MNB Controller blinking-red status LED
  • MNB Controller blinking-red status LED
  • RandyDavis
    RandyDavis
  • JonGreen
    JonGreen
  • sesa119747
    sesa119747
  • sesa116868
    sesa116868
‎2018-09-06 02:50 PM
Last Updated: Commander JonGreen Commander ‎2019-07-22 09:26 AM
MNB Controller firmware upgrade failed, which resulted in the device showing a blinking-red status LED.
TAC IA Series
  • I/A Series MNB Controllers (ASC) (All firmware revisions)
  • Note: This does not apply to the MNB-1000
A blinking-red status LED means the MNB controller is in Boot Loader mode and it cannot reboot. It is now a "slave" unit, listening to traffic, not initiating communication.
  1. Using the WorkPlace Commissioning Tool, click on the File pull-down menu and select "Add MS/TP Slave". If asked to select from IP, Ethernet or MS/TP, select MS/TP. (Note: It's a good idea to have the controller isolated from the trunk, so the firmware upgrade process runs less risk of being interrupted.)
  2. At the prompt for the address, enter the address set on the controller DIP switch. The controller should get added to the list. If it is already in the list, a message will indicate that there's a duplicate address. Answer prompts in such a manner to get the controller added to the list. The 'slave' controller may show up with a blank name.
  3. Do the firmware upgrade again. This procedure works 80% of the time.
  4. If the upgrade fails, put the controller into Dedicated Boot Loader Mode.
  5. Take the controller off the MSTP trunk, set the DIP switch address to 254, cycle power, and try another firmware upgrade (keep it addressed as 254). Following a successful firmware upgrade, set the DIP switch back to the correct controller address and cycle power to the controller.