Warning
Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.
Issue
The SLO Label shows an incorrect value range for kL.
Product Line
Field Devices
Environment
SpaceLogic SLO series Lux sensor
Cause
The label on the SLO shows the incorrect value range for kL.
Resolution
SLO:
The product specification sheet states the Ranges for the jumper as: -
0 to 500 lx and 0 to 20 kLx
The range to 500 lx can be seen on the circuit board.
The product’s label shows 0 – 4kL
The manufacturer has confirmed the label is incorrect the value should be 500 lx,
New labels will be used in production from August 2022.
SLR:
The tense delivery situation during the pandemic, especially for electronic components, has forced the manufacturer to make technical changes to the SLR in order to stay able to continue to deliver reliably.
The range has extended from 0.4 to 0.5 kLux.
These changes are incorporated in the corresponding instructions, provided with the devices.