Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,851
  • TAC IA Series 1,825
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 332
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 149
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 10
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 41
    • 42
    • 43
    • …
    • 508
  • Next »

Access Expert exception error adding a downstream device to an SSC

  Issue When attempting to add a downstream device to an SSC the error "exception of type \'Feenics.Keep.DomainModel.KeepException\' was thrown" Product Line EcoStruxure Access Expert Environment  Access Expert V3 Cause The SSC has a limitation of 32 downstream devices no matter what port(s) are being used either RS485 or virtual.  Resolution The SSC specification data sheet indicates the SSC can manage up to 64 downstream devices. However, R&D has corrected our understanding of this limitation which is only 32 downstream devices. Attempting to add a 33rd downstream device will result in the   \'Feenics.Keep.DomainModel.KeepException\' error. An additional SSC or Mercury upstream controller will be necessary to commission greater than 32  downstream devices.   From R&D: "The SSC can support a Total of 32 downstream devices no matter what port they are connected to either RS485 or Virtual. The SSC can also support 64 doors total." SSC data specification sheet  *Note: The specification sheet will be corrected in the future by the Product Owner.
View full article
Admiral Alan_Wood Admiral
‎2023-03-30 05:53 PM

on ‎2023-03-30 05:53 PM

Labels:
  • EcoStruxure Access Expert
954 Views

The procedure to follow for upgrading or downgrading the I/A Series G3 software in an I/A Series ENC

Issue What is the procedure for upgrading the I/A Series G3 software in an I/A Series ENC? Product Line TAC IA Series Environment I/A Series G3 Workbench software on computer (both the old version and new version need to be installed on the computer) I/A Series G3 ENC-520 or ENC-410 Cause Need to upgrade the software that is installed in the ENC. Resolution With the old version of Workbench running on the computer, backup the station running in the ENC.  All required graphic files, etc., stored in the ENC should also be backed up.  Note the station folder name for use in step 5, below. Verify that the license in the ENC is compatible with the new release to be installed. If not, use the License Manager (under the Platform) to install an updated license. If the correct version of the license is not currently available, it must be obtained and installed prior to beginning step 6, below. If the new release of the I/A Series G3 software has not already been installed on the computer, install it now. Verify that the Workbench computer has a license that is version compatible with the new release of the I/A Series software to be installed.  If the license is not version compatible, acquire a new license for the Workbench computer before continuing. Copy the entire named station folder (used in step 1) from the old release Stations folder to the new release Stations folder.  See NOTE below regarding the installation of a version downgrade. Run the "Install Platform Daemon" command from the Windows Start Menu folder for the new version of the software. Open the Workbench in the new version of the I/A Series G3 software and connect to the platform of the ENC to be upgraded. From the Platform menu, open the License Manager and verify that the ENC license has been updated to allow use with the new version of the I/A Series G3 software. Right-Click on the ENC platform in the Workbench tree and select Commissioning Wizard. Complete the commissioning process as documented in the Niagara AX Install and Startup Guide . On the first screen, select the operations to be performed.  The required minimum operations will normally be checked and shown in grey.  The "Install a station..." option needs to be checked if not already checked. Click [Next] to begin the commissioning process.  Continue through the various steps, as required.   When prompted, select the station copied in step 5. When prompted, verify that all required modules are available and are selected for installation. Allow the commissioning process to complete, following the prompts as required. The upgrade is now complete.  Start the station as required. NOTE: Do not use the process to directly downgrade the version of software installed in an ENC.  You must use the Platform "Distribution File Installer" to install the appropriate clean distribution (from the cleanDist folder under the software version to be installed.  Typically, only one clean distribution file will be available to be installed.  Select that file then click the [-> Install] button to downgrade the ENC software.  This process needs to be done as noted in step 5, above, after backing up the station but before beginning the commissioning of the device with the older I/A Series G3 software version.
View full article
Picard Product_Support
‎2018-09-10 09:04 PM

Last Updated: Administrator CraigEl Administrator ‎2023-03-30 05:51 PM

Labels:
  • TAC IA Series
4347 Views

Trend log limitations in SmartX IP Controllers

Issue What is the maximum number of trend logs in a SmartX IP Controller? What is the maximum number of trend log records in a SmartX IP Controller? Product Line EcoStruxure Building Operation Environment Building Operation Multi-purpose Controller Cause SmartX IP controller free object system memory is shared between objects and data in your application. There are no specific limits on the number of objects and/or trend logs that you can create. Several factors impact memory consumption: Every object added consumes a fixed amount of memory Memory is shared between objects and data. Adjustments to description fields or trend log buffer sizes will also impact the amount of memory consumed. Different controllers have different amounts of memory to start from. RPC controllers have roughly half of the memory of an MPC. Changes to EBO 3.X will also change the memory consumption, so upgrading your system may skew the memory consumption larger than it was in previous versions. Resolution After adding trend logs to the device consult the Free object system memory entry in the device report since this will help determine how much free memory is available. Trend log buffers are pre-allocated on creation of the trend object. The other place to find how much free memory the device have is in the device property page. This value can be put in a watch window, trended, or even bound to a low-limit alarm.     If the amount of free memory drops below 50 Kbytes, that is critically low available memory. A better target is to try to preserve 50% of available memory. Based on empirical testing, estimates of memory available inside a blank controller are: MP-C: 1890 Kbytes MP-V: 1780 Kbytes RP-C: 1115 Kbytes It is important to not overload the controller because the remaining memory can also be used for COV subscriptions (the last line in the table above). If there is no memory available, then opening a graphic which creates COV subscriptions could overrun memory or operate very slowly
View full article
Janeway Jonas_Brissman Janeway
‎2019-05-02 06:15 AM

Labels:
  • EcoStruxure Building Operation
3371 Views

Alarm Pane not shown in Webstation

Issue Alarm Pane not shown in Webstation Product Line EcoStruxure Building Operation Environment Building Operation Webstation Cause The User is viewing a Workspace which does not contain the Alarm Pane Resolution In the Top Left hand corner of the screen click View>Workspaces Select Engineering (or other applicable workspace)
View full article
Picard Product_Support
‎2018-09-07 07:15 AM

Last Updated: Administrator CraigEl Administrator ‎2023-03-29 05:23 PM

Labels:
  • EcoStruxure Building Operation
1246 Views

Locking down access to WebStation.

Issue Unable to lock down access to AS WebStation to all clients Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium Building Operation Webstation Cause Required to forbid accessing AS via http or https.. Resolution Https is the default workstation communication channel to an SBO server and therefore cannot be locked down. 
View full article
Picard Product_Support
‎2018-09-06 08:46 AM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-29 06:09 AM

Labels:
  • EcoStruxure Building Operation
1195 Views

Difference between "Workstation" and "Workstation Professional" licenses

Issue Information is needed regarding the content of the various license types Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause If a standard Workstation license and a Workstation Pro. license are purchased, and are loaded on to a License server, when is the professional license used? Resolution The difference between the standard Workstation license and the Workstation Pro. license is that the professional license allows the usage of the editors (Graphics Editor, Function Block Editor, Script Editor, Menta Editor, WorkPlace Tech Editor). The licenses can be seen as a bundle of license features that can be checked in and checked out separately from each other. When a workstation attempts to use any of these editors the license server is asked to check out the license feature for that editor and if successful, that feature is "taken" and cannot be used by any other Workstation until the first workstation leaves the editor. This means that if you have one professional license, only one Workstation can use the same editor at the same time, if you e.g. have 2 professional licenses you can have 2 Workstations using the same editor at the same time. However, any Workstation can use any editor as long as there is a free license feature for it on the license server.
View full article
Picard Product_Support
‎2018-09-06 09:22 AM

Last Updated: Administrator CraigEl Administrator ‎2023-03-29 05:20 PM

Labels:
  • EcoStruxure Building Operation
1522 Views

Script program does not execute correctly.

Issue The script program always executes the first condition, whatever the condition is. The code is shown below: Numeric Input AirFlowMin,AirFlowMax,AirFlowRead Numeric OutPut FlowFactor Line Judging if AirFlowMin<AirFlowRead<(AirFlowMax-AirFlowMin)/3 then goto 1 if (AirFlowMax-AirFlowMin)/3<AirFlowRead<(AirFlowMax-AirFlowMin)*2/3 then goto 2 if (AirFlowMax-AirFlowMin)*2/3<AirFlowRead line 1 FlowFactor=1 goto judging line 2 FlowFactor=2 goto judging line 3 FlowFactor=3 goto judging After the above program saves successfully, whatever the value of AirFlowRead is, the program only goes to line 1 and sets the value of FlowFactor to 1, and never goes to the other two lines. Product Line EcoStruxure Building Operation Environment B3s Script Program Cause Some expressions are supported in Continuum Plain English but are not supported in b3 Script programs Resolution Change the expression as shown below: Line Judging if AirFlowMin<AirFlowRead and AirFlowRead<(AirFlowMax-AirFlowMin)/3 then goto 1 if (AirFlowMax-AirFlowMin)/3<AirFlowRead and AirFlowRead<(AirFlowMax-AirFlowMin)*2/3 then goto 2 if (AirFlowMax-AirFlowMin)*2/3<AirFlowRead and AirFlowRead  
View full article
Picard Product_Support
‎2018-09-06 09:44 AM

Last Updated: Administrator CraigEl Administrator ‎2023-03-29 05:16 PM

Labels:
  • EcoStruxure Building Operation
1311 Views

Alarm email failure.

Issue Microsoft Outlook is not emailing alarms. Product Line Andover Continuum Environment Continuum 1.XXX Microsoft Outlook 2XXX Cause The created Contact folder used by Continuum Alarms to send emails was not being shown first.. Resolution Open Microsoft Outlook Select Tools > Address Book Select Tools > Options Once opened, select  "Show this address list first:" (It defaults to the Global Address List) Ensure the contact folder with the distribution list created for Continuum Alarms has been selected (Contact) Also see online help: Email, Creating an Event Notification List
View full article
Picard Product_Support
‎2018-09-06 02:14 PM

Last Updated: Administrator CraigEl Administrator ‎2023-03-29 05:10 PM

Labels:
  • Andover Continuum
2293 Views

Installation of StruxureWare Building Operation Enterprise Server (ES) fails during installation.

Issue When installing Enterprise Server an error is received at the end of the installation:  Clicking on the Details button the following error is shown:  -EnterpriseServer Service registration Starting Execute: "C:\Program Files\Schneider Electric\StruxureWare 1.2\Software Administrator\SE.SoftwareAdministrator.exe" ES /Install --DatabasePath="C:\Documents and Settings\All Users\Application Data\Schneider Electric\StruxureWare 1.2\Enterprise Server\db" --HTTPPort="80" --HTTPSPort="443" --TCPPort="4444" SE.SoftwareAdministrator.exe --install returned -532462766 -EnterpriseServer Service registration Leaving Completed In Software Administrator the Status of the Enterprise Server is indicated as Not Installed. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Cause It appears that the installation package has an issue with the authority to create the Enterprise Server Service, below are some options to try to rectify this.  Resolution SmartStruxure version 1.4 running on Windows 7 If this problem is encountered in 1.4 try the following steps Uninstall Enterprise Server software Restart PC Run the Enterprise Server installation software.  Use the Right Click "Run as administrator" option to ensure correct authority. Download and unzip this batch file Run the .bat file on the affected PC. Check the Software Administrator and confirm that the Server Status has now changed to "Running"   NOTE:  This batch file is only valid for 1.4 and will not work for 1.2 or 1.3.  Resolution #1 (Typically seen with SmartStruxure version 1.2) Changing the DCOM setting as described below has shown to allow for the installation process to complete. From the Start - Search programs and files entry type "dcomcnfg" and then select the dcomcnfg.exe file. Expand Component Services and also expand Computers. Right mouse click My computer and select properties and then select COM Security tab. Select the edit limits button from the  "Launch and activation permissions"  section. Select / Add the Everyone user and make sure all the permissions are set to allow   Reboot the computer. Then reinstall the Enterprise Server. Resolution #2 (Typically seen with SmartStruxure version 1.3) If Resolution #1 does not work or is not possible then you can manually add the Enterprise Server application manually.   Download and unzip this batch file Run the .bat file on the affected PC. Check the Software Administrator and confirm that the Server Status has now changed to "Running" NOTE:  This batch file is only valid for 1.3 and will not work for 1.2.  Alternative Workaround: Should neither of these options work.  You can run the Enterprise Server manually.  To do this: Locate the path: C:\Program Files\Schneider Electric StruxureWare\Building Operation 1.x\bin Double Click on the file name: SE.SBO.EnterpriseServer.exe A DOS Command prompt will open and display the Enterprise Server System log.  This window must stay open.  If you accidently close it, it will force the Enterprise Server to close and shutdown.
View full article
Picard Product_Support
‎2018-09-10 01:24 PM

Last Updated: Administrator CraigEl Administrator ‎2023-03-29 05:07 PM

Labels:
  • EcoStruxure Building Operation
2537 Views

How do you reset the Viconics VT7200, VT7300, &amp; VT7600 LON series thermostats back to factory default values?

Issue How do you reset the Viconics VT7200, VT7300, & VT7600 LON series thermostats back to factory default values? Product Line Field Devices Environment SSL SE7000 Cause There's no button or command that sets the thermostat to its default parameter settings. Resolution Either set them manually or through the snvts available via a LON integration.  The Viconics Lon Integration Manual will help with identifying the proper snvts to use.
View full article
Picard Product_Support
‎2018-09-06 02:29 PM

Last Updated: Administrator CraigEl Administrator ‎2023-03-29 04:57 PM

Labels:
  • Field Devices
3454 Views

Not possible for BACnet alarm to trigger directly on a variable from a Function Block Program

Issue Unable to have BACnet alarm trigger directly on a variable from a Function Block Program Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Cause Building Operation does not have the possibility for a BACnet alarm to directly monitor a variable from a Function Block Program.  The problem with doing this is that a Function Block Program is not a BACnet visible object (a BACnet client cannot see it, even as a proprietary object type), and we do not see any provision in the BACnet standard for an alarm object to reference something not visible to BACnet. Resolution The workaround is to create a BACnet point (a BACnet Value object would make the most sense), and bind it to the Function Block Program variable.   There is however an option which may avoid "double" work.  In Building Operation we have implemented intrinsic alarming on the BACnet points and values.  This means that the point can detect and report alarms without creating a separate alarm object.  (they still need to reference to a BACnet notification class just like normal BACnet alarm objects).   The only limitation is in the choice of algorithm: Analog objects (Input, output, Value) support the out-of-range algorithm (high-limit, low-limit). Digital and Multistate objects* (input, and value) support the change-of-state algorithm. *In Building Operation, we do not have digital or multi-state outputs with alarming, because we do not support "command-failure" type alarm that those require.
View full article
Picard Product_Support
‎2018-09-06 10:42 AM

Last Updated: Administrator CraigEl Administrator ‎2023-03-29 04:48 PM

Labels:
  • EcoStruxure Building Operation
2427 Views

Is the Continuum Cyberstation a B-OWS (BACnet Operator Workstation)?

Issue Is the Continuum Cyberstation a B-OWS (BACnet Operator Workstation)? Product Line Andover Continuum Environment Continuum Cyberstation BACnet Cause Can't find reference to Continuum Cyberstation being defined as a B-OWS. Resolution The Continuum Cyberstation is a B-OWS and complies with ANSI/ASHRAE standard 135-2004.  However, the Continuum Cyberstation has not been BTL tested, please see the Schneider Electric BTL Listing of Tested Products.    The following selection is taken from the Andover Continuum Family of User Interfaces document describing Continuum's Cyberstation capabilities. Native BACnet B-OWS CyberStation communicates with the BACnet devices using BACnet/IP in strict accordance with ANSI/ASHRAE standard 135-2004 and is designed to function as a BACnet Operator Workstation (B-OWS) and BACnet Broadcast Management Device (BBMD). The CyberStation can communicate to all Andover Continuum BACnet Devices as well as any third party BACnet Device on the BACnet network.
View full article
Picard Product_Support
‎2018-09-11 04:25 AM

Last Updated: Sisko GavinHe Sisko ‎2023-03-27 03:38 AM

Labels:
  • Andover Continuum
1758 Views

Creating Windows Firewall rules to allow StruxureWare Building Operation to communicate on the TCP port

Issue Unable to establish communication between the enterprise and automation servers through the TCP Port 4444. Values are not being passed between the enterprise to the automation servers or between automation server to automation server. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Premium Building Operation Workstation Cause Windows Firewall is not allowing inbound or outbound information from passing through the TCP port 4444. Resolution First download and run TCP View. With TCP View running, sort the list by the Local Port and find all devices that are talking on port 4444. If the automation servers are in a state of LISTENING then rules must be created to allow communication. Copy the file path of SE.EnterpriseServer.exe in order to create the rules. This can be found by right clicking on one of the SE.EnterpriseServer.exe process > Process Properties... (C:\Program Files\Schneider Electric\StruxureWare 1.2\Enterprise Server\bin\SE.EnterpriseServer.exe) If the automation servers are in the state of ESTABLISHED, then take a look at Binding between ES and AS or two AS shows Unresolved and "Communication Failed" Alarm occurs when Adding an AS. Source: /Server 1/Servers/ASL/System/Server Communications/Models/2deef04c-05d1-41ae-9c3f-f84a9f7e0b41 for more troubleshooting help.   Change Windows Firewall Settings to Allow Programs Go to Start > Control Panel. Click on Windows Firewall. Click on "Allow a program or feature through Windows Firewall" on the left hand side of the window. Find "StruxureWare Building Operation" in the list of programs and make sure Home/Work and Public networks are selected.  Note: If you do not have permission rights to make changes in this area of Windows, move on to the next section where you can set up inbound and outbound firewall rules.   Creating Inbound and Outbound Windows Firewall Rules Go to Start > Control Panel.  Click on Windows Firewall. Click "Advanced settings" on the left side of the window. Select Inbound Rules on the left side of the window and then click New Rule... on the right side of the window. On the first screen of the New Rule Wizard, choose Program. Click Next. In "This program path:" either browse to SE.EnterpriseServer.exe or paste the file path that was copied earlier from the TCP View into the box. Click Next. Select the option to "Allow the connection". Click Next. Leave Domain, Private, and Public checked unless otherwise desired. Click Next. Name the rule StruxureWare. Click Finish. Select Outbound Rules on the left side of the window and then click New Rule... on the right side of the window. Follow steps 5 through 9 to create the Outbound Rule. Note that the SBO Firewall Config tool on the community can be used to automatically create the required firewall rules.
View full article
Picard Product_Support
‎2018-09-10 10:40 PM

Last Updated: Administrator CraigEl Administrator ‎2023-03-28 09:49 PM

Labels:
  • EcoStruxure Building Operation
11009 Views

Upload objects required from a BACnet Device instead of uploading the entire Device.

Issue A BACnet devices can contain 1000's of objects, performing an upload on these devices can take upwards of 30 minutes to complete when only a few objects are required for integration. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Premium Cause Uploading all objects in a controller can take a lot of time and is often not required. Resolution From version 2.0 Open the device discovery view / BACnet - then Discover All. Once the Device is hosted, click on the device (in the Device Discovery window) and open the right-hand Object pane. Drag/drop the required Object into the hosted BACnet device Application folder. Alternatively, the Hardware folder can be used, this was the best method for some earlier versions Perform the BACnet discovery, then view the Hardware folder at /ServerName/System/Hardware/BACnet devices. Navigate to the required Device/Object, then Drag and drop the Device and Object as above.
View full article
Picard Product_Support
‎2021-02-15 06:58 AM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-28 07:40 AM

Labels:
  • EcoStruxure Building Operation
4024 Views

When logging in to an AS or ES, SBO WorkStation freezes or it takes a very long time to log in

Issue When logging in to an AS or ES, WorkStation freezes or it takes a very long time (>30 minutes) before the login process finishes. Building Operation WorkStation hangs on "Reading data..." when trying to login to an AS or ES Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation WorkStation Cause The problem is related to a delay when validating the license details. It only seems to happen when running a mixed EBO/SBO 1.9.3 system and after having EBO license administrator 2.0.1 previously installed. Resolution Run the SBO License Server Reset tool and perform Reset - Simple Log in to WorkStation, and if the hang or freezing is still present, then follow the next set of instructions. Run Diagnostics in the License Administrator and take note of all the ACT (Activation) and Entitlement IDs Return all the licenses Close all WorkStations and stop all SBO/EBO processes (whichever may be running) Uninstall all License Administrator and License Server Run the SBO License Server Reset tool and perform a Reset - Complete (you will get an output of the commands and result) Install the latest released version of License Administrator and License Server (the latest released version of License Administrator has fixes for virtual servers and some cyber security vulnerabilities, note that License Administrator is backward compatible with earlier SBO versions) Activate the licenses based on the info from step 3 Note: If running the demo license, steps 3 and 4 may be skipped. If problems continue to occur, then send the above details collated (in step 3) and email this/contact support.
View full article
Picard Product_Support
‎2021-01-14 04:23 PM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-28 08:33 AM

Labels:
  • EcoStruxure Building Operation
7844 Views

BACnet device Instance Number (Instance ID) in EcoStruxure Building Operation

Issue Finding the rules governing the BACnet device Instance ID in EBO and learning to change it if required. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Premium Building Operation Automation Server Bundled  Cause The BACnet device Instance ID must be unique within a BACnet system. There may be a need to find out or change the device Instance ID to ensure there are not duplicates.  Resolution When a BACnet Interface is added to an SmartX server, AS or ES, the Server will become a BACnet device and it will have an Instance ID (automatically generated or manually assigned).  To check an ES or AS BACnet device instance ID go to the properties of the BACnet Interface and then the Advanced tab. The device instance ID is defined as the Object ID. To check other BACnet device, SmartX controller or 3rd party BACnet device, go to the properties of the BACnet Device and then the Advanced tab. The device instance ID once again is defined as the Object ID.  No 2 BACnet devices in any system may have the same Instance ID/Object ID. The valid range of Instance Numbers for a BACnet device is 0 to 4194302.   Change BACnet Device ID: You can change BACnet device IDs for SmartX Server or Controller when there is a conflict with another BACnet device, move controller or in those situations where you need to change the originally selected value for some local or site-specific reason. In EBO V3.2.3 or higher (except V3.3), it is possible to change BACnet Device ID of an SmartX server (ES, AS-P or AS-B), as explained in: Changing the BACnet Device ID in a SmartX Server To change SmartX IP Controller BACnet device ID, follow: Changing a BACnet/IP Device ID
View full article
Picard Product_Support
‎2020-12-17 06:13 AM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-28 08:40 AM

Labels:
  • EcoStruxure Building Operation
11479 Views

WebStation login error when using Internet Explorer

Issue When trying to log in to WebStation Version 1.7.1 using Internet Explorer 11 you get the following error message: Wrong domain, user name or password Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium Building Operation Webstation Cause The cookie sent from the SmartStruxure server has an old expiry date. This can be confirmed by tracing communication using Fiddler or similar. Resolution Set the correct date and time in the Automation Server or Windows PC where the Enterprise Server is installed. Refer to Web Help #4388 for instruction on how to set the time in an Automation Server
View full article
Picard Product_Support
‎2020-10-12 08:03 PM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-28 09:00 AM

Labels:
  • EcoStruxure Building Operation
3498 Views

Is it possible to use TAC Vista WebStation over ISDN Routers in a WAN Intranet?

Issue Is it possible to use TAC Vista WebStation over ISDN Routers in a WAN Intranet? Product Line TAC Vista Environment TAC Vista Webstation ISDN Routers WAN Intranet Cause This is possible to configure. Resolution To run TAC Vista Webstation, log into a NT domain. An ISDN router can be a link on an Intranet.
View full article
Picard Product_Support
‎2018-09-06 03:15 PM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-28 11:54 AM

Labels:
  • TAC Vista
1226 Views

When TAC Vista is setup as an OPC Server, Can you access the Historical Data (HDA) from TAC Vista SQL DB

Issue When TAC Vista is setup as an OPC Server, Can you access the Historical Data (HDA) from TAC Vista SQL DB Product Line TAC Vista Environment TAC Vista OPC Server OPC Client Cause When TAC Vista is acting as an OPC Server and providing integration with a third party software / device, online and alarm values are all that is supported. Historical data is not supported via the OPC interface. Resolution It is not possible to access the historical data from the Vista SQL database, when using Vista's OPC Server . It may be possible to get historical data with the help of some third party OPC-HDA-Server for SQL software.  This option has not been tested, and issues related to this interface are also not supported. Click on below link to see an example of OPC-HDA Server for SQL. http://www.opcti.com/OPC-HDA-Server-for-SQL.aspx
View full article
Picard Product_Support
‎2018-09-10 10:59 AM

Last Updated: Administrator CraigEl Administrator ‎2023-03-28 09:35 PM

Labels:
  • TAC Vista
1507 Views

How does TAC Vista manage log retrieval when the unit is offline?

Issue TAC Vista appears to keep trying to retrieve logs from controllers despite them being offline. This causes a lot of event messages to be created and fills up the log database quicker. Product Line TAC Vista Environment TAC Vista 5.X Older RPU (remote processing unit) under a PLB ( 5751), containing logs to be retrieved by Vista. Cause TAC Vista appears to keep trying to retrieve logs from controllers despite them being offline. This causes a lot of event messages to be created and fills up the log database quicker. Resolution Vista continues cyclically trying to retrieve the log/s even when the RPU under the PLB is offline.
View full article
Picard Product_Support
‎2018-09-06 01:36 PM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-28 11:57 AM

Labels:
  • TAC Vista
1192 Views
  • « Previous
    • 1
    • …
    • 41
    • 42
    • 43
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of