a main 'Check-in/Check-out' reader

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Use a PE Program to grant/deny access to areas dynamically based on a main 'Check-in/Check-out' reader
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1580 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Use a PE Program to grant/deny access to areas dynamically based on a main 'Check-in/Check-out' reader

Picard Product_Support
‎2018-09-11 03:07 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-07-22 08:01 AM

Issue

A site physical access is configured as follows...

Upon arriving at the site, the employee must check-in at a gate where a main biometric reader at a VIRTUAL door is configured with entry/exit readers for Check-in and Check-out. This 'Registration' reader is not controlling access to any physical door, the Registration door in Continuum has zero for door relay channel but IT IS configured with entry/exit readers so the Continuum access control panel can detect the check-in/check-out transactions.

Once the employee has checked in, he can continue on to the building where he must then present his physical access credentials at a physical door to gain access into the building.

The site requirement is that the employee can not be given access to the building until they have checked-in at the Registration reader at the gate, also, access to the building must be removed upon the employee checking-out at the gate when leaving the site.

The doors in the buildings are configured with entry reader ONLY, so entry/egress anti-passback cannot be used.

Product Line

Andover Continuum

Environment

  • CyberStation
  • ACX2
  • NC2
  • NC1
  • 9702

Cause

Documentation

Resolution

Since this must be done on a per employee basis, an InfinityNumeric is created per employee and assigned as the area schedule in the personnel object for the areas that are in the building.

A specific convention is used for the name of the numerics (Key_XXXXX) where XXXXX is the card number assigned to the employee.

A PE program monitors the registration door at the gate, when en employee arrives and checks-in the program finds the appropriate employee key numeric and turns it ON to grant access to the areas in the building, conversely, when the employee leaves, the program finds the right key and turns it to OFF to deny access.

PROGRAM SAMPLE

IMPORTANT: PE PROGRAM IS PROVIDED HERE AS PROOF OF CONCEPT ONLY AND IS NOT INTENDED TO BE TAKEN AS A COMPLETE TESTED SOLUTION.

'This program controls access to the building on a per employee basis
'The area schedule numeric for the employee is turned ON when the employee 
'reports at the entrance reader (GIVE EMPLOYEE THE KEY) and OFF when the 
'employee reports his departure at the exit reader. (TAKE THE KEY FROM THE EMPLOYEE)

'ASSUMPTIONS
'1. All cards have the same site code

'AUTO START
'LOOPING

Numeric Direction, DEBUG
String theKey

Line INIT
  DEBUG = 1 'SET THIS TO 1 FOR DEBUG HELP
  Goto WAIT_FOR_ACCESS

Line WAIT_FOR_ACCESS
  theKey = "Key_" 'RESET KEY NAME
'WAIT FOR A VALID ACCESS AT THE LOBBY
  If Lobby ValidAccess then Goto GET_DIRECTION

Line GET_DIRECTION
'DETERMINE IF ENTRY OR EGRESS
  If Lobby TimeEntered > Lobby TimeExited then Goto ENTRY Else Goto EXIT

Line ENTRY
  theKey = theKey ; Lobby EntryLastCard 'FIND THE KEY FOR THIS CARD
  getname(theKey) = On 'GIVE THE EMPLOYEE THE KEY
  Goto WAIT_FOR_ACCESS

Line EXIT
  theKey = theKey ; Lobby ExitLastCard 'FIND THE KEY FOR THIS CARD
  getname(theKey) = Off 'TAKE THE KEY FROM THE EMPLOYEE, NO KEY NO ACCESS
  Goto WAIT_FOR_ACCESS

Line E
  If DEBUG then Print "Hit the error line" to Debug_STR
  If TS > 0 then Goto WAIT_FOR_ACCESS
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 17050
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore