Calculation for converting static air pressure to cfm
  • Calculation for converting static air pressure to cfm
  • GavinHe
    GavinHe
  • sesa139513
    sesa139513
  • Roger_Bently
    Roger_Bently
‎2018-09-06 03:28 PM
Last Updated: Sisko GavinHe Sisko ‎2022-08-25 09:15 AM
TAC INET
  • INET HVAC Site
What are the calculations for converting static air pressure to cfm?
SRVP ("water column") * 4005 = FPM (feet per minute).
The second calculation is FPM * AreaFtSQ (size of box) = CFM
You will need an airflow monitoring device and duct static pressure sensor to measure SRV P (v of Vs of P).
  • TAC INET