Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,855
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 476
    • 477
    • 478
    • …
    • 509
  • Next »

SpaceLogic SLO/SLR Label showing incorrect kL range value

Warning Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source. Issue The SLO Label shows an incorrect value range for kL. Product Line Field Devices Environment SpaceLogic SLO series Lux sensor Cause The label on the SLO shows the incorrect value range for kL. Resolution SLO: The product specification sheet states the Ranges for the jumper as: - 0 to 500 lx and 0 to 20 kLx The range to 500 lx can be seen on the circuit board. The product’s label shows 0 – 4kL The manufacturer has confirmed the label is incorrect the value should be 500 lx, New labels will be used in production from August 2022.   SLR: The tense delivery situation during the pandemic, especially for electronic components, has forced the manufacturer to make technical changes to the SLR in order to stay able to continue to deliver reliably. The range has extended from 0.4 to 0.5 kLux. These changes are incorporated in the corresponding instructions, provided with the devices. New labels will show the extended range.
View full article
Gary Schneider Alumni (Retired)
‎2022-08-24 08:37 AM

Labels:
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • TAC Vista
932 Views

Template for TAC Xenta 102-B, Xenta 102-VF and TAC Xenta 102-EF

Issue What template to use for TAC Xenta 102-B What template to use for TAC Xenta 102-VF What template to use for TAC Xenta 102-EF Environment TAC Xenta 102-B TAC Xenta 102-VF TAC Xenta 102-EF Cause The Xenta 102-B TAC Xenta 102-VF and TAC Xenta 102-EF uses the same template. Resolution Use the TAC Xenta 102 template
View full article
Picard Product_Support
‎2018-09-06 11:00 AM

Labels:
  • TAC Vista
978 Views

Control signal Xenta102B.

Issue What is the control signal to the actuator for a Xenta 102B? Environment Xenta 102B Cause The 102B is designed to be used with a Belimo actuator. This is why the out signal is not specified anywhere in the documentation.   Resolution The out control signal to the actuator is 0-10V.  
View full article
Picard Product_Support
‎2018-09-06 11:00 AM

Labels:
  • TAC Vista
911 Views

Meter Consumption calculation type does not generate log records

Issue On an existing trend log, the calculation type can be set to the “Meter Consumption”, but this does not generate any log records. Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Cause The “Set initial meter” under the “Meter Info” tab has been set to false when the trend log was initially created. Resolution The following image demonstrates the issue. The “Is meter log” is false because in the trend log creation process the “Set initial meter” has been set to false. This causes the “Meter Consumption” calculation type does not generate any log records. To resolve this: Create another Trend log with the “Set initial meter” set to true Or Right-click on an existing trend log (with “Is meter log” = false), press manage meter, configure the required settings, and then press save. This will change the “Is meter log” to true  Now, if the calculation type is set to “Meter Consumption” on the trend log, the log records are getting populated.
View full article
Lt. Commander Reza Lt. Commander
‎2022-04-12 01:19 PM

on ‎2022-04-12 01:19 PM

Labels:
  • EcoStruxure Building Operation
984 Views

Accessing non bindable b3/i2 object properties in Script

Issue Some of the Continuum attributes in b3/i2 objects are not listed for binding in Script, one such example is the ElecValue of an input object, in Continuum, the difference between the Value attribute and ElecValue attribute is the former is the software value while the latter is the actual value read from the sensor. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Cause For reasons that are beyond the scope of this article, not all Continuum properties have been included for binding in Script   For example, the list of bindable properties for a b3 Analog Input is missing the ElecValue property as can be seen below   Resolution In a b3 Script or Infinet Script Program, there is a way to access any property (attribute as they are known in Continuum) of an object by simply referencing the property's name right after a binding variable to the object's value   Consider the situation that can be seen in the screen capture below...     Due to some strange failure the software contains an incorrect value for the input, but accessing the input's electrical value from a b3 Script program reveals the sensor is reading the room temperature correctly.   Below, screen capture of how this is accomplished in b3/i2 Script program     NOTES "theInput" is bound to the value of the "RoomTemperature" input. "theInElecValue" is bound for output to an AnalogValue in the b3 where the program will place the electrical value of the input We access the property by adding its Continuum attribute name right after the variable bound to the input's value, you will need to know the exact Continuum name of an object's attribute in order to access it this way. This works for any attribute that is accessible by Plain English in Continuum including the PriorityArray of b3 commandable objects.
View full article
Captain AbeMeran Captain
‎2022-02-10 03:49 PM

on ‎2022-02-10 03:49 PM

Labels:
  • EcoStruxure Building Operation
957 Views

Updating Firmware of SP-MNR2

Issue Unable to find firmware update instructions in the SP-MNR2 installation guide Product Line EcoStruxure Security Expert Environment Security Expert Controller Security Expert SP-MNR2 Cause TFTP is needed to upgrade firmware Resolution What you need: TFTP WinAgent software (tftp.exe) PRT-MNR2-DIN firmware Download these files to the same folder(ex c:\fw) Steps: log into SP-MNR2's built-in web interface (default: 192.168.1.3) (if you are having trouble connecting to the interface, review the SP-MNR2 installation guide p.16-18) Browse to the MNR2 module and select the ‘Device’ page. Put the module into boot mode as seen below Open Command Prompt (Win key+R; cmd, Enter) Type: cd c:\fw Then Type: tftp -v -i <MNR2_IP_address> PUT <MNR2_Firmware_Filename.bin>   The command window should fill up with ‘packet received’ messages while the file transfer is being processed. Bring your SP-MNR2 back online. You should find that the firmware version is now updated
View full article
Lieutenant JG JamesMorgan Lieutenant JG
‎2022-08-03 11:25 AM

on ‎2022-08-03 11:25 AM

Labels:
  • EcoStruxure Security Expert
928 Views

UI-8-10 does not update input values in Continuum.

Issue UI-8-10 module is reporting no change of state on inputs when shorted. Environment UI-8-10 Cause Setting the voltage range switch to 10V when the Reference Resistor is in the on position is an invalid configuration. Resolution Change the voltage range settings to 5v on the input.
View full article
Picard Product_Support
‎2018-09-06 10:50 AM

Labels:
  • Andover Continuum
907 Views

Print menu is greyed out on the graphics menu when the a user is logged in

Issue Print menu is greyed out on the graphics menu when the a user is logged in   Environment Sigma Cause Print menu is grayed out on the graphics menu when the user is logged in Resolution In System Setup, go to User Groups, highlight the User Account required. In Basic Settings, enable "Logged On" This will enable the print functions to work for all users associated to this account.
View full article
Picard Product_Support
‎2018-09-06 10:49 AM

Labels:
  • Satchwell BAS & Sigma
928 Views

Controller hardware with battery/clip connection

Issue What is the purpose of the battery/coin clip on some of the I/NET Hardware Product Line TAC INET Environment TAC INET Hardware  7718, 7716, 7798C  Cause The initial development path plan was to include an additional feature to allow communication with Dallas Semiconductor ID tag/coin, similar to that used with the I/NET Access Control I/DISC.  This development was never implemented Resolution This battery/coin tag serves no active purpose or functionality
View full article
Guinan RobertAndriolo Guinan
‎2021-09-16 08:42 PM

on ‎2021-09-16 08:42 PM

Labels:
  • TAC INET
909 Views

MS41 SmartX Damper Actuator Replacement

Issue Replacements for Schneider-Electric SmartX MS41 Damper Actuator Product Line Field Devices Environment SmartX MS41 Cause Replacement of SmartX MS41 Damper Actuators within the Schneider-Electric range Resolution Outgoing Actuator Model          Replacement Model (Part Number)       MS41-6083-G00                        MD10A-24 (875 1019 000)       MS41-6153-G00                        MD20A-24 (875 1029 000)       MS41-6153-G10                        MD20A-24 (875 1029 000)       MS41-6153-G12                        MD20A-24 (875 1029 000) + Aux Switch (914 1061 000)
View full article
Admiral David_Kendrick Admiral
‎2021-09-10 12:58 AM

Last Updated: Sisko DavidChild Sisko ‎2021-09-10 01:04 AM

Labels:
  • Field Devices
996 Views

Using multiple tags in Access Expert acts as though there are no tags

Issue Permissions are set with multiple tags as the following:      When the user logs into Access Expert and looks at the hardware tree, they are able then to see all the hardware on the instance rather than just those with the matching tags. Product Line EcoStruxure Access Expert Environment Access Expert Hosted Software Access Expert Premise Software Cause The tags are meant to be on separate permissions and shouldn't be used on the same individual permission Resolution Tags and permissions should be set up as illustrated:
View full article
Commander JonGreen Commander
‎2021-09-07 12:54 PM

on ‎2021-09-07 12:54 PM

Labels:
  • EcoStruxure Access Expert
911 Views

Disable alarm using the status of another object / point

Issue Disable alarm using the status of another object / point Environment I/A Series G3 Workbench Cause Alarms are not required to be generated when equipment is not running. As an example, alarms should not be generated when the equipment is not running after hours.  Resolution Object alarm extensions have an 'Alarm Inhibit' property which a Boolean object can be linked to. A true value at the 'Alarm Inhibit' prevents alarm generation due to any transition or state change.  The Alarm Inhibit property is within the alarm extension. As such, it is not visible on the parent object and therefore, unlinkable. We can expose properties of an extension by using the 'Composite' function. After adding an extension to a Control object. Right click on the object and select 'Composite'. The Composite Editor window will appear.   In the Composite Editor, expand the object and the extension.   Find 'Alarm Inhibit' and double click on it. Alarm Inhibit will be added to the right of the Composite Editor window. You can rename it if required. Click OK.   The Alarm Inhibit property will now be available on the parent object and linkable from a Boolean object. 
View full article
Picard Product_Support
‎2018-09-10 11:18 PM

Labels:
  • TAC IA Series
921 Views

A computer running UltiVist locked up and was rebooted. Each reboot brings it right back to its locked up state.

Issue A computer running UltiVist locked up and was rebooted.  Each reboot brings it right back to its locked up state.  How can this be prevented? Environment OS/2 UltiVist Cause A task or program does not execute properly and causes OS/2 to lock up with no response from keyboard or mouse. Resolution Boot up from the installation diskettes to gain access to a command prompt.  On the hard drive, modify the config.sys file to include the following lines: set restartobjects=startupfoldersonly set autostart=programs,tasklist,folders,warpcenter These lines will prevent the computer from running programs or tasks that lead to its locked up state.
View full article
Picard Product_Support
‎2018-09-06 10:45 AM

Labels:
  • TAC IA Series
907 Views

Longtext number is seen when a DI Object is displayed in System Manager and the object does not have an alarm.

Issue A Longtext number is seen when a DI Object is displayed in System Manager when an Alarm is not configured on the object  Environment Sigma Cause A Longtext number is seen when a DI Object is displayed in System Manager when an Alarm is not configured on the object. This does not occur with AI objects. Resolution An alarm on the DI object with Longtext may have been configured in the past and assigned with a Longtext number. To prevent the Longtext from being displayed: 1. Re-enable the alarm, set the Longtext number on the alarm tab to "0" 2. Disable the alarm 3. Download the Object to the controller.
View full article
Picard Product_Support
‎2018-09-10 11:24 PM

Labels:
  • Satchwell BAS & Sigma
913 Views

Auto Generated Reports not running in 64-bit Environment

Issue Auto Generated Reports not running in 64-bit Environment Environment I/NET 2.43 64-bit I/NET 2.42 64-bit Cause Issue with windows scheduler is causing Auto Generate reports to fail. Resolution Modify existing or newly created auto generate reports. Click on the Recurrence button On the "Task" Tab, modify the "Run" string. At end of the string you will notice sch=<ScheduleName>. Add the characters"/T0" or "-T0" as shown below Before:   After:
View full article
Picard Product_Support
‎2018-09-11 12:54 AM

Labels:
  • TAC INET
991 Views

Dual credential fields aren't showing in webclient

Issue The ability to add a second card is available in webclient, but there is no where to add the second card Environment Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause Steps are needed to configure dual credentials to show in webclient, but those steps have not been completed. Resolution Steps to configure dual credential access in webclient: 1. Right click on Continuum icon in the system tray and select Allowed Credentials and select 'Credential1And2' Note: Say yes to enable on the controllers and distribute 2. Open Personnel Manager, click configure, click the right arrow to add ‘Card#2’ and ‘Card2 Type’, click Ok 3. Once that is done, go back into webclient and you will now see an additional tab added called ‘Credential2’
View full article
Picard Product_Support
‎2018-09-06 10:36 AM

Labels:
  • Andover Continuum
931 Views

Error "HRDB Tree View has stopped working" when adding a Network in TreeTech

Issue After creating a new Project and a new E: Equipment Database in TreeTech, the following error message appears when adding a new Network: Product Line TAC IA Series Environment Windows 7 TreeTech Cause TreeTech requires administrative rights to the Windows user account Resolution Right-click on the TreeTech shortcut Select 'Run as Administrator'
View full article
Picard Product_Support
‎2018-09-11 12:55 AM

Labels:
  • TAC IA Series
926 Views

Can the AS be positioned in the middle of the mstp bus?

Issue Typically the master controller is at the end of the bus, but is it possible to place it in the middle? Environment AS b3 Cause Depending on the buildings wiring there could be a need to place the AS in the middle of the bus. Resolution The AS can be placed in the middle of the bus, but the terminating resistors must then be placed at both ends of the bus. This method wasn't officially tested in this manner by SQA, but it works similar to how a BCX 4040 does which can be placed in the middle of the bus in this fashion.
View full article
Picard Product_Support
‎2018-09-06 10:33 AM

Labels:
  • EcoStruxure Building Operation
903 Views

How to force a user action in StruxureWare when an alarm is generated in I/NET.

Issue Is there a way to activate a function which requires a cause note, action note to be added to every I/NET alarm? Environment I/NET SmartStruxure Alarm User Action Cause Need to document user actions in SmartStruxure when an I/NET alarm changes state. Resolution Create a Change of State alarm and bind it to the I/NET alarm object in SmartStruxure. Create a Change of State alarm. On the User Action page of the alarm configuration attach a Cause Note Group, Action Note Group or Checklist. Bind the alarm object to the Alarm attribute of the I/NET Value.
View full article
Picard Product_Support
‎2018-09-06 10:33 AM

Labels:
  • Andover Continuum
  • TAC INET
909 Views

Linkage kits to be used with Satchwell ALE (s) , ALi, ALX (s), ALM (s) on Schneider Electric Venta V and VG Valve bodies

Issue Linkage kits to be used with Satchwell ALE (s) , ALi, ALX (s), ALM (s) on Schneider Electric Venta V and VG Valve bodies Environment Linkage Kits Cause Linkage kits to be used with Satchwell ALE (s) , ALi, ALX (s), ALM (s) on Schneider Electric Venta V and VG Valve bodies. Resolution Use the L8TV linkage kit part no. 914-1080-000 on V type valve bodies e.g. V211, V211T, V311, V311T, V231, V241, V212, V222, V232, V292, V341 Use the L9TVG linkage kit part no. 914-108-000 on VG type valve bodies e.g. VGS211F, VG221F, VG311F
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Labels:
  • Field Devices
983 Views
  • « Previous
    • 1
    • …
    • 476
    • 477
    • 478
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.