Upload objects required from a BACnet Device instead of uploading the entire Device.
  • Upload objects required from a BACnet Device instead of uploading the entire Device.
  • Dave_Shore
    Dave_Shore
  • DavidChild
    DavidChild
  • Ramaaly
    Ramaaly
  • AdamSteele
    AdamSteele
‎2021-02-15 06:58 AM
Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-28 07:40 AM
A BACnet devices can contain 1000's of objects, performing an upload on these devices can take upwards of 30 minutes to complete when only a few objects are required for integration.
  • Building Operation Automation Server Premium
Uploading all objects in a controller can take a lot of time and is often not required.
From version 2.0
  • Open the device discovery view / BACnet - then Discover All.
  • Once the Device is hosted, click on the device (in the Device Discovery window) and open the right-hand Object pane.
  • Drag/drop the required Object into the hosted BACnet device Application folder.
Alternatively, the Hardware folder can be used, this was the best method for some earlier versions
  • Perform the BACnet discovery, then view the Hardware folder at /ServerName/System/Hardware/BACnet devices.
  • Navigate to the required Device/Object, then Drag and drop the Device and Object as above.