Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

BACnet device Instance Number (Instance ID) in EcoStruxure Building Operation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet device Instance Number (Instance ID) in EcoStruxure Building Operation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • David_Kendrick
    David_Kendrick
  • DavidChild
    DavidChild
  • Ramaaly
    Ramaaly
  • RyanSuar
    RyanSuar
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
13029 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet device Instance Number (Instance ID) in EcoStruxure Building Operation

Picard Product_Support
‎2020-12-17 06:13 AM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-28 08:40 AM

Issue

Finding the rules governing the BACnet device Instance ID in EBO and learning to change it if required.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled 

Cause

The BACnet device Instance ID must be unique within a BACnet system. There may be a need to find out or change the device Instance ID to ensure there are not duplicates. 

Resolution

When a BACnet Interface is added to an SmartX server, AS or ES, the Server will become a BACnet device and it will have an Instance ID (automatically generated or manually assigned). 

  • To check an ES or AS BACnet device instance ID go to the properties of the BACnet Interface and then the Advanced tab. The device instance ID is defined as the Object ID.
  • To check other BACnet device, SmartX controller or 3rd party BACnet device, go to the properties of the BACnet Device and then the Advanced tab. The device instance ID once again is defined as the Object ID. 
  • No 2 BACnet devices in any system may have the same Instance ID/Object ID.
  • The valid range of Instance Numbers for a BACnet device is 0 to 4194302.

 

Change BACnet Device ID:

You can change BACnet device IDs for SmartX Server or Controller when there is a conflict with another BACnet device, move controller or in those situations where you need to change the originally selected value for some local or site-specific reason.

  • In EBO V3.2.3 or higher (except V3.3), it is possible to change BACnet Device ID of an SmartX server (ES, AS-P or AS-B), as explained in: Changing the BACnet Device ID in a SmartX Server
  • To change SmartX IP Controller BACnet device ID, follow: Changing a BACnet/IP Device ID
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 14776
  • DavidKendrick20
  • MahmoudSayed21
  • RamaAly23
Was this article helpful? Yes No
75% helpful (3/4)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore