Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

MNB Controller blinking-red status LED

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • MNB Controller blinking-red status LED
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • JonGreen
    JonGreen
  • sesa119747
    sesa119747
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5385 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

MNB Controller blinking-red status LED

Picard Product_Support
‎2018-09-06 02:50 PM

Last Updated: Commander JonGreen Commander ‎2019-07-22 09:26 AM

Issue

MNB Controller firmware upgrade failed, which resulted in the device showing a blinking-red status LED.

Product Line

TAC IA Series

Environment

  • I/A Series MNB Controllers (ASC) (All firmware revisions)
  • Note: This does not apply to the MNB-1000

Cause

A blinking-red status LED means the MNB controller is in Boot Loader mode and it cannot reboot. It is now a "slave" unit, listening to traffic, not initiating communication.

Resolution

  1. Using the WorkPlace Commissioning Tool, click on the File pull-down menu and select "Add MS/TP Slave". If asked to select from IP, Ethernet or MS/TP, select MS/TP. (Note: It's a good idea to have the controller isolated from the trunk, so the firmware upgrade process runs less risk of being interrupted.)
  2. At the prompt for the address, enter the address set on the controller DIP switch. The controller should get added to the list. If it is already in the list, a message will indicate that there's a duplicate address. Answer prompts in such a manner to get the controller added to the list. The 'slave' controller may show up with a blank name.
  3. Do the firmware upgrade again. This procedure works 80% of the time.
  4. If the upgrade fails, put the controller into Dedicated Boot Loader Mode.
  5. Take the controller off the MSTP trunk, set the DIP switch address to 254, cycle power, and try another firmware upgrade (keep it addressed as 254). Following a successful firmware upgrade, set the DIP switch back to the correct controller address and cycle power to the controller.
Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 2942
  • RandyDavis19
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of