Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

BACnet proxy points and BACnet devices are configured to use COV subscriptions however points are listed as Polled when added to database.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet proxy points and BACnet devices are configured to use COV subscriptions however points are listed as Polled when added...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa116873_brid
    sesa116873_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
7541 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet proxy points and BACnet devices are configured to use COV subscriptions however points are listed as Polled when added to database.

Picard Product_Support
‎2018-09-06 10:38 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-07-12 08:53 AM

Issue

BACnet proxy points and BACnet devices are configured to use COV subscriptions however points are listed as Polled when added to database.

Product Line

TAC IA Series

Environment

Niagara G3 all version, ENC-520, ENC-410

Cause

The "Use Cov" property is set to false in the BACnetNetwork Default Tuning Policy.

The "Use Cov" property default is "False." If set to "True," and the assigned proxy points are under a BacnetDevice that supports the Subscribe COV service, any necessary updates (Niagara proxy subscriptions) are attempted using BACnet COV subscriptions to the device. If the subscription attempt succeeds, the "Read Status" property of the point's BacnetProxyExt displays "COV." If the subscription attempt for a proxy point fails, normal polling is used and the "Read Status" property shows "Polled."

Resolution

The "Use Cov" property must be set to true for COV subscription to function. It’s a good idea to create a separate tuning policy for BACnet COV subscriptions.

Creating a new Tuning Policy

  1. Expand Tuning Policies under the BACnetNetwork
  2. Right-clicking an existing policy, then choosing "Duplicate" in the shortcut menu. "Name" it as desired.
  3. Open the tuning policy you just created
  4. Set "Use Cov" to true and save.

Assigning the new tuning policy to the proxy points under the BACnetDevice that is configured for COV subscriptions.

  1. Expand the Points folder of the BACnet Device
  2. Double-click on the proxy point you wish to configure to use Cov
  3. Click on the drop down menu next to Tuning Policy Name and select the tuning policy you created. Save.

Configuring the BACnetDevice to use COV

  1. Open the BACnetDevice under the BACnetNetwork
  2. Set the "Use Cov" property to True.

Note: Typically, you create multiple tuning policies in the BACnetNetwork—especially if you have multiple BACnet network ports enabled. This allows you to reference different tuning policies from BACnet proxy points under different networks (often with vastly different performance capabilities). For example, points under a BACnet MSTP network would likely use different tuning policies than those under a BACnet IP network.

Reference the "About BACnet Tuning Policies" section of the Niagara AX-3.x BACnet Guide document for additional information.
 

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 12603
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore