Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

MNL-800 LON SNVT Programming Standards

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • MNL-800 LON SNVT Programming Standards
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support
  • SESA113595
    SESA113595

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3683 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

MNL-800 LON SNVT Programming Standards

Picard Product_Support
‎2018-09-06 02:50 PM

Issue

MNL-800 LON SNVT Programming Standards

Environment

Workplace Tech Tool software (any version)
MNL-800 controller application

Cause

Problems occasionally arise as a result of improper LON SNVT programming and configuration in the MN-800 device application.  These issues include problems with the re-commissioning of the updated controller and potential network variable mismatch situations.

Resolution

 The following standards will prevent these problems from occurring.

  1. Network variables MUST be manually indexed. This prevents issues with the network variables becoming renumbered when application programming changes are made. (See NOTE 1)
  2. Change the application "Program ID" any time network variables are added or removed from an application.  To change the "Program ID" use the WPT Hardware Wizard,  (See NOTE 2)
    1. Select Hardware Wizard from Application Menu
    2. Click [Next] in MicroNet Setup Wizard screen
    3. Change the displayed program ID by entering a different program ID or adding a suffix letter/number. Maximum length is 8 characters.
    4. Click [Finish] to save the changed program ID and exit the MicroNet Setup Wizard.
  3.  In addition, one method of minimizing the need to repeatedly change the "Program ID" as the application is developed and debugged is to add a few extra common SNVT input and output definitions when first creating the application, leaving them unconnected to the application program.  If one of these SVNTs is needed, it is available in the LON network image (XIF file) and it is not necessary to change the "Program ID".
  4. If the MNL-800 controller has firmware version 2.0 (or later) installed, the standard nci network variables do not have to be indexed as the highest numbered SNVTs in the application.  It is perfectly acceptable to number them as the first 17 indexed SNVTs. Note that there are 17 standard network variables (12 nci, 2 nvo & 1 nvi), not just ten nci SNVTs.
  5. SNVT variable names should be limited to 16 characters or less.  Longer names are accepted by the WorkPlace Tech programming tool but the names will automatically be truncated by the LON Network Management tool when commissioning the controller.

In addition, when programming the MNL-800 applications with the WorkPlace Tech Tool version 5.0, or later, it is not necessary to put each MNL-800 application in a separate project.

NOTE 1: If using the WorkPlace Tech Tool version 5.8 or above, you can use the "Object Indexer" to automatically number all the network variables for you.  This tool also includes functions for detecting duplicate SNVT index numbers and for detecting gaps in the assigned index numbers.

NOTE 2: If using the WorkPlace Tech Tool version 5.8 or above, you can set an option in the Hardware Wizard to automatically generate a new ProgramID and reindex the network variables when compiling the application.  Please be aware that this automatic generation of the ProgramID will require the Echelon network image for this device to be updated in any Echelon compatible network management tool.  Please refer to the documentation for the network management tool to determine what actions will be required. For example, if Niagara was used to manage the LON network, then the old shadow will need to be deleted, a new one added, and the device points rediscovered and the device re-commissioned.

 

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 2945
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of