WebReport login errors.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • WebReport login errors.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4184 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

WebReport login errors.

Picard Product_Support
‎2018-09-10 08:16 PM

Last Updated: Picard RobertAndriolo Picard ‎2021-07-22 06:24 PM

Issue

  • Receive an error: "The user session is lost, no specific reason has been set." when logging into StruxureWare Building Operation WebReports from Internet Explorer (browser), while Reports from within Workstation work fine. 
  • Receive an error: "The user session is lost, no specific reason has been set." when logging into StruxureWare Building Operation WebReports from Internet Explorer (browser), and get no Reports folder within Workstation.
    Error.png
  • Login Screen appears as expected, but when attempting to log in with the user name/password; It times out and comes with the message 'Failed to establish connection with server.'

Product Line

EcoStruxure Building Operation

Environment

Building Operation WebReports 1.1 / 1.2

Cause

The error is most likely due to ports been blocked and/or the incorrect port settings entered during the WebReports installation process. When installing (or upgrading) WebReports, you must enter this information on each occasion as this information is not retained from previous installations.

If you need to change these settings, then you should follow the procedure detailed below.

Resolution

If installed on separate machines, then check the firewall settings and ensure the ports used for the Enterprise Server and the Report Server are not blocked. 

If this does not resolve the issue or if you are running both the Enterprise Server and Report Server on the same PC, then the Enterprise Server port configuration during the WebReports installation may need to be changed.  This is achieved as follows: this, and follow these key steps:

  1. Run the WebReports Installation setup program, and at the Setup Type prompt, select Upgrade from...
    WebReportsInstaller_UPgrade.png
  2. Proceed through the other options as normal. Once you reach the Reporting Agent setup, make sure you enter the correct URL (path and port number - this is unique for each installation) used during the Enterprise Server setup.
    ReportAgentCorrectESURL.png
  3. Continue through the other settings as required - Ensure that any Path and URL ports are set correctly.  Once you complete these settings, the WebReports Installer package then goes through the following checks and installation:
    • Checking Installation Requirements
    • Pre-upgrade Configuration
    • Installation of Reporting Agent, WebReports, and WebReports Service
    • Post-Installation Configuration
    • Installation PublishedReports
  4. After the above steps, the upgrade is completed. This will now allow login to the WebReports URL using your web browser.

For additional assistance in installing/upgrading WebReports, refer to the online help website. 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 7691
  • RobertAndriolo21
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore