Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Common causes of duplicate or multiple alarm events logged in database.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Common causes of duplicate or multiple alarm events logged in database.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • GavinHe
    GavinHe
  • DavidFisher
    DavidFisher
  • JohnBoehmer
    JohnBoehmer
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1299 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Common causes of duplicate or multiple alarm events logged in database.

Picard Product_Support
‎2018-09-06 10:32 AM

Last Updated: Admiral GavinHe Admiral ‎2024-01-04 02:48 AM

Issue

The database is logging multiple alarm entries each time a point goes into alarm.

Product Line

Andover Continuum

Environment

  • Alarms
  • MSMQ
  • SQL Server
  • Event Notifications

Cause

Various causes.

Resolution

The following is a list of conditions which may produce multiple alarm event logging.

Network Latency  In cases where the network is extremely slow or workstation are overburdened, the process of logging alarms may be slowed to the point where a second alarm is sent by the controller while the previous alarm is still in the process of being logged. In one particular case the logging workstations associated with the duplicate log entries were all in India while the database server was in the US.  The problem was resolved by changing the ACCID of all of the India workstations to 253 or higher so that they were not involved in logging alarms.

Database insertion errors If there are database insertion errors in the ACCTrace, Cyberstation cannot send an acknowledgement that the alarm event has been logged. Consequently the controller will continue to send the alarm event until it receives notification that the alarm has been successfully logged.

Database Server latency It is not unusual to see Database Insertion errors when a Continuum DB server is struggling to keep up with the demands that the system has placed on it. A use Task Manager and other tools to evaluate the processor and memory consumption.

Enhanced Alarm Logging and Enhanced Alarm Delivery. If Enhanced alarm logging/delivery is broken due not shutting down all workstations before doing a database update, it is possible to have combination of enhanced and old style alarm delivery.  The solution is to shut down all workstations and perform a db update with Enhanced Logging and Enhanced Delivery selected.

Workstation Resources.  If the logging workstation is over burdened with reports, programs, extended log downloading, etc.

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 12870
  • GavinHeward24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of