Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Trouble configuring zero Box Flow on MP-V controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Trouble configuring zero Box Flow on MP-V controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • JohnBoehmer
    JohnBoehmer
  • JonGreen
    JonGreen
  • David_Purser
    David_Purser

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3681 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Trouble configuring zero Box Flow on MP-V controllers

JohnBoehmer Schneider Alumni (Retired)
‎2019-06-27 09:45 AM

Last Updated: Commander JonGreen Commander ‎2020-05-06 01:18 PM

Issue

In an MP-V controller, Box flow is reading air flow when the VAV damper is closed

Not Zero.png

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Multi-purpose VAV FW v2.00.01.00016
  • Building Operation Workstation (Version 2.0.x or later)

Cause

Confinguring the MP-V Box Flow Zero Point WebHelp article in Building Management System WebHelp is missing steps needed for MP-V with firmware version 2.00.01.00016.

Resolution

In addition to the procedure described in Configuring the MP-V Box Flow Zero Point, two additional steps are required to zero the Box flow on an MP-V using firmware version 2.00.01.00016.

Under Flow Balance Data...

  • The Box Measured maximum flow must be an appropriate value based on the box size. 
  • The Hood Measured maximum flow must be an appropriate value based on the box size.

BoxFlow Zeroed.png

Once the procedure in WebHelp is followed and these to settings are configured, the Box Flow will read zero when the Velocity Pressure is below the Minimum value setting in Velocity Pressure properties.

 

If the Box Flow is still a non-zero value:

  • While the damper is closed, put in an offset value to counter the Box Flow
  • Make sure that the minimum value setting is a small positive value ex/ 0.002

2020-05-06_16-10-45.png

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • JohnBoehmer19
  • JonGreen20
Was this article helpful? Yes No
100% helpful (7/7)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now