IO Channel number out of range when creating a door on AC1/AC1A/AC1Plus
  • IO Channel number out of range when creating a door on AC1/AC1A/AC1Plus
  • GavinHe
    GavinHe
  • AbeMeran
    AbeMeran
‎2018-09-11 08:25 AM
Last Updated: Sisko GavinHe Sisko ‎2024-01-10 04:23 AM
Received error 'IO Channel number out of range' when creating a door on AC1/AC1A/AC1Plus on an IO module.  The same door configured on a module with a lower IOU number saves successfully.
Andover Continuum
  • Continuum CyberStation
  • Netcontroller
  • AC Module
The IO module is configured with an IOU number that is above the MAX IOU modules supported by the NetController.  Note this is true even if there is only ONE module configured.
Check the IOU module number entered in the door object (1)
Check the Max IOU module supported (2)
Delete the IOU module and recreate it using an IOU number at or below the max IOU number supported by the Net Controller.
Tags (2)
  • 17856
  • GavinHeward24