Can't find reference to Continuum Cyberstation being defined as a B-OWS.
The Continuum Cyberstation is a B-OWS and complies with ANSI/ASHRAE standard 135-2004.  However, the Continuum Cyberstation has not been BTL tested, please see the Schneider Electric BTL Listing of Tested Products.
The following selection is taken from the Andover Continuum Family of User Interfaces document describing Continuum's Cyberstation capabilities.
Native BACnet B-OWS
CyberStation communicates with the BACnet devices using BACnet/IP in strict accordance with ANSI/ASHRAE standard 135-2004 and is designed to function as a BACnet Operator Workstation (B-OWS) and BACnet Broadcast Management Device (BBMD). The CyberStation can communicate to all Andover Continuum BACnet Devices as well as any third party BACnet Device on the BACnet network.