Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 15
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 31
    • 32
    • 33
    • …
    • 508
  • Next »

Field Devices - What is the replacement actuator for the EM42?

Issue What is the replacement actuator for the EM42? Environment EM42 Actuator Cause The EM42 is obsolete. Resolution The EM42 actuator is generally associated with the V280/290, and the V380/390 series valves. The replacement actuator for the EM42 is the Schneider Electric Forta M310 Actuator. Please note that an adaptor kit (880-0252-000) is required for DN15 valves. For a copy of the EM42 data sheet please click HERE. For a copy of the M310 data sheet please click HERE.
View full article
Picard Product_Support
‎2018-09-10 11:29 AM

Labels:
  • Field Devices
3858 Views

Contact info for United Kingdom Schneider Electric Buildings Business Order Entry

Issue Contact info for Schneider Electric Buildings Business Order Entry in the UK Environment Purchasing UK Price and Delivery information Cause For all questions from end users, pricing and delivery information. Resolution UK CCC in Telford: Phone 0870 608 8608 Email OrderEntry.UK@Schneider-Electric.com
View full article
Picard Product_Support
‎2018-09-11 03:52 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
3856 Views

Unable to register EBO site's new system ID

Issue When using EBO's registration page, the registration website that is opened allows the user to login and enter the new system ID, however, the user then cannot proceed any further. Product Line EcoStruxure Building Operation Environment Building Operation WorkStation Cause The link https://registration.smartstruxure.schneider-electric.com/, which redirects to the https://registration.smartstruxure.schneider-electric.com/WebConnectUI/RegisterUser/home This page may not allow the user to complete the site’s registration with the new system ID. Resolution Register the site’s EBO new system ID using the following website address. https://registration.smartstruxure.schneider-electric.com/ebo/Home
View full article
Gary Schneider Alumni (Retired)
‎2021-04-09 05:44 AM

Labels:
  • EcoStruxure Building Operation
3801 Views

Trouble configuring zero Box Flow on MP-V controllers

Issue In an MP-V controller, Box flow is reading air flow when the VAV damper is closed Product Line EcoStruxure Building Operation Environment Building Operation Multi-purpose VAV FW v2.00.01.00016 Building Operation Workstation (Version 2.0.x or later) Cause Confinguring the MP-V Box Flow Zero Point WebHelp article in Building Management System WebHelp is missing steps needed for MP-V with firmware version 2.00.01.00016. Resolution In addition to the procedure described in Configuring the MP-V Box Flow Zero Point, two additional steps are required to zero the Box flow on an MP-V using firmware version 2.00.01.00016. Under Flow Balance Data... The Box Measured maximum flow must be an appropriate value based on the box size.  The Hood Measured maximum flow must be an appropriate value based on the box size. Once the procedure in WebHelp is followed and these to settings are configured, the Box Flow will read zero when the Velocity Pressure is below the Minimum value setting in Velocity Pressure properties.   If the Box Flow is still a non-zero value: While the damper is closed, put in an offset value to counter the Box Flow Make sure that the minimum value setting is a small positive value ex/ 0.002
View full article
JohnBoehmer Schneider Alumni (Retired)
‎2019-06-27 09:45 AM

Last Updated: Commander JonGreen Commander ‎2020-05-06 01:18 PM

Labels:
  • EcoStruxure Building Operation
3867 Views

Is there a conduit box accessory for the I/A Series VAV controllers?

Issue Some jobsites require the use of conduit for all wiring between controllers. Is there a specific enclosure made for this purpose?  A general purpose enclosure such as the ENCL-100 can be used but must be punched or drilled to fit the damper shaft. Product Line TAC IA Series Environment MN-FLO / MN-FLO3T MNL-V1RVx / MNL-V2RVx MNB-Vx Cause Installation manual with reference to part number was misplaced. Resolution MNA-FLO-1 This enclosure is listed as an optional item in the installation manuals for all VAV controllers listed above. Click here to see F-26282-5, Installation Instructions for the MNL-V1RVx and MNL-V2RVx. Click here to see F-27346-4, Installation Instructions for the MNB-V1 and MNB-V2 Click here to see F-25718-6, Installation Instructions for the MN-FLO and MN-FLO3T
View full article
Picard Product_Support
‎2018-09-06 02:03 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-15 08:51 PM

Labels:
  • TAC IA Series
3811 Views

DC1100 / DC1400 - Changes to the Set Space Temperature do not work.

Issue Changes to the Set Space Temperature do not work. Environment DC1100 DC1400 Controller Compensator Optimiser Setpoint Cause The pump overrun is timing down and will not allow the controller to act normally until it is complete. Resolution If the "Set Space Temperature" value is modified, then after the rotary switch is returned to "Auto", the user must wait until the Pump Overrun function has timed out. Where adjustments are generally being made, it is recommended that the Pump Overrun setting is set to 1 minute until  testing has been completed, after which it should be return to its required setting. To change the Pump Overrun setting carry out the following: Turn the rotary switch to "Setup". Select "System Menus" then "Alter Settings", and then enter the password of 0112. Select "Compensator", then "Set-up Menu", and then "Pump Overrun". Note the current value then change it to 1. On completion of the tests return the setting to its correct value. For the DC1100 data sheet, click here. For the DC1400 data sheet, click here.
View full article
Picard Product_Support
‎2018-09-10 04:06 AM

Labels:
  • Field Devices
3821 Views

Access controller configuration on a Generation 1 controller

Issue Since Generation 1 controllers do not have a controller webpage, how can I access the controller configuration to set up the controller or access controller information. Product Line Andover Continuum Environment Hyper Terminal CX9900 CX9940 CX9400 CX9410 CX9200 Cause 1st Generation Controllers do not have an embedded webpage. Resolution Find information about the pin configuration of the direct connection cable in PinOuts for the RS-232 Connection of the older 1st Generation CX controllers. The following document describes how to log into a generation 1 controller via a PC with a terminal emulation application: CX Operators Guide.pdf
View full article
Picard Product_Support
‎2018-09-10 04:45 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 10:45 PM

Labels:
  • Andover Continuum
3867 Views

Field Devices - General configuration of the DC1100 / DC1400 Optimiser Compensator.

Issue General configuration for these controllers. Environment Drayton DC1100 Satchwell DC1400 Cause Access to the documentation unavailable and uncertain of the correct configuration. Resolution The available controller configurations are all shown in the controller data sheets, please select the required data sheet below. To review the Drayton DC1100 general data sheet, please click HERE. To review the Drayton DC1100 "A" data sheet, please click HERE. To review the Satchwell DC1400 general data sheet, please click HERE. To review the Satchwell DC1400 "A" data sheet, please click HERE. For a general overview of the DC1100/DC1400, please click HERE.
View full article
Picard Product_Support
‎2018-09-11 07:53 AM

Labels:
  • Field Devices
3826 Views

Error Codes: The Error Sys Var has been incremented or GLB_ELOG_DUP_START

Issue Error Codes: Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2 1631 E 04/05/2012 10:55:30.00 0x0000640b 0x04dd8500 0x02124e26 0x00005c20 0x00000000  Error Code Meaning: The Error Sys Var has been incremented Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2 1632 E 04/05/2012 10:57:30.00 0x00001c0b 0x04dd8500 0x02124e26 0x0000640b 0x00000000  Error Code Meaning: GLB_ELOG_DUP_START Product Line Andover Continuum Environment Continuum Site with BCX Controllers and an Error Log Cause Crash of BCX and log reveals: Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2 1629 E 04/05/2012 10:51:30.00 0x0000640b 0x04dd8500 0x02124e26 0x00005c20 0x00000000 Error Code Meaning: The Error Sys Var has been incremented Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2 1630 E 04/05/2012 10:53:30.00 0x0000640b 0x04dd8500 0x02124e26 0x00005c20 0x00000000  Error Code Meaning: The Error Sys Var has been incremented Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2 1631 E 04/05/2012 10:55:30.00 0x0000640b 0x04dd8500 0x02124e26 0x00005c20 0x00000000  Error Code Meaning: The Error Sys Var has been incremented Line Level Time Stamp Error Code TCB Addr Prg Cntr Data1 Data2 1632 E 04/05/2012 10:57:30.00 0x00001c0b 0x04dd8500 0x02124e26 0x0000640b 0x00000000  Error Code Meaning: GLB_ELOG_DUP_START Resolution It is in the range of “Global System errors” that is usually not good, either faulty controller or need reloading of the O/S. Cold start and update O/S with the latest version supported by the Cyberstation version. Then run it on a test rig with different ID and see if it still crashes, if so will need to be repaired or replaced.
View full article
Picard Product_Support
‎2018-09-10 09:05 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:16 PM

Labels:
  • Andover Continuum
3854 Views

EcoStruxure Building Operation WorkPlace Tech Editor Supported Microsoft Visio Versions

Issue EcoStruxure Building Operation WorkPlace Tech Editor Supported Microsoft Visio Versions The following error context is encountered when trying to run WorkPlace Tech Editor to edit a program: WorkPlace Tech Editor returned errorClass not registered 0x80040154 REGDB_E_CLASSNOTREG Product Line EcoStruxure Building Operation, TAC I/A Series Environment EcoStruxure Building Operation WorkPlace Tech Editor I/A Series MNL, MNB Controllers (MNB - from SBO v1.8.1 and newer) Cause Only the 32-bit versions of Microsoft Visio is supported for use with WorkPlace Tech Editor. The error is seen when a 64-bit version of Microsoft Visio 2010 is installed. Resolution Currently, only 32-bit versions of Microsoft Visio is supported for use with WorkPlace Tech Editor. SBO 1.5, 1.6, 1.7 Microsoft Office Visio 2010 SP1, 2007 SP2, 2003 SBO 1.8 Microsoft Office Visio 2010 SP1 (32-bit), 2007 SP2, 2003 SBO 1.9, EBO 2.x, 3.x Microsoft Office Visio 2016 (32-bit), 2013 (32-bit), 2010 SP1 (32-bit) EBO 2022 Microsoft Office Visio 2021 (32-bit), 2019 (32-bit), 2016 (32-bit), Microsoft Office Visio Plan 2 (32-bit) EBO 2023 Microsoft Office Visio 2021 (32-bit), 2019 (32-bit), 2016 (32-bit), Microsoft Office Visio Plan 2 (32-bit) EBO 2024 Microsoft Office Visio 2021 (32-bit), 2019 (32-bit), 2016 (32-bit), Microsoft Office Visio Plan 2 (32-bit)
View full article
Picard Product_Support
‎2018-09-06 03:47 PM

Last Updated: Guinan RandyDavis Guinan ‎2024-12-18 10:23 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
3831 Views

Obtaining a Database Schema for EBO WebReports / Report Server

Issue Where can you obtain the Database Schema for the EBO WebReports / Report Server Database Product Line EcoStruxure Building Operation Environment Building Operation Report Server Cause From EBO version 3.2.x WebReports/RS is no longer being developed as we move to External Log Storage with Postgres and Timescale DB.    To allow our customers to continue to work with existing WebReports/RS databases if they so wish, it may be helpful to provide the DB Schema. Resolution An inbuilt Report already exists within WebReports call 'Database Schema' which allows you to select which Tables you would like to see in the WebReports / RS Database Running this will produce a .pdf Report detailing the RS Database Schema tables, to aid with 3rd Party integrations and other DB manipulation. A full database schema report is attached for reference (Version 3.2.3) 
View full article
Admiral David_Kendrick Admiral
‎2022-03-14 08:36 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-06-07 12:06 AM

Labels:
  • EcoStruxure Building Operation
3876 Views

Modbus Batch Read Multiple Registers Groups

Issue What is the maximum number of registers that can be read/written using the multiple read/write function codes in Modbus Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Modbus Register Groups Cause When deciding how to group registers using a Modbus Register Group, what are the maximum number of registers that can be grouped. Resolution There is a limit to the number of packets that can be polled in a single packet, however, if this number is exceeded then two or more polls will be made (blocks).  The nominal Read multiple registers maximum is 125 16 bit registers (250 8-bit bytes, so the register count will vary for 32 and 64bit polls).  The Register Group Properties Tab shows the number of blocks being polled. The Modbus register grouping function has a direct effect on system performance. A poorly grouped device can easily increase the overall poll time as points, or blocks, in each Modbus network are polled sequentially.  See the section "Batch Read Function" in the EcoStruxure Building Operation Technical Reference Guide for full details. Note: Multiple group writes are not possible and are not controlled via Modbus Register Groups.  
View full article
Picard Product_Support
‎2018-09-06 09:06 AM

Last Updated: Sisko GavinHe Sisko ‎2023-03-31 03:58 AM

Labels:
  • EcoStruxure Building Operation
3870 Views

Calculation for converting static air pressure to cfm

Issue Calculation for converting static air pressure to cfm Product Line TAC INET Environment INET HVAC Site Cause What are the calculations for converting static air pressure to cfm? Resolution SRVP ("water column") * 4005 = FPM (feet per minute). The second calculation is FPM * AreaFtSQ (size of box) = CFM You will need an airflow monitoring device and duct static pressure sensor to measure SRV P (v of Vs of P).
View full article
Picard Product_Support
‎2018-09-06 03:28 PM

Last Updated: Sisko GavinHe Sisko ‎2022-08-25 09:15 AM

Labels:
  • TAC INET
3773 Views

MNL-800 LON SNVT Programming Standards

Issue MNL-800 LON SNVT Programming Standards Environment Workplace Tech Tool software (any version) MNL-800 controller application Cause Problems occasionally arise as a result of improper LON SNVT programming and configuration in the MN-800 device application.  These issues include problems with the re-commissioning of the updated controller and potential network variable mismatch situations. Resolution  The following standards will prevent these problems from occurring. Network variables MUST be manually indexed. This prevents issues with the network variables becoming renumbered when application programming changes are made. (See NOTE 1) Change the application "Program ID" any time network variables are added or removed from an application.  To change the "Program ID" use the WPT Hardware Wizard,  (See NOTE 2) Select Hardware Wizard from Application Menu Click [Next] in MicroNet Setup Wizard screen Change the displayed program ID by entering a different program ID or adding a suffix letter/number. Maximum length is 8 characters. Click [Finish] to save the changed program ID and exit the MicroNet Setup Wizard.  In addition, one method of minimizing the need to repeatedly change the "Program ID" as the application is developed and debugged is to add a few extra common SNVT input and output definitions when first creating the application, leaving them unconnected to the application program.  If one of these SVNTs is needed, it is available in the LON network image (XIF file) and it is not necessary to change the "Program ID". If the MNL-800 controller has firmware version 2.0 (or later) installed, the standard nci network variables do not have to be indexed as the highest numbered SNVTs in the application.  It is perfectly acceptable to number them as the first 17 indexed SNVTs. Note that there are 17 standard network variables (12 nci, 2 nvo & 1 nvi), not just ten nci SNVTs. SNVT variable names should be limited to 16 characters or less.  Longer names are accepted by the WorkPlace Tech programming tool but the names will automatically be truncated by the LON Network Management tool when commissioning the controller. In addition, when programming the MNL-800 applications with the WorkPlace Tech Tool version 5.0, or later, it is not necessary to put each MNL-800 application in a separate project. NOTE 1: If using the WorkPlace Tech Tool version 5.8 or above, you can use the "Object Indexer" to automatically number all the network variables for you.  This tool also includes functions for detecting duplicate SNVT index numbers and for detecting gaps in the assigned index numbers. NOTE 2: If using the WorkPlace Tech Tool version 5.8 or above, you can set an option in the Hardware Wizard to automatically generate a new ProgramID and reindex the network variables when compiling the application.  Please be aware that this automatic generation of the ProgramID will require the Echelon network image for this device to be updated in any Echelon compatible network management tool.  Please refer to the documentation for the network management tool to determine what actions will be required. For example, if Niagara was used to manage the LON network, then the old shadow will need to be deleted, a new one added, and the device points rediscovered and the device re-commissioned.  
View full article
Picard Product_Support
‎2018-09-06 02:50 PM

Labels:
  • TAC IA Series
3779 Views

How to Export a Trend Log List as a .csv File

Issue Need to Export a Trend log file without using Reports Server Product Line EcoStruxure Building Operation Environment SmartStruxure Workstation Cause Customer needs a log file, but does not have Report Server Resolution In Workstation, right click on a Trend and create a new Trend Log List View Once the List populates, click on the Icon showing a green arrow labeled .csv Save the file to an appropriate location. If this is a frequent action, save the Trend Log List View Please Note that this feature is not available in WebStation  At v2.0 WebStation introduced the option to export to Excel, creating an XLSX file, this can be opened in Excel and saved as a CSV if required (this option is not available if WebStation is directly logged on to the AS/P/B)
View full article
Picard Product_Support
‎2018-09-06 10:27 AM

Labels:
  • EcoStruxure Building Operation
3798 Views

WebReport login errors.

Issue Receive an error: "The user session is lost, no specific reason has been set." when logging into StruxureWare Building Operation WebReports from Internet Explorer (browser), while Reports from within Workstation work fine.  Receive an error: "The user session is lost, no specific reason has been set." when logging into StruxureWare Building Operation WebReports from Internet Explorer (browser), and get no Reports folder within Workstation. Login Screen appears as expected, but when attempting to log in with the user name/password; It times out and comes with the message 'Failed to establish connection with server.' Product Line EcoStruxure Building Operation Environment Building Operation WebReports 1.1 / 1.2 Cause The error is most likely due to ports been blocked and/or the incorrect port settings entered during the WebReports installation process. When installing (or upgrading) WebReports, you must enter this information on each occasion as this information is not retained from previous installations. If you need to change these settings, then you should follow the procedure detailed below. Resolution If installed on separate machines, then check the firewall settings and ensure the ports used for the Enterprise Server and the Report Server are not blocked.  If this does not resolve the issue or if you are running both the Enterprise Server and Report Server on the same PC, then the Enterprise Server port configuration during the WebReports installation may need to be changed.  This is achieved as follows: this, and follow these key steps: Run the WebReports Installation setup program, and at the Setup Type prompt, select Upgrade from... Proceed through the other options as normal. Once you reach the Reporting Agent setup, make sure you enter the correct URL (path and port number - this is unique for each installation) used during the Enterprise Server setup. Continue through the other settings as required - Ensure that any Path and URL ports are set correctly.  Once you complete these settings, the WebReports Installer package then goes through the following checks and installation: Checking Installation Requirements Pre-upgrade Configuration Installation of Reporting Agent, WebReports, and WebReports Service Post-Installation Configuration Installation PublishedReports After the above steps, the upgrade is completed. This will now allow login to the WebReports URL using your web browser. For additional assistance in installing/upgrading WebReports, refer to the online help website. 
View full article
Picard Product_Support
‎2018-09-10 08:16 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2021-07-22 06:24 PM

Labels:
  • EcoStruxure Building Operation
3792 Views

Trend intervals with StruxureWare Building Operation

Issue What are the intervals for Trends when using StruxureWare Building Operations Product Line EcoStruxure Building Operation Environment Enterprise Server or Automation Server Cause Questions regarding what the interval in time is for trending Resolution Intervals can be in Days, Hours, Minutes, Seconds, and Milliseconds. . Trend logs can be of different types and used for different purposes. All logs in StruxureWare use circular storage. The interval trend log collects data at a specific time interval. Each logged value is stored as a record in the trend log. Use this trend log when the logging interval is less than 1 hour. You create interval trend logs using WorkStation or WebStation. In WorkStation, you configure the properties of the interval trend log to meet the specific needs of your site. The interval trend log does not record the values between the intervals. An interval log checks the monitored value at each interval and records the new value if it differs from the previously recorded value by more than the delta. Delta is the difference between the current variable value and the last log value. To log a variable according to the time interval, use a delta of zero. You use an extended trend log to transfer records from a trend log. An extended trend log can be connected to a trend log or connected in a series to another extended trend log. Only one extended trend log can be connected to a trend log. You create and configure extended trend logs using WorkStation. The extended trend log is often saved on a higher server level with more storage capacity than the server of an ordinary trend log. This extra storage capacity enables the server to store more records before it overwrites old ones. The extended trend log can be viewed in a trend log list or a trend chart. Trend log lists and records can be exported in two different formats: CSV (Comma separated values) is a standard file format for digital storage of data structured in a table of lists form. The CSV format can be used by Excel and in databases such as SQL. XML (Extensible Markup Language) is a standard file format for structured data and can be use with a lot of different tools. One last suggestion is the number of records, depending on how many records you want to store is important. For example: a single one minute interval Trend Log, and for 66 day, that would be 99,792 records. The maximum is 100,000 on an AS, so take this into account when configuring. This is why Extended Trend Logging is important. Check out Maximum number using StruxureWare Building Operation (Scalability and Capacity) for information on trends and extended trendlogs.
View full article
Picard Product_Support
‎2018-09-10 10:28 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:49 PM

Labels:
  • EcoStruxure Building Operation
3756 Views

After copying the px file from G3 (Niagara) a station to another station's file, I cannot view the px, instead receive an error: "java.io.EOFException at javax.baja.xml....

Issue java.io.EOFException    at javax.baja.xml.XParser.read(XParser.java:753)    at javax.baja.xml.XParser.parseString(XParser.java:555)    at javax.baja.xml.XParser.parseAttr(XParser.java:492)    at javax.baja.xml.XParser.parseElemStart(XParser.java:421)    at javax.baja.xml.XParser.next(XParser.java:262)    at javax.baja.xml.XParser.parseCurrent(XParser.java:146)    at javax.baja.xml.XParser.parse(XParser.java:119)    at javax.baja.xml.XParser.parse(XParser.java:102)    at javax.baja.ui.px.PxDecoder.decodeDocument(PxDecoder.java:77)    at javax.baja.ui.px.PxDecoder.decodeDocument(PxDecoder.java:64)    at javax.baja.workbench.px.BWbPxView.loadPx(BWbPxView.java:176)    at javax.baja.workbench.px.BWbPxView.doLoadValue(BWbPxView.java:90)    at javax.baja.workbench.BWbEditor.loadValue(BWbEditor.java:233)    at com.tridium.workbench.shell.NHyperlinkInfo.loadView(NHyperlinkInfo.java:563)    at com.tridium.workbench.shell.NHyperlinkInfo.hyperlink(NHyperlinkInfo.java:100)    at com.tridium.workbench.shell.BNiagaraWbShell.doHyperlink(BNiagaraWbShell.java:350)    at com.tridium.workbench.shell.BNiagaraWbShell.hyperlink(BNiagaraWbShell.java:316)    at com.tridium.workbench.shell.WbCommands$BackCommand.doInvoke(WbCommands.java:718)    at javax.baja.ui.Command.doInvoke(Command.java:303)   Environment G3 (Niagara) station with px files, any revision level. Cause The px file did not copy correctly. Resolution There are three possible approaches to recover from this situation, as follows: Try copying the file again.   Open the px file with a text editor. It might be possible to determine what was either not copied at all, or what might have been corrupted during the copying process. The example shown below is part of the BoilerRoom.px file from niagara-3.6.47 \ stations \ demo \ px \ plant. Lines 489 through 495 contain 'closing tags' for the Canvas Pane, Scroll Pane, Border Pane, content, and px statements that were opened at an earlier point in the px file. If one or more of these 'closing tags' were not copied, or were somehow corrupted during the copying process, the error would result .  If necessary, restore the px file from a backup.
View full article
Picard Product_Support
‎2018-09-06 02:53 PM

Labels:
  • TAC IA Series
3768 Views

Running I/NET Seven as a service on Windows

Issue Running I/NET Seven as a service on Windows Product Line TAC INET Environment I/NET Seven All supported Operating Systems Cause When you log out of Microsoft Windows or restart the computer, all running processes are shut down. These processes are not resumed at log on or at restart. You have to start I/NET manually again. To get I/NET to start up when the computer restarts, you can run it as a service. Running a program as a service means that it runs in the background, but it is not visible on the Windows task bar. Resolution Use the INET Run Mode tool available on the Community.  Alternatively, you can perform the following steps to set/unset the InetIoSrv.exe as a service or application. To register I/NET Seven to run as a service Open a Windows command prompt. Go to Start > Run and type "cmd" Use right-click on the command prompt and select "Run as Administrator" Use commands cd.. (to go back one directory) and cd (to go into a folder) to navigate to the following location: C:\Program Files\INET Seven\ If this is being run on a 64 Bit OS, the location then would be: C:\Program Files (x86)\INET Seven\ Type the following command. This will unregister I/NET as an application inetiosrv /unregserver Type the following command. This will register I/NET to run as a Windows service inetiosrv /service To verify the changes have taken effect Right-click on "My Computer" and select "Manage" Select Services and Applications > Services Look for Inet7Iosrv. It should be set to Automatic. You are now running I/NET as a service. IOSrv will now be running in the background when the PC boots up. This does not require a Log On to the PC, however, you will have to Log On to the PC as a user to launch I/NET or AMT from the desktop icon. You will notice that IOSrv has been logging all AMT transactions, messages and alarms. The SQL Server and Agent were also running in the background receiving data to the database. To set I/NET back to running as an application Open a Windows command prompt. Go to Start > Run and type "cmd" Use right-click on the command prompt and select "Run as Administrator" Use commands cd.. (to go back one directory) and cd (to go into a folder) to navigate to the following location: C:\Program Files\INET Seven\ Type the following command. This will unregister I/NET as a service inetiosrv /unregserver Type the following command. This will register I/NET to run as an application inetiosrv /regserver
View full article
Picard Product_Support
‎2018-09-07 12:15 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2019-09-22 05:53 PM

Labels:
  • TAC INET
3724 Views

Contact Barber Colman

Issue What is the contact information for Barber Colman Dyna group? What is the contact information for Barber Colman Aerospace division? What is the contact information for Barber Colman Industrial Instruments division? Environment Barber Colman Cause The old Barber Colman Dyna group is now a part of Woodward Governor. The old Barber Colman Aerospace division is now a part of the GE Aerospace. The old Barber Colman Industrial Instruments is now part of Eurotherm, an Invensys company. Resolution Barber Colman Dyna group is now Woodward Governor. They can be reached at 800-543-5811 Barber Colman Aerospace division is now GE Aerospace. They can be reached at 815-637-3500 Barber Colman Industrial Instruments is Eurotherm, an Invensys company. They can be reached at 815-637-3222 or 815-637-3404 for tech support.
View full article
Picard Product_Support
‎2018-09-07 02:24 AM

Last Updated: Administrator CraigEl Administrator ‎2021-02-01 02:10 PM

Labels:
  • Field Devices
  • TAC IA Series
3792 Views
  • « Previous
    • 1
    • …
    • 31
    • 32
    • 33
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of