How to uninstall an I/NET Seven Host MPC

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to uninstall an I/NET Seven Host MPC
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1807 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to uninstall an I/NET Seven Host MPC

Picard Product_Support
‎2018-09-06 03:29 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-07-15 07:02 AM

Issue

How to uninstall an I/NET Seven Host MPC

Product Line

TAC INET

Environment

I/NET Seven Host MPC

Cause

Uninstall an I/NET Seven Host MPC

Resolution

  1. Demote all workstations (clients) one at a time.
  2. After all workstations are in standalone mode, demote the File Master.
  3. On the File Master:
    1. Log off the I/NET Seven system
    2. Shut down the I/NET I/O Server Driver
    3. Go into the Task Manager Function and "End Task" on the following Files -- SQL Server & SQL Agent.
  4. If you have a SQL Database on the File Master and you want to save this database, go to the DbCreate editor and do a SQL Backup. Make sure the path of this backup is located OUTSIDE of Inet Seven directory.
  5. Launch the Windows Control Panel. Go to Add/Remove Programs.
  6. Remove the "Inet Seven" Program
  7. Remove the "Microsoft SQL Desktop Engine" program
  8. Exit out of the Control Panel.
  9. Launch Windows Explorer.
  10. Go to the following directory - "Program Files\Inet Seven"
  11. Highlight the "Inet Seven" directory, and delete this folder
  12. While you are still in the "Programs Files" directory, look for the following file folder “Microsoft SQL Server”. Once you find this, highlight the folder and delete.
  13. Go to the Recycle Bin and delete all entries in this folder.
  14. Exit out of the window explorer function.
  15. Next go to the desktop and look for the icon "My Computer"
  16. Right click and highlight the "Manage" directory.
  17. Scroll down the list until you find the section "Local Users & Groups"
  18. Double click this folder, then double click the "Users" folder.
  19. Highlight and delete the following user account "INMPROXY"
  20. Reboot the PC to make sure all of the actions you performed take effect.
    Note: you need to repeat steps # 5 through step # 20 on every workstation (client) on the I/NET Network.
  21. Once the reboot is complete, you are now ready to re-install the I/NET Seven from the CD.
    To return the I/NET system to the File equalization mode you need to do the following steps.
  22. Shut down the I/O Server Driver if it is running on the File Master.
  23. Go into the DbCreate Editor and perform a Database "Restore" to place the saved database back in the File Master.
  24. Promote the File Master PC to the File Master Mode.
  25. Wait until the snapshot is complete.
  26. Promote the Workstation PCs to the Client Mode one at a time.
  27. Wait until the snapshot is complete. Then verify the database was received at the workstation
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 981
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore