Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Andover Continuum
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "andover continuum"

View in: "Building Automation Knowledge Base" | Community

2197 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 22
    • 23
    • 24
    • …
    • 110
  • Next »
Label: "Andover Continuum" Show all articles

Microsoft Edge browser alternative for accessing Continuum WebClient

Issue What alternatives are available for accessing Continuum WebClient from browsers other than Internet Explorer? Product Line Andover Continuum Environment Continuum WebClient Server Cause While Internet Explorer is the only officially supported browser for Continuum WebClient, Microsoft has announced that support for Internet Explorer will end in June 2022.   When accessing WebClient sites using Microsoft Edge in Internet Explorer mode. WebClient server returns an error, indicating that Internet Explorer is needed to access WebClient. Resolution It is possible to access WebClient using Microsoft Edge in Internet Explorer Mode. 1. In Edge click on the ellipses (...) top right then select Settings and set like the snapshot below. a. Allow sites to be reloaded in Internet Explorer Mode(Allow) b. Add the webclient machine's login page (http://webclientservername/webclient/logon.aspx) 2. Setting Internet Explorer compatibility mode and Internet Explorer mode for future use. Navigate to the webclient URL with Edge and select Reload in Internet Explorer mode By default, these settings will be Disabled, Set both of the buttons to Enable as shown below. Note: you may have to go through the process twice to enable both buttons   A snapshot of a successful login to webclient with Edge and also the selection in yellow to Exit Internet Explorer Mode if necessary to run other web applications.   The method of specifying Internet Explorer Mode for a site’s webClient URL will depend on how the customer treats the configuration of Edge – either settings at the individual Edge level or via group policy settings.
View full article
JohnBoehmer Schneider Alumni (Retired)
‎2021-11-17 01:15 PM

Last Updated: Admiral Alan_Wood Admiral ‎2024-03-07 11:06 AM

Labels:
  • Andover Continuum
2553 Views

Error replacing IOU module

Issue Changing the Module ID after physically replacing a modules gives error "Incorrect response (or no response) from IO module" Product Line Andover Continuum Environment CyberStation CX9900 CX9940 CX9680 IOU Module Cause Controller's OMS database is out of sync with SQL database. Resolution To synchronize the OMS database with the SQL database:- Put CyberStation in offline edit mode. Edit the IOU Module object and enter the new Module ID. Save the object Return CyberStation to online edit mode. Perform a Send to controller, reloading the controller will sync the OMS db in the controller with the SQL database. Note the following: Make sure to use the option to reload attached objects but not attached controllers If IOUs go offline when sending to controller after doing this, manually get IOUs online, perform a send to database and send to controller. If a number of IOUs were replaced this process may need to be repeated several times until the send to controller works with no errors.
View full article
Picard Product_Support
‎2018-09-06 12:25 PM

Last Updated: Sisko GavinHe Sisko ‎2024-03-04 02:55 AM

Labels:
  • Andover Continuum
2197 Views

Error 'The UPREV engine was asked to process an invalid code type' when flashing the firmware in the controller.

Issue Error 'The UPREV engine was asked to process an invalid code type' when flashing the firmware in the controller. Product Line Andover Continuum Environment bCX9640 CX9680 ACX5720 ACX5740 Cause RAM issues Resolution Using a browser login to the controller and perform a 'Clear Database Backup', commit changes and restart the controller. When the controller has re-started  disconnect the battery, power down the controller and after a minute power the controller up and re-connect the battery. Wait for the controller to come back online and then try the uprev operation once again.
View full article
Picard Product_Support
‎2018-09-06 11:15 AM

Last Updated: Sisko GavinHe Sisko ‎2024-02-26 04:26 AM

Labels:
  • Andover Continuum
2471 Views

BACnet multi state object number of states and states label

Issue Can the user set the 'Number of States' and the 'State Text' in a multi state object? Product Line EcoStruxure Building Operation Environment BACnet b3 controllers Multi-state values Cause The b3 firmware does not allow the Number of States or State Text to be modified This is Function as designed. Resolution Continuum DOES NOT allow changes to the default number of states and state labels. The 'Number of States' field is read only. An attempt to change any of the label will result in the following error: An error code was returned from a BACnet operation, but the reason could not be determined. The same is seen in EBO if any attempt is made to edit the State Text, see below
View full article
Picard Product_Support
‎2018-09-06 03:54 PM

Last Updated: Dave_Shore Schneider Alumni (Retired) ‎2024-02-20 01:52 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1939 Views

Restart modes of the second generation Infinity controllers

Issue bCX9640, CX9680, ACX5720 and ACX5740 do not have ACCRestartMode system variable. Product Line Andover Continuum Environment CyberStation bCX9640 CX9680 ACX5720 ACX5740 Cause The restart mode of the second generation Infinity CX controllers (9640, 9680, 5720/40) is not user selectable. Resolution The second generation Infinity CX controllers (9640, 9680, 5720/40) have a fixed startup sequence as follows: Warm to Cool to Cold, meaning the controller will ALWAYS first attempt to WARM start, if warm start is not possible the controller will attempt a COOL start, if cool start if not possible the controller will attempt a COLD start. Warm start: Controller is re-starting with its RAM memory intact because the controller has remained powered or the memory has been kept by the battery. In this case all the configuration data (points, programs) and run time data (logs, points current values) is restored. Cool start: Controller is re-starting with its RAM memory erased or is unable to restore data from RAM for whatever reason. In this case the configuration data only (points, programs) is restored provided it has been previously backed up to flash memory. NOTE: Personnel objects are NOT kept in flash, upon cool start the controller will automatically request a personnel distribution from its access server CyberStation. Cold start: Controller unable to warm start or cool start, all configuration and runtime data will be lost. It must be reloaded from CyberStation.
View full article
Picard Product_Support
‎2018-09-06 12:20 PM

Last Updated: Crewman ContentModerator ‎2024-02-16 12:30 AM

Labels:
  • Andover Continuum
2890 Views

SLP BACnet Setpoint limits

Issue SLP BACnet Setpoint limits Product Line EcoStruxure Building Operation, Andover Continuum, Field Devices Environment SpaceLogic SLP Series Cause The BACnet Object "Temperature Setpoint" includes properties Minimum and Maximum values These can be used to limit the setpoint, however the values are not saved in non volatile memory, thus the value revert to default after a power cycle (0 and 50 degC). The Setpoint object needs to be manually downloaded from EBO following a power cycle to set these properties. These properties cannot be written to individually. Thus changing these properties is unlikely to be good practice. Resolution A script program can be used to set limits to the Temperature Setpoint. Example below Note the "Value transfer settings" need changing to "Transfer value each time..." as below
View full article
Dave_Shore Schneider Alumni (Retired)
‎2024-02-07 08:53 AM

on ‎2024-02-07 08:53 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
4651 Views

How to convert Continuum dump file to an older version of AS-P using Project Configuration Tool(PCT) 2.0

  Issue Unable to convert DMP file to SmartX servers with EBO 3.x, 4.x and 5.x using Continuum Conversion Tool(CCT) with PCT 2.0 Example: CCT3.2 is unable to connect to an AS-P in v3.2 created in PCT 2.0 It shows the "The user session is lost, no specific reason has been set" error when trying to connect. Product Line EcoStruxure Building Operation Environment Continuum Conversion Tool Project Configuration Tool Cause PCT 2.0 is not compatible with earlier versions of CCT Resolution In PCT 2.0, create a version 6.0 ES. In PCT 2.0, create an older version of AS-P. In PCT 2.0, make the older version AS-P a child of version 6.0 ES. In WorkStation 6.0, log on to the ES, navigate to the AS-P, and create the desired MS/TP or Infinet networks. In CCT 6.0, log on to the ES and import and analyze the desired Continuum dump file. In CCT 6.0, click to select the target MS/TP or Infinet networks. When doing so, navigate into the older version of AS-P to select the desired networks. Convert the dump file.
View full article
Admiral StephenYang Admiral
‎2024-02-05 07:42 AM

on ‎2024-02-05 07:42 AM

Labels:
  • Andover Continuum
  • Project Configuration Tool
6052 Views

Firmware version and bootloader version do not match

Issue Firmware version and bootloader version do not match Product Line Andover Continuum Environment BCX b3 Cause Verification required on why the two do not always match Resolution When firmware versions (application firmware files) are posted to the web, they do not always included the associated bootloader version. The reason for this is that rarely is a bootloader version changed. When bootloader versions do change it will be announced in the release notes for the particular firmware version.
View full article
Picard Product_Support
‎2018-09-06 01:49 PM

Last Updated: Sisko GavinHe Sisko ‎2024-01-30 12:39 AM

Labels:
  • Andover Continuum
1754 Views

Test the network card of a PC

Issue The network card is not working on the PC.  Product Line Andover Continuum, EcoStruxure Access Expert, EcoStruxure Building Expert, EcoStruxure Building Operation, EcoStruxure Security Expert, Satchwell BAS & Sigma, Satchwell MicroNet, TAC IA Series TAC I/NET, TAC Vista Environment PC Network Interface Card Cause Require a method to test the network card. Resolution Assuming you have the correct protocols loaded:- Open up a command prompt and type ‘ipconfig’(1) then press enter to get a list of the available network cards. Find the specific network card by name (2) Record the IP Address (3) assigned to the card, e.g. 192.168.5.90 If the card is unplugged (4) connect a network cable and start back at step 1 If the network card does not appear in Device Manager check the drivers are correctly installed for the card and when installed correctly start back at step 1. If the network card still does not appear it could be disabled.  In Network Connections right click the adaptor and select Enable (5) and start back at step 1. After these steps if the network card still does not appear when running ipconfig it is most likely damaged. If/when an IP Address is successfully obtained open a Command Prompt and type ping followed by the IP Address of the card, for example ping 192.168.5.90 (1). A functioning card will respond with 4 successfully replies (2) and the associated statistics (3) As additional information a good first step would be to "ping 127.0.0.1". This will not test a network card but indicates that the TCP/IP protocol is installed and functioning on the host PC.
View full article
Picard Product_Support
‎2018-09-06 03:27 PM

Last Updated: Sisko GavinHe Sisko ‎2024-01-25 08:06 AM

Labels:
  • Andover Continuum
  • EcoStruxure Access Expert
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
2159 Views

IO Channel number out of range when creating a door on AC1/AC1A/AC1Plus

Issue Received error 'IO Channel number out of range' when creating a door on AC1/AC1A/AC1Plus on an IO module.  The same door configured on a module with a lower IOU number saves successfully. Product Line Andover Continuum Environment Continuum CyberStation Netcontroller  AC Module Cause The IO module is configured with an IOU number that is above the MAX IOU modules supported by the NetController.  Note this is true even if there is only ONE module configured. Resolution Check the IOU module number entered in the door object (1) Check the Max IOU module supported (2)   Delete the IOU module and recreate it using an IOU number at or below the max IOU number supported by the Net Controller.
View full article
Picard Product_Support
‎2018-09-11 08:25 AM

Last Updated: Sisko GavinHe Sisko ‎2024-01-10 04:23 AM

Labels:
  • Andover Continuum
2269 Views

Reload error: Type not valid for this IO channel

Issue Infinity controller error: Type not valid for this IO channel Product Line Andover Continuum Environment Continuum Cyberstation Cause ElecType mismatch between what is in the database and the field controller hardware. An example of this problem would be offline creating a voltage output on a DO-4.  It will save to the DB since it is a valid InfinityOutput configuration.   Although when attempting to do a Send to Controller the controller knows that point type is not valid on the specific IOU module hardware. This can also happen when an object is imported into Continuum because the database error checking is less strict than when creating the object online. Resolution Go into offline editing Check the point configuration If it does not match the field hardware, then correct it, save it, go to online mode and reload.
View full article
Picard Product_Support
‎2018-09-06 10:57 AM

Last Updated: Sisko GavinHe Sisko ‎2024-01-10 05:11 AM

Labels:
  • Andover Continuum
2495 Views

Common causes of duplicate or multiple alarm events logged in database.

Issue The database is logging multiple alarm entries each time a point goes into alarm. Product Line Andover Continuum Environment Alarms MSMQ SQL Server Event Notifications Cause Various causes. Resolution The following is a list of conditions which may produce multiple alarm event logging. Network Latency  In cases where the network is extremely slow or workstation are overburdened, the process of logging alarms may be slowed to the point where a second alarm is sent by the controller while the previous alarm is still in the process of being logged. In one particular case the logging workstations associated with the duplicate log entries were all in India while the database server was in the US.  The problem was resolved by changing the ACCID of all of the India workstations to 253 or higher so that they were not involved in logging alarms. Database insertion errors If there are database insertion errors in the ACCTrace, Cyberstation cannot send an acknowledgement that the alarm event has been logged. Consequently the controller will continue to send the alarm event until it receives notification that the alarm has been successfully logged. Database Server latency It is not unusual to see Database Insertion errors when a Continuum DB server is struggling to keep up with the demands that the system has placed on it. A use Task Manager and other tools to evaluate the processor and memory consumption. Enhanced Alarm Logging and Enhanced Alarm Delivery. If Enhanced alarm logging/delivery is broken due not shutting down all workstations before doing a database update, it is possible to have combination of enhanced and old style alarm delivery.  The solution is to shut down all workstations and perform a db update with Enhanced Logging and Enhanced Delivery selected. Workstation Resources.  If the logging workstation is over burdened with reports, programs, extended log downloading, etc.
View full article
Picard Product_Support
‎2018-09-06 10:32 AM

Last Updated: Sisko GavinHe Sisko ‎2024-01-04 02:48 AM

Labels:
  • Andover Continuum
1471 Views

Setting up a Custom Wiegand HID Corporate 1000 48-bit format access card

Issue HID Corporate 1000 48-bit card not natively supported by Continuum System Product Line Andover Continuum Environment CX9900/9940 CX9702 CX9680 ACX5740/5720 Cause Continuum does not have built-in support for the HID Corp 1000 48-bit cards.  The system must be configured using a custom card format program. Beginning March, 2015, HID Global will introduce a new Corporate 1000 format referred to as “Corporate 1000 – 48”. All end-users who register for the Corporate 1000 program after February, 2015 will be issued a unique Company ID in the new Corporate 1000 – 48 format. The original 35-bit Corporate 1000 format will now be referred to as “Corporate 1000 – 35”. Those end-users who have been issued a unique Company ID in the Corporate 1000 – 35 format can continue to order credentials without interruption or change. Introduction of the new format will not impact or affect customers who registered for the program under the original structure. Resolution Here is the process to create a custom format for a HID Corp 1000 48-bit card in Continuum.  Only one custom card format can be used in NC1(CX99xx), NC2(CX968x) using AC1 modules, while up to four custom formats can be used with the ACX57xx and NC1/NC2 using AC1Plus modules. Create in each NC1, NC2, ACX57xx an InfinityNumeric point called AccessFormat (use this spelling exactly!). During the creation process, attach a manual array (log) with 22 entries to the point.  If creating more than  custom card format create InfinityNumeric points called Accessformat2, AccessFormat3 and AccessFormat4. Create the following InfinityProgram in each controller. The program should be type FallThru, and AutoStart.  The program can be copied to other access controllers where it is needed.   Note: The HID Corp 1000 48-bit card format allows site codes to be up to 22 bits, however, site codes in Continuum are restricted to a 16 bit value (0 to 65535), due to this Continuum limitation only the 16 least significant bits of the site code encoded on the cards can be read in Continuum, site code values above 65535 will show as different smaller number in Continuum. Program Name: SetCustCrdArray FlowType: FallThru AutoStart: True Code: Line SetFormat Set accessformat[0] to 1 'array has been initialized Set accessformat[1] to 48 'total number of bits in the format Set accessformat[2] to 0 'control mask Set accessformat[3] to 0 'mfg mask Set accessformat[4] to 0 'start bit of mfg Set accessformat[5] to 0 'end Set accessformat[6] to 8 'start of site code Set accessformat[7] to 23 'end Set accessformat[8] to 24 'start of card number Set accessformat[9] to 46 'end of card Set AccessFormat[10] to 14043 ' odd parity mask, first 16 bits Set AccessFormat[11] to 28086 ' odd parity, next 16 Set AccessFormat[12] to 56173 'odd parity, next 16 Set AccessFormat[13] to 0 ' odd parity, next 16 Set AccessFormat[14] to 23501 ' even parity, first 16 Set AccessFormat[15] to 45811 ' even parity, next 16 Set AccessFormat[16] to 28086 'even parity, next 16 Set AccessFormat[17] to 0 ' even parity, next 16 Set accessformat[18] to 0 'even number multiplier Set accessformat[19] to 0 'card number divider Set accessformat[18] to 0 'even number multiplier Set accessformat[19] to 0 'card number divider Set accessformat[20] to 0 'start bit of issue code Set accessformat[21] to 0 'end bit of issue code Set accessformat[22] to 0 'decimal shift of issue code stop
View full article
Picard Product_Support
‎2018-09-06 07:34 AM

Last Updated: Captain AbeMeran Captain ‎2023-12-15 06:55 AM

Labels:
  • Andover Continuum
10329 Views

Generate a Report of all card holders that have access to an Area

Issue Creating a Listview/Report to show all the personnel objects which have access to a given area.   Product Line Andover Continuum   Environment CyberStation   Cause Reports can be used to do a security audit of which individuals have access to certain Areas in a building.   Resolution Create a Listview object In the class field select AreaLink Add columns for PersonID and AreaID (Add any other column as needed) In the Qualifier tab enter the following qualifier: AreaID Is XXX Id where XXX = full path to area Example: AreaId is Root\AreaFolder\Lobby Id **NOTE Use folder\area aliases ONLY in the qualifier, do not use names. Save and run the Listview.  The Listview should show all Personnel objects that have the Area specified by AreaID in their Area list. To generate actual Report Object from the list view see How to create a Report from a Listview.
View full article
Picard Product_Support
‎2018-09-10 12:28 AM

Last Updated: Admiral David_Kendrick Admiral ‎2023-12-13 03:50 AM

Labels:
  • Andover Continuum
1938 Views

How to create a Report from a Listview

Issue Sending the results of a Listview to a Report.   Product Line Andover Continuum   Environment CyberStation   Cause Available options are not commonly known   Resolution There are two ways to display the contents of a Listview in a Report.   The first method is to create a Report and set its data source to 'Listview'.  Then in the filter tab add the desired Listview as a filter. Please note that only ONE list view can be added. When the Report executes it populates data from the Listview object.   The second method is to create an HTML Report template Then the HTML Report in the Listview's Report Template field In this case the report can be invoked right from the Listview
View full article
Picard Product_Support
‎2018-09-06 01:39 PM

Last Updated: Admiral David_Kendrick Admiral ‎2023-12-13 03:48 AM

Labels:
  • Andover Continuum
1995 Views

B3 and I2 Conversion Setting

Issue The Conversion Settings guideline is not documented. Product Line EcoStruxure Building Operation Environment Continuum Conversion Tool Infinet i2 BACnet B3 Cause Lack of information on "Conversion" column in Conversion Settings for B3 and I2 Resolution The Conversion column has the highest priority in the setting. If a formula exists then the setting below will not affect the Value.   Example The ElecValue is set to 10 for the following examples. 1. The Conversion field is empty, the ElecValue = 10 which corresponds to 100 on the Engineering scale. The Input Value = 100. 2. The Conversion field is set to ElecValue, and the ElecValue = 10. The Input Value = 10. 3. The Conversion field is set to ElecValue - 7. The Input Value = 3.  
View full article
Admiral StephenYang Admiral
‎2023-10-31 04:40 PM

on ‎2023-10-31 04:40 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
4749 Views

Why do BACnet objects that are deleted keep coming back?

Issue BACnet objects that are deleted from the BACnet side keep coming back. Product Line Andover Continuum Environment Cyberstation BACnet IP devices BACnet MSTP devices Cause Require to be able to find all the BACnet devices, delete the ones not required, and not have them reappear in Continuum Explorer. Resolution When BACnet is enabled, Cyberstation will automatically add devices into its database when it hears an “I-Am” message containing a Device Identifier it does not already know about. There is no way to disable this behavior without shutting BACnet off completely. I-Am messages are typically sent in response to Who-Is messages, but not always. Sometimes devices send I-Am messages when they start up for example.  Also, since I-Am’s are typically broadcast across the entire BACnet internetwork, the Cyberstation is likely to hear I-Am messages for lots of different reasons, like in response to Who-Is/I-Am sequences it’s not directly a part of.
View full article
Picard Product_Support
‎2018-09-06 10:35 AM

Last Updated: Sisko GavinHe Sisko ‎2023-10-30 03:57 AM

Labels:
  • Andover Continuum
1565 Views

Script Programs in Continuum compared to StruxureWare Building Operation and using floats (32 bits) and 64 bit numbers.

Issue With Script Programs in Continuum we were able to check the variable time against an integer value. Like "if time>500 then...".  In StruxureWare Building Operation time is of the type datetime, no longer an integer. Product Line EcoStruxure Building Operation Environment Script Program Cause In StruxureWare Building Operation a datetime internally is now a 64 bit number, so dates can go beyond the year 2038 which was the top limit for Continuum.  Numbers in script for StruxureWare, like in Continuum are just floats ( 32 bits ) so when trying to map a 64 bit number ( the date ) into a float it is not going to work.  You will get very erroneous readings, therefore the ban. Resolution Here are some examples of the correct StruxureWare program: Remember that for the dates, you can only compare dates to dates, not dates to numbers… In general,   you CAN do the following:       compare dates to dates                ==>   if Date1 > Date2  then     add numbers to dates                   ==>    LaterDate = LastDate + 24*3600     subtract numbers from dates         ==>    EarlierDate = LastDate - 24*3600   you CANNOT do the following   compare dates to numbers                ==>   if Date1 > 500  then
View full article
Picard Product_Support
‎2018-09-06 01:43 PM

Last Updated: Dave_Shore Schneider Alumni (Retired) ‎2023-10-17 07:13 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
2350 Views

Can Plain English interact with the Continuum Alarm Engine?

Issue How to setup and use the Plain English Alarm function?   Product Line Andover Continuum   Environment PEAlmFunction, PERtnFunction CyberStation Alarm Workstation PE function Cause Manual configuration is required to create the Plain English alarm function and set certain registry keys.   Resolution As a function of Continuum CyberStation Alarm Engine, user written Plain English functions are automatically invoked at a workstation when an alarm occurs when an alarm is acknowledged when a return-to-normal condition occurs. The user optionally specifies the names of those functions in the Windows registry, and they will be called appropriately. Registry keys used for calling Plain English Alarm function PEAlmFunction : The name of the user-defined PE Alarm Function. (Ex. “AlmProcess”) PERtnfunction : The name of the user-defined PE Return-to-Normal Function. (Ex. ”AlmProcess”) Example of the Plain English Alarm function is as follows: Arg 1 A ' Network AliasName(16) Arg 2 B ' Controller AliasName(16) Arg 3 C ' Infinet Controller AliasName(16) Arg 4 D ' Object name(32) Arg 5 E ' Object AliasName(16) Arg 6 F ' Object Description(32) Arg 7 G ' Object Value(Numeric) Arg 8 H ' Alarm State(3) ALM,RTN,ACK Arg 9 I ' Graphic Object AliasName(16) Arg 10 J ' Alarm Enrollment Alarm Message(String) Arg 11 K ' Alarm Enrollment AliasName(16) Arg 12 L ' EventNotification AliasName(16) Arg 13 M ' EventNotification Priority (Numeric 1~255) Arg 14 N ' TimeStamp(16) Arg 15 O 'Logging Flag (1~255) ' String 1 Q String 80 AlmDir, Fnam File AlmF ' If M < 100 then AlmDir = "C:\" Q = chr(96) Fnam = NumToStr(random(Second)) OpenFile(AlmDir ; Fnam ; ".alm", WriteOnly, AlmF) Print L ;", " ; K ; ", " ; A , B , C , D , ", " ; G to AlmF CloseFile(AlmF) Endif Return Success Create the following registry keys in HKEY_LOCAL_MACHINE\SOFTWARE\Andover Controls \Continuum\Settings: PEAckFunction (REG_SZ) PEAlmFunction (REG_SZ) PERtnFunction (REG_SZ) PEMaxBufferedAlarms (REG_DWORD) PEPopAlarm (REG_DWORD) Set PEAlmFunction to “AlmProcess” Set PERtnFunction to “RtnProcess” Restart Continuum. Create PE programs in the workstation called AlmProcess, and RtnProcess with source code similar to the example function. Files will be created in the specified directory containing the alarm and return to normal information.
View full article
Picard Product_Support
‎2018-09-10 11:14 AM

Last Updated: Admiral David_Kendrick Admiral ‎2023-10-06 07:07 AM

Labels:
  • Andover Continuum
2487 Views

BACnet Schedules and BACnet command priorities

Issue A BACnet Schedule is working but not changing the point it is controlling   Product Line Andover Continuum   Environment CyberStation Schedules BACnet command priority Cause A BACnet Schedule will by default, write to a BACnet point at a certain command priority level.  However if that BACnet point is also being commanded by a higher command priority then the present value of the point will not change according to the Schedule.   Resolution Example: A BACnet Binary value is created and the operator wishes to set the value to Off. If the value is set by a Manual Operator then by default this will command the point to Off at command priority 10. If a Schedule is then created and the point is attached to that Schedule, because a Schedule's default priority is 16, at the configured time, when the Schedule tries to change the point to On it can only command that point at command priority 16 The point itself always obeys the highest command priority which in this case is command priority 10 so the value stays Off.   To correct the above scenario there are two main options: Edit the Command Priority Tab of the BACnet Point and perform a Relinquish at command priority 10 to clear out that command, at which point the BACnet object will then defer to the next highest command priority (which in this case would be command priority 16) Edit the Schedule and change the command priority on the Schedule configuration page to an appropriately higher priority such as command priority 10.     NB. In cases where a point is written to at the same command priority as another object then the point will be controlled by whichever object wrote last...
View full article
Picard Product_Support
‎2018-09-06 01:36 PM

Last Updated: Admiral David_Kendrick Admiral ‎2023-10-06 07:02 AM

Labels:
  • Andover Continuum
3501 Views
  • « Previous
    • 1
    • …
    • 22
    • 23
    • 24
    • …
    • 110
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore