Setting up a Custom Wiegand HID Corporate 1000 48-bit format access card

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Setting up a Custom Wiegand HID Corporate 1000 48-bit format access card
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran
  • DavidFisher
    DavidFisher
  • JohnBoehmer
    JohnBoehmer
  • Clifton_eakes
    Clifton_eakes
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
10325 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Setting up a Custom Wiegand HID Corporate 1000 48-bit format access card

Picard Product_Support
‎2018-09-06 07:34 AM

Last Updated: Captain AbeMeran Captain ‎2023-12-15 06:55 AM

Issue

HID Corporate 1000 48-bit card not natively supported by Continuum System

Product Line

Andover Continuum

Environment

  • CX9900/9940
  • CX9702
  • CX9680
  • ACX5740/5720

Cause

Continuum does not have built-in support for the HID Corp 1000 48-bit cards.  The system must be configured using a custom card format program.

Beginning March, 2015, HID Global will introduce a new Corporate 1000 format referred to as “Corporate 1000 – 48”. All end-users who register for the Corporate 1000 program after February, 2015 will be issued a unique Company ID in the new Corporate 1000 – 48 format.

The original 35-bit Corporate 1000 format will now be referred to as “Corporate 1000 – 35”. Those end-users who have been issued a unique Company ID in the Corporate 1000 – 35 format can continue to order credentials without interruption or change. Introduction of the new format will not impact or affect customers who registered for the program under the original structure.

Resolution

Here is the process to create a custom format for a HID Corp 1000 48-bit card in Continuum.  Only one custom card format can be used in NC1(CX99xx), NC2(CX968x) using AC1 modules, while up to four custom formats can be used with the ACX57xx and NC1/NC2 using AC1Plus modules.

  1. Create in each NC1, NC2, ACX57xx an InfinityNumeric point called AccessFormat (use this spelling exactly!). During the creation process, attach a manual array (log) with 22 entries to the point.  If creating more than  custom card format create InfinityNumeric points called Accessformat2, AccessFormat3 and AccessFormat4.
  2. Create the following InfinityProgram in each controller. The program should be type FallThru, and AutoStart.  The program can be copied to other access controllers where it is needed.
     

Note: The HID Corp 1000 48-bit card format allows site codes to be up to 22 bits, however, site codes in Continuum are restricted to a 16 bit value (0 to 65535), due to this Continuum limitation only the 16 least significant bits of the site code encoded on the cards can be read in Continuum, site code values above 65535 will show as different smaller number in Continuum.

Program Name: SetCustCrdArray
FlowType: FallThru
AutoStart: True

Code:
Line SetFormat
  Set accessformat[0] to 1 'array has been initialized
  Set accessformat[1] to 48 'total number of bits in the format
  Set accessformat[2] to 0 'control mask
  Set accessformat[3] to 0 'mfg mask
  Set accessformat[4] to 0 'start bit of mfg
  Set accessformat[5] to 0 'end
  Set accessformat[6] to 8 'start of site code
  Set accessformat[7] to 23 'end
  Set accessformat[8] to 24 'start of card number
  Set accessformat[9] to 46 'end of card
  Set AccessFormat[10] to 14043 ' odd parity mask, first 16 bits 
Set AccessFormat[11] to 28086 ' odd parity, next 16
Set AccessFormat[12] to 56173 'odd parity, next 16
Set AccessFormat[13] to 0 ' odd parity, next 16
Set AccessFormat[14] to 23501 ' even parity, first 16
Set AccessFormat[15] to 45811 ' even parity, next 16
Set AccessFormat[16] to 28086 'even parity, next 16
Set AccessFormat[17] to 0 ' even parity, next 16 Set accessformat[18] to 0 'even number multiplier Set accessformat[19] to 0 'card number divider Set accessformat[18] to 0 'even number multiplier Set accessformat[19] to 0 'card number divider Set accessformat[20] to 0 'start bit of issue code Set accessformat[21] to 0 'end bit of issue code Set accessformat[22] to 0 'decimal shift of issue code

stop

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 19501
  • AbeMeran23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore