Webclient Pre-Installation Requirements for Windows Server 2016

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Webclient Pre-Installation Requirements for Windows Server 2016
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood
  • JonGreen
    JonGreen

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1725 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Webclient Pre-Installation Requirements for Windows Server 2016

Admiral Alan_Wood Admiral
‎2019-07-18 07:50 AM

on ‎2019-07-18 07:50 AM

Issue

WebClient Pre-Installation Requirements for Server 2016 are not included in the 2.03 webClient installation guide

Product Line

Andover Continuum

Environment

  • Windows Server 2016
  • Continuum webClient Server 2.03

Cause

The Pre-Installation requirement steps provided in the webClient planning and installation guide do not show all the steps needed to install webClient successfully

Resolution

This material is intended as a supplement to the webClient Planning and Installation Guide

 

Installing IIS on Windows Server 2016
For Windows Server 2016, install IIS on the designated web.Client application
server (LAN systems) or the standalone CyberStation/web.Client workstation
(standalone system).
1. Start the Server Manager by clicking on the Administrative Tools menu.
2. In the Server Manager, click Add Roles and Features.
3. In the Add Roles and Features Wizard, Before You Begin tab, click Next.
4. In Installation Type, select Role-based or feature-based installation.

Select Installation TypeMan.png

5. Click Next and then select a server or virtual hard disk on which to install
roles and features.
6. In Server Selection, click Select a server from the server pool.

Server Selction Man.png

7. Click Next and select one or more roles to install on the selected server.
8. In Select Server Roles, please select the items from the following snapshots carefully

Note: In previous Windows Server instructions from the webClient pre-installation guide, a reference was made to select Application Server. This option is selected and installed by default in Windows Server 2016.

No selection for Application Server is offered.

 

Select Server Roles1.png

Select Server Roles2.png

Select Server Roles3.png

Select Server Roles4.png

Select Server Roles5.png

Select Server Roles6.png

Select Server Roles7.png

Select Server Roles8.png

Once these Pre-Installation steps have been performed the webClient Server is ready for Chapter 4 - Installing web.client on the IIS PC (Found in the webClient planning and installation guide.pdf)

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • AlanWood19
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore