Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 501
  • Next »

Do not install N4.11 or 4.12 to a JACE-8000 or Edge 10 running 4.10U7 or later

Issue Upgrading a JACE-8000 or Edge-10 from 4.10U7 to 4.11 or 4.12 will prevent Niagara Daemon from starting.  You will be unable to connect via Workbench or Browser. Product Line TAC IA Series Environment I/A Series N4 Jace 8000 Tridium Edge 10 Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Cause The software in builds 4.10u7 and later LTS builds (4.10u8, 4.10u9, 4.10u10) was released after 4.11 and 4.12 reached EOL.   4.10u7 contains a newer signing key that is not recognized by 4.11 and 4.12. Resolution When upgrading JACE-8000 and/or Edge 10 running 4.10 LTS builds 4.10u7 and later, please skip over 4.11 and 4.12 and instead upgrade to 4.13u3 or newer. Alternatively, you may apply the dist that reverts JACE-8000 to clean 4.9u1 state, or for Edge-10, the dist that reverts it to clean 4.7 state. You can then install 4.11u2 or 4.12u2, if that's the version you have to use.  If you've already attempted the commissioning operation and bricked a device, and have backups, you can connect to the debug port and use the factory reset process per the documentation.  For Edge 10, consult the section titled Factory Default Recovery  in the Niagara Edge 10 Install and Startup Guide.  For JACE-8000, consult the section titled Restoring factory defaults  in the JACE-8000 Backup and Restore Guide. If you are lacking any backups for the host, then before performing the factory reset, you should enable SSH/SFTP via the debug port, and then copy out the Station files using Filezilla or WinSCP or equivalent.  Reach out to your support channel if you have difficulty finding the location of station files. Typically, the files will be in a subfolder of /home/niagara/stations. The config.bog file will be keyring encrypted, and you'll have to reset it using the Bog File Protection Tool. See Editing the .bog file passphrase offline in the Niagara Platform Guide  for details on using the Bog File Protection Tool.  For details on using the debug port on JACE-8000, see Debug port  in the JACE-8000 Install and Startup Guide.  For details on using the debug port on Edge-10, see Connecting to the debug system shell  in the Niagara Edge 10 Install and Startup Guide.
View full article
Guinan RandyDavis Guinan
‎2024-10-15 09:09 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:31 AM

Labels:
  • TAC IA Series
22894 Views

Unable to log into WorkStation due to license error codes -12, -15, -18 or -97

Issue When logging into Workstation one of the following error codes is given.  Invalid returned data from license server system. (Error code: -12) Cannot connect to license server system. (Error code: -15) License server system does not support this feature (Error code: -18) The desired vendor daemon is down. (Error code: -97) Product Line EcoStruxure Building Operation Environment Workstation License Server Cause These type of issues are contributed to the License Server, Vender Daemon being down or not having a valid license for the application which is used. Here is a complete list of error codes Resolution If Workstation is installed on a different PC than the license server, refer to SmartStruxure Workstation or editors can't get license when using firewall (errors -15 or -96). If you get license error -18 refer to Error "Requested license is not available on the license Server" even though the license for the StruxureWare Building Operation is valid. Start by working through the troubleshooting steps below. In some cases the Building Operation License Server was unable to start due to antivirus programs on the computer.    Cannot connect to FlexNet License Admin Using your internet browser and go to localhost:8888. If you are unable to connect to this address then the License Server is not running.  Ensure that the Building Operation X.X License Server is running as a service. Right Click on the Computer icon on the desktop and click on manage. In the system tree on the left, go to Services and Applications > Services.  Scroll through the list and select Building Operation X.X License Server. Click start in the top left corner of the window. Some times the following Windows Error 1067 is given when trying to start the License Server. Note: In the past this error has been caused by antivirus software on the computer. In this situation the antivirus program had to be uninstalled in order to allow the License Server to start.    If the Building Operation License Server will not start then it may be due to another program using TCP port 8888. Use TCPView to search for programs running on local port 8888 and stop the other program.      Vendor Daemon is Down Note: If working with a 32 bit PC, replace "Program Files (x86)" with "Program Files" in the file paths below. Using your internet browser go to the address localhost:8888. Click on Administration in the top right corner of the screen and login with admin/admin (If logging in for the first time it will prompt you to change the password.  Click on the Vendor Daemon Configuration tab and then select the taclic daemon.  Verify that the path in the License File or Directory field matches the location of the taclic.lic file. The first half of the file path is C:\Program Files (x86)\Schneider Electric StruxureWare\Building Operation X.X\License Server\ followed by what is in the License File or Directory field. Verify that the taclic.exe is located in the path found in the Vendor Daemon Location field. The first half of the file path is C:\Program Files (x86)\Schneider Electric StruxureWare\Building Operation X.X\License Server\ followed by what is in the Vendor Daemon Location field. If changes were made then click Save and then Start.    Vendor Daemon is Down issue caused by ipv6 Cases have been seen where having ipv6 enabled on the same computer where the license server is running causes the Daemon is down error.  Often there will be entries in the license server logs that are similar to: 17:46:44 (demo) Lost connection to lmgrd, heartbeat timeout expired, exiting. 17:46:44 (demo) EXITING DUE TO SIGNAL 37 Exit reason 5 17:46:44 (demo) IN: "f1" user1@host1 (SHUTDOWN) 17:46:44 (lmgrd) demo exited with status 37 (Communications error) To confirm whether this is the issue ask the site if it is OK to disable ipv6 on the machine temporarily. In Windows control panel disable ipv6 Reboot the computer. In some cases, it might be needed to disable IPv6 completely in the registry: https://tweaks.com/windows/40099/how-to-properly-disable-ipv6/ If the issue is resolved then inquire with the site if it is OK to leave ipv6 disabled. If SIGNAL 37 errors are seen in the license server logs, these can be caused by having the localhost name associated with the IPv6 loopback address in the hosts file. This can cause communication problems between the license server daemon (lmgrd) and the vendor daemon, resulting in shutdown of the latter. If you have a line like the following in the /etc/hosts file: ::1 localhost ip6-localhost ip6-loopback please change it to ::1 localhost6 ip6-localhost ip6-loopback so that the localhost name is associated only with the IPv4 127.0.0.1 address. Please note that modifying this file requires Windows administrative privileges.  
View full article
Picard Product_Support
‎2018-09-06 09:05 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:49 AM

Labels:
  • EcoStruxure Building Operation
22150 Views

EcoStruxure Workstation or editors can't get license when using firewall (errors -15 or -96)

Issue When PC based firewall's are used, some configuration in the license system and in the firewall are required to be made. In some cases, the error below when logging into Workstation appears: License server machine is down or not responding (Error code -15 or -96) Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause The TAC license (taclic) vendor daemon by default uses a random port each time it's started. This setting makes it difficult to handle in a firewall. Also the various EcoStruxure programs using the license system needs to be allowed in the firewall, as well as the ports used by the license system. Here is a simple explanation of how the license request from a client is made. Resolution Make sure there is a valid license installed on the license server. For more information read Requested license not available for Enterprise Server, Workstation or editors The easiest way to configure Windows firewall, is to run the SBO Firewall Config tool on all PC's having EcoStruxure software installed. For any questions regarding the use of this tool please contact the developer, details in the tool. In order to manually make the configuration follow the steps below. For more information on how to create Windows firewall rules, read Creating Inbound and Outbound Windows Firewall Rules.   On the server PC Make the port used by the vendor daemon fixed. Follow Define the port used by the taclic vendor daemon guide to do that. On the PC having the license server installed, open the following TCP ports in the firewall both inbound and outbound.  80 443 4444 2170 27000 through 27009 (If a user defined defined port has been used other than 2170 for the vendor daemon then use that instead of 2170)   On the client PC On the PC having EcoStruxure software installed using the license server on a remote PC, make these exceptions in the firewall: Allow ports TCP 80, 443, 4444, 2170 and TCP 27000 through 27009 both inbound and outbound. (If you defined a port other than 2170 for the vendor daemon then use that instead of 2170) Allow the following programs: SE.Graphics.Editor.exe SE.SBO.Script.Editor.Proxy.exe SE.SBO.ScriptEditor.exe SE.SBO.WorkStation.exe SE.WorkStation.IA.WptEd.exe tam32.exe They are typically located here: On 32 bit OS: C:\Program Files\Schneider Electric StruxureWare\Building Operation 1.X\WorkStation On 64 bit OS: C:\Program Files (x86)\Schneider Electric StruxureWare\Building Operation 1.X\WorkStation
View full article
Picard Product_Support
‎2018-09-11 07:47 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:49 AM

Labels:
  • EcoStruxure Building Operation
21630 Views

Time Synchronization of the ES and AS

Issue Trouble synchronizing the time of the Automation Server or Enterprise Server to a NTP server or between each other Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Enterprise Server EcoStruxure Building Operation Automation Server Cause The Enterprise Server and the Automation Server (ASP/ASB) do not synchronize time to each other, they must use an NTP server for synchronization Resolution The information below is mainly concerned with synchronizing the time setting but not the actual time.   Overview To synchronize the server times an NTP Server will be required, they do not synchronize time with each other. A common misconception is that the Automation Servers sync time with the Enterprise Server via server-to-server communications. To find an external NTP server consult support.ntp.org . Alternatively, an existing internal NTP server can be used or consult Setting up a Local / Internal NTP Server to configure the Enterprise Server computer as a time server The time settings on the Enterprise Server are configured through the operating system settings on the computer where Enterprise Central is installed.  EcoStruxure Building Operation cannot be used to configure the NTP server for the Enterprise Server. Please refer to Network Time on WorkStation, Enterprise Server, and Enterprise Central To find the Network Time Protocol (NTP) configured on a WorkStation, Enterprise Server, or Enterprise Central computer open a command prompt and enter w32tm /query /peers. If configured the peer NTP server(s) will be listed If you need to ensure an NTP server is actually running on certain IP or DNS address, please reference Ensure IP or DNS address is valid NTP server The time settings on the Automation Servers can only be configured via the Workstation. As per the image they can be configured to look at an NTP server (1) or set manually (2). For synchronization, they must use an NTP Server. Please refer to  Network Time Server on an Automation Server on Webhelp Starting in version 1.5, the time adjustment depends on how much the Automation Server drifts from the NTP server. The faster the Automation Server drifts, the more frequently the time is updated.  Please refer to How often will an Automation Server ask the NTP server for the time?  If the time server is a URL, such as time.nist.gov, then it is critical that a Primary DNS is set for each Automation Server, and possibly a Secondary DNS via Device Administrator. Without a DNS, the Automation Server will be unable to resolve the URL to an IP address. Please refer to Configuring the Automation Server IP Address on Webhelp The time displayed for a server in Workstation (Properties -> Basic) will reflect the time zone of the local computer that Workstation is installed on. All events and alarms will be automatically modified to match the time of the workstation that was used to log into the server. The "Server time" will represent the date and time of the server adjusted to client local time zone, while the fields below "Server time" represent the settings of the Automation Server.   How to synchronize date and time settings on multiple Automation Servers   IMPORTANT: Only the time settings are synchronized via the Lead/Shadow configuration, the time itself IS NOT synchronized via the Lead/Shadow but rather by all servers synchronizing with the configured timer server.   The synchronizing of multiple Automation servers can be achieved with a lead/shadow relationship. The primary and secondary network time server settings for connected shadow Automation servers are defined on the Enterprise server. Setting up the Primary and secondary time servers in the Enterprise Server only passes those configuration settings to the AS controllers, it does not send the actual time and date value.   Select the Enterprise server (1), click the Date & Time tab (2), select Enable (3) and enter the Primary time server (4) and, if used, the Secondary time server (5) the Automations Servers will use. Ensutre the time zone for the Enterprise Server is set correctly (6).   Save the settings  From EBO version 2.0 all Automations Servers are automatically configured to shadow the date and time settings configured in the Enterprise Server. To verify this expand the System folder of an Automation Server and select Time Settings -> Date and Time (1). Observe the Date and Time are Shadow-Read only (2), replicating the Enterprise Server settings. Attempting to change any of the settings, other than the Lead object (3), will result in an error. All the Automation Servers will be 'looking' to the same Primary (4) and Secondary time servers, i.e. they will all receive the same time and be synchronized Similarly, select the Time Zone (1) of the Automation Server in the System Tree; this will also be shadow-read only (2). The lead object is set to the Time Zone on the Enterprise Server (3) Before EBO version 2.0 the Automation Servers were not automatically set to shadow the Enterprise Server settings but this could easily be achieved en masse using Search . In the Search box in the top right corner of the Workstation, type "Date and Time" and click Search (1) to find the date and time object of all connected servers. In the Search view select the servers (2) that require their Date and Time settings synchronized to the Enterprise Server, the Enterprise Server does not need selecting. Select the Time tab (3) and then click the triple dots (4) to navigate to and select the Date and Time object on the Enterprise Server (5)   You may need to stop and start the Enterprise server to get the configuration settings to pass down to the shadow Automation servers Note: To set up synchronization of the time zone settings follow the above search steps for date and time but search on Time Zone Tip/Tricks To see the time of on the Enterprise Server and multiple Automation Servers use the Search to find the Date and Time object (1). Individually select each server (2) and then drag the Date and Time object (3) into the Watch Window (4) It is the Automation Server that initiates the synchronization. To check the Automation Server communication settings select the Automation Server (1) and in the Communication tab (2) select the Enterprise Server (3) and make sure the Automation Server has the correct IP address (4) To check the Enterprise Server communication settings select the Enterprise Server (1) and in the Communication tab (2) select each Automation Server (3) and make sure the correct IP address is specified for each Automation Server (4).  If a firewall exists ensure that the ports are open so the Automation Server can connect to the Enterprise Server. Please search for the EcoStruxure Building Operation IT Reference Guide on Exchange for details Further Information Release 1.2.0 and higher Until the time is set, b3 data will not update in the Watch Window Until the time is set, BACnet COV will not be functional Automation Server time does not synchronize directly with the Enterprise Server. Instead, all servers can synchronize to the same accessible time server To adjust the Automation Server time, time zone, and DST, access to the Automation Server is through a WorkStation
View full article
Picard Product_Support
‎2018-09-10 06:31 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:50 AM

Labels:
  • EcoStruxure Building Operation
21557 Views

Software and Firmware compatibility matrix for older versions of the traditional product lines

Issue Current information will be stored and updated in release notes and online documentation. Compatibility Matrix of Operating Systems, Video, Product Announcements, SQL Compatibility Product Line Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Windows Operating Systems and iBMS (intelligent Building Management System) Software Cause Compatibility, Firmware, Product Announcements Resolution Please see release documentation for current and recent products. For the Firmware compatibility matrix for: I/NET, it is available HERE or the EcoBuilding Download Center Continuum, click HERE Xenta Software Downloads HERE Vista, click HERE EcoStruxure Building Operation, click HERE Product Announcements can be a great tool for discovering which products have been tested and are compatible with the different versions. These documents are available on the Extranet, but have been compiled here for ease of access: I/NET 2.40   Product Announcement 2.41   Product Announcement 2.41a Product Announcement 2.42   Product Announcement and Compatibility Matrix (page 5) 2.43   Product Announcement PA-00239 2.44a Software Available from Exchange Download Center 2.45   Software Available from Exchange Download Center 2.46 Software Available from Exchange Download Center 2.47 Software Available from Exchange Download Center 2.47a Software Available from Exchange Download Center 2.47b Software Available from Exchange Download Center 2.48 Software Available from Exchange Download Center Operating Systems and SQL Supported Video Compatibility Support Policy PA-00279 Software Support for TAC I/NET Continuum v1.92 Product Announcement v1.93 Product Announcement v1.94 Product Announcement PA-00210 1.94 SP1 Product Announcement PA-00273 1.9 - 2.1 Software, Firmware, & Video Compatibility Matrix Concerning IE10 and IE11 browser support  2.0 Feature Blast 2.0 + 2.01/ 2.02 Update Compatibility Matrix 2.0  Product Announcement PA-00353 2.0 CyberStation Installation Guide 2.0 WebClient Installation Guide 2.0 Software License and Ordering Activation Process 2.0 Software and Controller Upgrade Process Andover Continuum PA-00333 Support Policy PA-00272 for Andover Continuum Vista v5.1.5 Product Announcement v5.1.6 Technical Product Advisory v5.1.7 release note document, TAC Vista Compatibility Matrix, SNVT Matrix documents, and TPA-VSTA-11-0020.00 v5.1.7 Product Announcement x5.1.8 Release Note TAC Vista 5.1.8 and TAC Xenta 500/700/900 5.1.8 v5.1.9 Vista Compatibility Matrix SecurityIAS Product Announcement PA-00291 Product Announcement TAC Vista transition to SmartStruxure solution overview  Support Policy PA-00274 for TAC Vista Satchwell Sigma v4.05 SEB Release Notes v4.06 Release Notes v4.06 Release Note Supplement v4.07 Release Notes Satchwell Sigma Standard Edition Installation and User’s Guide Support Policy PA-00297 for Satchwell Sigma v4.08 Release Notes PA-00397 Sigma Version 4.08 Sigma server on a virtual machine Satchwell Micronet data sheet - MicroNet View 2.1 OS Compatibility - Micronet View PA-00228 Product Announcement Support Policy PA-00298 for Satchwell MicroNet PA-00228 Satchwell MicroNet End of Commercialization Announcement I/A Series PA-00163 I/A Series R2 & G3 Product Announcement PA-00114 Legacy Products Windows 7 Compatibility I/A Series R2 with Windows Compatibility Chart PA-00243 Software Product Update - Q2 2013 PA-00251 Hardware Product Update - Q2 2013 PA-00278 Software Product Update - Q3 2013 I/A Series (Niagara) R2 Windows Compatibility Matrix with additional detail I/A Series (Niagara) AX/G3/N4 Windows Compatibility Matrix with additional detail Support Policy PA-00280 R1 for TAC I/A Series StruxureWare Building Operation Please visit Maximum number using StruxureWare Building Operation (Scalability and Capacity) SmartStruxure Lite Please visit SmartStruxure Lite solutions
View full article
Picard Product_Support
‎2018-09-07 07:37 AM

Last Updated: Crewman ContentModerator ‎2025-10-15 03:40 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • TAC IA Series
  • TAC INET
  • TAC Vista
21330 Views

Installation Guidelines for Electromagnetic Compatibility (EMC)

Issue Building Management System (BMS) equipment may malfunction due to electromagnetic interference (EMI) from nearby electrical devices. Diagnosing and resolving such issues can be complex and costly, making preventive installation practices essential. Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC Vista Environment All electrical equipment Cause Improper installation can lead to the generation or exposure to high- and low-frequency EMI, which may disrupt system performance or cause equipment failure. Resolution To ensure reliable operation and minimize EMI-related issues, follow these key EMC installation practices: Key EMC Practices Follow Manufacturer Recommendations Always adhere to the installation guidelines provided by equipment manufacturers, as they are tailored to the specific EMC requirements of each product. Proper Cable Routing Separate power and signal cables. Avoid parallel runs near high-interference sources (e.g., motors, transformers). Shielding Use shielded cables for sensitive signals. Ground shields correctly—typically at one end to prevent ground loops. Grounding and Bonding Establish a low-impedance ground path. Bond all equipment to a common ground reference. Surge Protection Install surge protection on power and communication lines. Protect against lightning and switching transients. Filtering Use EMI filters on power inputs. Apply ferrite beads or chokes on signal lines where needed. Physical Separation Maintain spacing between high-voltage and low-voltage components. Isolate noisy equipment from sensitive electronics. Enclosure Design Use metal enclosures for shielding. Ensure proper sealing and grounding of enclosure panels. Installation Environment Avoid placing equipment near strong EMI sources (e.g., radio transmitters, welding equipment). Maintain clean, dry conditions to prevent corrosion and poor connections. Compliance Testing Verify installations against relevant EMC standards (e.g., IEC, EN). Conduct site surveys if persistent issues arise. Reference Document: Practical Installation Guidelines for Electromagnetic Compatibility
View full article
Picard Product_Support
‎2018-09-06 12:00 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-29 07:41 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC Vista
21067 Views

Difference in Expansion IO Port power consumption between i2 and b3 field devices

Issue Continuum i2 and b3 devices share the same hardware platform, however, power consumption on the devices IO Expansion Port differs depending on the communication protocol firmware (Infinet or BACnet) running in the device. Product Line Andover Continuum, EcoStruxure Building Operation Environment All i2 devices All b3 devices Cause Even though the hardware of an i2 device is identical to that of its counterpart b3 device, the difference in firmware causes variation in power consumption on the device's Expansion IO port, specifically, it has been observed that the b3 devices adhere more strictly to the 180 mA limit than the i2 devices, resulting in loss of operation on IO channels located on the Expansion Port if the power limit is exceeded.  Now that conversion of devices from one protocol to another is occurring in the field, it has become evident that there are cases where the 180 mA limit is exceeded in an i2 device without any negative results, but once the i2 device is converted to a b3 device, all IO on the expansion port stop working. Resolution Before converting an i2 device to a b3 device in the field, it is crucial to review the Expansion IO Datasheet (attached) to ensure that the configuration does not exceed the specified power consumption limit. If the configuration exceeds the 180 mA limit, take the following steps: Remove any additional xP module causing the limit to be exceeded. Reconfigure the xP modules to ensure that the configuration does not consume more than 180 mA.
View full article
Captain AbeMeran Captain
‎2024-05-02 07:14 PM

on ‎2024-05-02 07:14 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
20926 Views

Refused to evaluate a string as JavaScript because 'unsafe-eval' is not an allowed source of script

Issue TGML Graphic worked without error in EcoStruxure Building Operation 2.0 WebStation. After an upgrade to 3.0, WebStation displays one of the following errors on page load: Script error in DocumentLoadEvent (Component_Name) Refused to evaluate a string as JavaScript because 'unsafe-eval' is not an allowed source of script in the following Content Security Policy directive: "script-src 'self' blob: 'unsafe-inline'". Do you want to continue running this script? This site says... Script error in DocumentLoadEvent (Component_Name) Blocked by Content Security Policy Do you want to continue running this script? Script error in DocumentLoadEvent (Component_Name) call to eval() blocked by CSP Do you want to continue running this script? Product Line EcoStruxure Building Operation Environment Building Operation 3.0 TGML Graphics Cause A new security setting in 3.0 disallows eval() statements by default in TGML JavaScripts presented in WebStation. An eval() statement executes a string of characters as code, which can open security vulnerabilities if enabled, something akin to a SQL injection or cross-site scripting attack. If graphics were created in earlier versions and relied on eval() to execute dynamic code, the user will be notified upon opening the graphic in 3.0 WebStation. Resolution Any graphics relying on eval() to execute dynamic code should have their JavaScript functions rewritten to avoid use of eval(). This is the preferred approach with respect to cyber-security. Work-Around It is possible, but not recommended, to disable the new security check in WebStation TGML graphics. Within WorkStation open the Control Panel Go to Security Settings Check the box for "Enable WebStation to use unsafe string evaluated JavaScript methods like 'eval' For more information, see Web Help article: Enabling WebStation to Use Unsafe JavaScript Methods. For the latest solution to this issue please refer to: Cannot Open Graphics in WebStation 
View full article
Administrator DavidFisher Administrator
‎2019-07-11 01:23 PM

Last Updated: Lt. Commander Reza Lt. Commander ‎2022-04-20 11:34 AM

Labels:
  • EcoStruxure Building Operation
19822 Views

Upgrade path from version 1.0 to current version

Issue Upgrade path from version 1.0 to a current version Product Line EcoStruxure Building Operation Environment SmartStruxure Building Operation versions 1.0, 1.1, 1.2, 1.3, 1.4, 1.5, 1.6, 1.7, 1.8, 1.9 EcoStruxure Building Operation versions 2.0, 3.0, 3.1, 3.2, 3.3 (limited), 4.0, 5.0, 6.0 Cause Upgrade path from version 1.0 to current - version Important - The upgrade process is sequential, for example, 1.1 to 1.2 to 1.3 to 1.4 From v1.9, non-sequential upgrades are possible  The primary released versions were, Release Note Dates (approximate) 1.0.0.161   1.1.0.362 Dec 2011 1.2.0.767 July 2012 1.3.0.938 Nov 2012 1.3.0.10100 SP1   1.3.0.20011 SP2   1.4.0.4020 Sept 2013 1.4.1.68-73 Oct 2013 1.5.0.532 July 2014 1.6.0.250 (RC) Dec 2014 1.6.1.5000 Feb 2015 1.6.2.27 Maintenance Release Jun 2016 see TPA-SBO-16-0003 1.7.0.255 (RC) July 2015 1.7.1.89 Oct 2015 1.7.2.29 Maintenance Release Jun 2016 see TPA-SBO-16-0003 1.8.0.244 (RC) Mar 2016 1.8.1.79-87 Jun 2016  1.9.1.95 Apr 2017   1.9.2.45 Maintenance Release Oct 2017  - See release note 1.9.3.24 Maintenance Release April 2018  - See release note 1.9.4.29 Maintenance Release April 2019  - See release note 2.0.1.130 & 135 June 2018 (130(License, WS, Reports Server) 135 - Server (AS, ES, EC)) - See release note 2.0.2.67 Maintenance Release Sep 2018  - See release note 2.0.3.45 Maintenance Release Dec 2018  - See release note 2.0.4.83 Maintenance Release June 2019  - See release note 3.0.1.104 May 2019  - See release note 3.0.2.33 Maintenance Release July 2019  - See release note 3.0.3.11 Maintenance Release Aug 2019  - See release note 3.0.4.43 Maintenance Release Dec 2019  - See release note 3.1.1.312 Dec 2019  - See release note 3.1.2.29 Maintenance Release Mar 2020  - See release note 3.2.1.630 Aug 2020  - See release note 3.2.2.61 Maintenance Release Nov 2020  - See release note 3.2.3.59 Maintenance Release Mar 2021  - See release note 3.3.1.59L Limited distribution release Feb 2021 - intended for specific feature compatibility with some hardware or applications - See release note EBO 2022 (4.0.1.86) Dec 2021 - This version follows v3.x, and reflects a new naming convention focused on release year for clarity - See release note EBO 2022 (4.0.2.559 & 562) Maintenance Release Apr 2022 - WorkStation Hotfix and License Admin 4.0.2.562, others 4.0.2.559, see revised release note EBO 2022 (4.0.3.176) Maintenance Release Jul 2022 - See release note EBO 2023 (5.0.1.86) Dec 2022 - See release note EBO 2024 (6.0.1.93) Mar 2024 - See release note Resolution It is most important to read the Release Notes and System Upgrade Reference Guide for each version you are upgrading to, as there are some special notes that only apply to some installation types. Click Here for Release Notes Click Here for Upgrade documentation The Minimum upgrade path would be as below (See Release Notes for any special instruction) 1.0.0.161 1.1.0.362 See StruxureWare Building Operation v1.0 to v1.1 upgrade issues Appendix A 1.1.0.1225 See Appendix A 1.2.0.767 See Appendix A This version can be avoided by using 1.2.0.1412 if possible 1.2.0.2207 (Hotfix) Available from PSS See also Appendix A 1.3.0.938 See also Appendix A 1.3.0.10100 (SP1) (needed if runtime compatibility is required during upgrade) 1.4.0.4020 or 1.4.1.68 (Only needed if runtime compatibility is required during upgrade) See Upgrading Automation Servers from 1.3 to 1.4 1.5.0.532 1.6.1.5000 See Upgrade to 1.5.0 or 1.6.0 fails 1.7.1.89 1.8.1.87 See Product Announcement 00471 Pre-Upgrade LON Add-On 1.7.1 to 1.8.x 1.9.1.95 Possible to upgrade directly from v1.5, but carefully study the release notes and upgrade instructions Option to 1.9.2.45 Upgrade options more limited with this version, only from v1.7.2, see the release note Option to 1.9.3.24 Upgrade options more limited with this version, only from v1.7.2, see the release note Option to 1.9.4.29 Upgrade options more limited with this version, only from v1.7.2, see the release note 2.0.1.130/135 Possible to upgrade directly from v1.5, but carefully study the release notes and upgrade instructions. NOTE the new License structure for v2.0. 3.0.1.104 Possible to upgrade directly from v1.8, see the table in "System Upgrade Reference Guide" (3.0.1 System Upgrade Overview), but carefully study the release notes and upgrade instructions. NOTE the new Licenses for v3.0. 3.1.1.312 Possible to upgrade directly from v1.8 See Release notes and upgrade documents for full details 3.2.1.630 AS Classic not supported, Win 7 and Win server 2008 not supported 3.3.1.59L Limited distribution release - intended for specific feature compatibility with some hardware or applications, see release note for details. If you do not require the specific features outlined in this Release Notes, it is recommend installing EcoStruxure Building Operation 3.2.x instead EBO 2022 (4.0.1.86 and later) The following protocols, objects, and devices are not supported in EcoStruxure Building Operation 4.0 or higher: I/NET, Sigma, MicroNet, NETWORK 8000 ASD and LCM. A multi-version system supports I/NET, MicroNet, NETWORK 8000 ASD and LCM on automation servers and Sigma on an enterprise server, running an earlier version than 4.0. Report Server/WebReports is not supported in EcoStruxure Building Operation 4.0 or higher. See release notes for details. EBO 2023 (5.0.1.128 and later) New SpaceLogic and Easylogic Controller support, External Storage support for MS SQL, Some support for IPv6, BACnet protocol rev.16, Virtualized Automation Server - Edge Server added,   See release notes for details. EBO 2024 (6.0.1.93 and later) Added New Software Assurnace, Sustainability Pack, EBO Enterprise Server and Enterprise Central for Linux, OPC UA Client Support, Modbus2 Support, Visual Programming for Function Block, XLSX Report, and Touch Room Controller Support. See release notes for details. Appendix A - Upgrading from Specific 1.x Builds Upgrade from V1.0.0.XXXX to V1.3 (via V1.1 and V1.2) Upgrade from 1.0.0.XXXX to 1.1.0.1225 Upgrade from 1.1.0.1225 to 1.2.0.1412 (Do not use 1.2.0.767) Upgrade from 1.2.0.1412 to 1.3 Upgrade from V1.1.0.XXXX to V1.3 (via V1.2) Upgrade from 1.1.0.XXXX to 1.2.0.1412 (Do not use 1.2.0.767) Upgrade from 1.2.0.1412 to 1.3 Upgrade from V1.2.0.767 to V1.3 Apply hotfix 1.2.0.2207 Upgrade from 1.2.0.2207 to 1.3 NOTE: These hotfix builds are not available for download from the Extranet site, you will need to contact Product Support and request them
View full article
Picard Product_Support
‎2021-02-16 12:31 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:22 AM

Labels:
  • EcoStruxure Building Operation
19215 Views

Error - Upgrade using DFU mode system alarm AS status LED red

Issue AS status LED solid red for a few seconds followed by a quick blink. Device administrator and/or event log shows system alarm ..."Error - Upgrade using DFU mode"  Product Line EcoStruxure Building Operation Environment Building Operation Automation Server, AS, ASP, ASB Building Operation Device Administrator Building Operation WorkStation Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Cause The indication of "Error – Upgrade using DFU mode" occurs due to the fact that a possible problem with writing to the file system has been detected when booting the system. This error can be seen in WorkStation as an Alarm Event, in the Server Logs, or in Device Administrator. Nosync errors are usually seen in the system log. The configuration of the system could have been compromised as a result, although the issue is not necessarily fatal and therefore the AS is allowed to run and the situation is indicated via the red status light. A system alarm is also generated as a warning as seen in the screenshot above. Resolution Since the AS file system could have been compromised, it must be re-initialized from scratch. To clear the red light: Make sure a backup of the AS is available. Attach the Device Administrator to the AS via USB and put the AS in DFU mode (press the reset button 3 times in rapid succession) Install a new database Once the AS has had its FW and database reinstalled, restore the backup using Workstation. NOTES See Error – Upgrade Using DFU Mode  If this error occurs, especially if it occurs multiple times on the same server, check the site installation include Grounding/Earthing and power supplies and for possible EMC issues (Electromagnetic Compatibility)
View full article
Picard Product_Support
‎2021-02-11 08:06 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:34 AM

Labels:
  • EcoStruxure Building Operation
19180 Views

Conversion of Continuum devices from i2 to b3 and vice-versa in the field

Issue Continuum i2 and b3 field devices use the same hardware. With the exception of their -V models and the bCX (bCX9640/bCX4040) controller, they were not designed to have their firmware swapped from Infinet to BACnet (or BACnet to Infinet) in the field. Product Line Andover Continuum, EcoStruxure Building Operation Environment Continuum i2 Controllers (except -V) Continuum b3 Controller (except -V) Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Cause With the exception of the -V controllers, the devices were not designed to have their protocol (Infinet/BACnet) swapped in the field, however, due to changes in market needs R&D is now providing a method to allow the protocol to be changed in the field. Resolution IMPORTANT: If a RoamIO2 is available, it can be used to do the conversion without the need to have Continuum Cyberstation and Continuum controllers. https://community.se.com/t5/Building-Automation-Knowledge/Conversion-of-Continuum-devices-from-i2-to-b3-and-vice-versa-in/ta-p/448337    To convert i2 field devices into b3 BACnet (or vice-versa) from CyberStation Contact PSS and request the conversion files for the specific model(s) you wish to convert. Follow the procedure detailed below or as per the attached document. To swap the firmware of any non -V i2 device from one protocol to the other (in this case, from Infinet to BACnet b3), you use the following procedure.  For more information, see section 1.3 “Converting Infinet i2 Field Devices to BACnet b3 Devices from CyberStation” below. NOTE: This procedure was developed by Schneider Electric’s R&D and tested in the Product Support Services (PSS) lab.   Before starting the procedure, you need the following items: An I2 device(s) to be converted. A Continuum CyberStation with i2 device(s) configured and online. A special, conversion b3 upgrade file for the appropriate device model as provided by PSS A b3 bootloader file for the appropriate device model, provided by PSS Physical access to the device.  You need this to push its Restart switch or to access the switch or breaker where you can shut off power to the device to force a restart. A bCX4040 controller configured in CyberStation xP Expansion I/O Note If the device to be converted from i2 to b3 has any expansion modules attached, make sure the modules do not exceed the power capacity of the expansion port (180 mA), it has been observed that the b3 devices adhere more strictly to the 180 mA limit than the i2 devices, resulting in loss of operation on IO channels located on the Expansion Port if the power limit is exceeded.  See attached xP Expansion IO Datasheet for information on power consumption of each xP IO module.   1.2 Preparing the Field Bus for the i2 to b3 Device Conversion To ensure a smooth conversion, it is necessary that you reduce the traffic on the field bus as much as possible in order to provide the necessary bandwidth to the upgrade operations required for the conversion. Before starting the process with the conversion file, be sure to follow these instructions.    To prepare the field bus for the i2 to b3 device conversion Disable all the programs in all the devices residing in the field bus. Close all Continuum Workstations except the one performing the upgrade. In the Workstation performing the upgrade, close all graphics, List views, and anything else that could be polling data from the field bus. Make sure MS/TP field bus is on same baud rate as Infinet field bus, mainly 19.2K 1.3 Converting i2 Field Devices into b3 BACnet from CyberStation You can convert Infinet i2 field devices into b3 BACnet field devices by swapping the firmware of any non -V model i2 device. IMPORTANT: When using this procedure, be aware of the following guidelines: It applies ONLY to the firmware or communication protocol (Infinet or BACnet) of the device. It does not convert the control application in the device. Following conversion, the device’s memory is cleared, so you need to configure a new control application. It may result in a loss of critical data if not performed properly. Before beginning, ensure that all important data is backed up in the event of data loss or the device losing its application and becoming non-operational.  For more information, see section 1.1 “Introduction” above. To convert i2 field devices into b3 BACnet from CyberStation Contact PSS and request the conversion files for the specific model(s) you wish to convert. You will be provided with an application file (namely, i2920toB3920B4.500077.upd) and a boot loader file (namely, B3920BootB4.500077.upd). From CyberStation, edit the i2 device and record its Serial Number and Infinet id. Consult the General tab to locate this information. From the Runtime tab, perform a Reset to clear the device’s database. Upgrade the i2 device using the application file provided by PSS. Once the upgrade is complete, the i2 device stays Offline since its communication protocol has now been swapped from Infinet to BACnet. Disconnect the device from the Infinet field bus of its host master controller (for example, a CX9680 or a bCX9640). Connect it to the bCX4040 MS/TP field bus. (MAKE SURE MS/TP FIELD BUS IS RUNNING AT SAME BAUD AS INFINET FIELD BUS DEVICE WAS ON, NAMELY 19.2K BAUD) In the bCX4040, configure a b3 device using the appropriate model as well the Serial Number and ID recorded previously. NOTE: You will need to provide BACnet Device ID. Typically, it will be the same as the Serial Number. You can also use a Learn to bring the device online under the bCX4040 and automatically assign the model, id etc.  Refer to this Knowledge Base article on using the serial number for the Device ID.  Remember here to set the Comm Port for comm2. Restart the device either by power cycling or using the restart button. The device will come online under the bCX4040 as a b3 device. Perform an Update b3 OS operation to send the appropriate b3 boot loader file provided by PSS. Go to the Runtime tab, and reset the device once the update is finished. Once the device reboots and comes back online, you can confirm it has the right boot loader by looking at the device from the BACnet side. The screenshots that follow display the before and after results of the i2 to b3 conversion process. Before: After: NOTE 1 If Continuum system is not available it is also possible to convert i2 to b3 using RoamIO and EBO server using the following steps Disconnect device from field bus and connect RoamIO directly to i2 device. Use InfinetServiceTool to send the application conversion file to the i2 device. After the uprev operation is done disconnect RoamIO and cycle power to the i2 device Connect converted device (now a b3) to MSTP of AS-P or other EBO server that supports BACnet MSTP Perform a b3 learn operation to bring the device online Right click the b3 device and proveed to 'Device->Update firmware...' Navigate to appropriate boot loader file for the b3 model After uprev of boot loader is complete, cycle power to the b3 device. NOTE 2 Similar steps can be used to convert b3 device to i2 device. Make sure to use the V2 version of the b3 to i2 conversion files as it was found the original set of b3 to i2 conversion files did not work in some cases. Please note that once a b3 device has been converted to i2 using this procedure the device will ONLY accept conversion uprev files, attempt to uprev using regular uprev file will result in the following error:   This Uprev file does not match this type of controller. This applies to b3 to i2 conversion only, it does not apply to i2 to b3 conversion.
View full article
Captain AbeMeran Captain
‎2022-12-06 09:57 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:33 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
18960 Views

License activation or repair without Internet access

Issue License needs to be activated or repaired, but there is no Internet access on the computer hosting the license. Product Line EcoStruxure Building Operation Environment Building Operation License Administrator  Cause The computer cannot be moved to a location with Internet access for activation or repair. IT policies prohibit temporary Internet access for licensing purposes. Resolution SBO Offline Activation Tool Use the SBO Offline Activation Tool for offline license activation. Access the tool here: SBO Offline Activation Tool. Click Instruction and Help in the tool for step-by-step guidance and helpful videos/charts. SBO Offline License Repair The same tool can repair offline licenses. Access the tool here: SBO Offline Activation Tool. After launching the tool, go to Special Operations → Repair License. If repair fails, contact Support for further troubleshooting.
View full article
Picard Product_Support
‎2018-09-06 11:16 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-20 04:10 AM

Labels:
  • EcoStruxure Building Operation
18861 Views

Alarm Email notifications with a 3rd party mail account (SMTP)

Issue Email notifications from 3rd party email account such as Gmail, Hotmail, Yahoo SMTP issues Event notification Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation site with any of the following: AS, ES, Reports Server Cause Sending notifications to Gmail, Yahoo mail, Hotmail, or other outside email account. Wanting to use other SMTP than Schneider Electric E-mail Server: if wanting to setup an ES or AS to send email notifications with third party SMTP, an Exchange server using port 25 supports the notifications. In release 1.7.1 and earlier though Gmail, for example, suggests port 465 and 587, the workstations alarms that the email can not be sent since it cannot connect to email server. The problem is with the Gmail-account and often other 3rd party email providers both public and private, Google requires that you connect with SSL, which have been missing in the requirements and therefore these releases do not have this functionality. In release 1.8.1 and later, you can send emails not encrypted or encrypted using either the TSL or the SSL protocol. You can select one method for the primary email server and another method for the secondary email server. The Schneider Electric Email Server does not support encrypted emails. When logging on to the email server, the user is authenticated using an authentication protocol. If no user name is specified, no authentication protocol is specified. If a user name is specified, the SmartStruxure server tries to authorize the user using the CRAM-MD5 protocol. If the first authentication fails, the SmartStruxure server tries to authorize the user using the LOGIN protocol using the CRAM-MD5 protocol. Resolution In Email Notification put the 3rd party email address such as yourname@mailprovider.com. AS and ES will use the Schneider Electric SMTP server or the POP server of your choice to send the email notification. For multiple emails, check Multiple Email Addresses for Email Notifications or Alarm Recipients. Sometimes the mail is put in the Spam folder for the recipient. Check there and change settings to Not Spam. Installing a valid SSL certificate for the Enterprise Server to allow SSL operation is not planned in a future version. Currently, the default certificate does not identify the system and is not trusted, but nevertheless enables SSL operation. ESMTP (Extended) is not supported through current release. Base64 SMTP authentication is not supported. Wanting to use SMTP other than Schneider Electric E-mail Server: An Exchange server or SMTP server which supports POP and uses port 25 supports AS and ES Notifications. Other servers which would require the setting of Primary/Secondary E-mail server fails to login to SMTP Server require an encrypted (SSL/TLS) connection which is not supported in Struxureware Building Operation versions up to and including 1.7.1. A solution is to use an SMTP proxy on the ES or another computer on the network that will handle the TLS/SSL authentication. Release 1.8.1 and later support TLS and SSL for email authentication natively. Using SmtpProxy on an Enterprise Server SmtpProxy is a small freeware application that listens on a port you choose; the default port is 25. When SmtpProxy detects a connection on this port, it does the following: Connects to the SMTP server you configure (GMail / Microsoft Live Mail / any other SMTP server) Starts an encrypted connection with the SMTP server Returns the connection information to the ES After the initial connection is established, SmtpProxy acts as a middleman. Any SMTP data received from the ES is forwarded to the SMTP server and any data returned from the SMTP server is sent the ES. SmptProxy runs as a Windows service so it can be installed on a LAN server and used by multiple devices such as AS. Note that SmtpProxy does NOT login to the SMTP server but rather credentials are passed through from the ES or AS. Note: SmtpProxy is a third party application and therefore no support is provided by Schneider Electric. Installing SmtpProxy SMTPProxy can be downloaded from http://smtpproxy.codeplex.com/ The download is a Windows Installer (MSI) file that can be used to install SmtpProxy on any machine that supports the .NET Framework v4 – Client Profile. Configuring SMTPProxy for Gmail SmtpProxy is configured using a config file. A sample config file is installed with SmtpProxy, this is a plain text file that can be edited with Notepad. Create a copy of the sample config file and rename it to: On 32 bit machines: C:\Program Files\SmtpProxy\SmtpProxy.exe.config On 64 bit machines: C:\Program Files (x86)\SmtpProxy\SmtpProxy.exe.config The following items can be configured with SmtpProxy’s config file: SmtpProxy can write a log of all its activities. The default file to write the log file to is SmtpProxy.trace.log. SmtpProxy can log several different types of activities. You can control what is written to the log file by setting the log switches. By default, they are set to Off so nothing is written to the log file. Valid switch values are Off, Error, Warning, Info, and Verbose with each one providing more information than the last. Once you have SmtpProxy working, you should turn logging Off. The Url to the SMTP server. Default is smtp.live.com. The SMTP server port. Default is 587. The port to listen on. Default is 25. Scroll to the end of the config file and locate the section SmtpProxy.Properties.Settings section and find the string mail.live.com Edit this to smtp.gmail.com After modification, you must restart the Smtp Proxy service from the services control panel for the new settings to take effect. Configuring ES to use SmtpProxy Right click on the Server in the tree and select Properties then click the Email tab Select Primary/Secondary E-Mail Server Enter Sender E-mail (e.g. Mysite@gmail.com) Under Primary E-Mail Server Settings enter Host: localhost (or 127.0.0.1) Enter the users account information. User name: e.g. gmailaccountname@gmail.com Password: MyPassword Confirm: MyP
View full article
Picard Product_Support
‎2018-09-10 05:06 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 05:17 PM

Labels:
  • EcoStruxure Building Operation
18822 Views

Tridium N4.11 Upgrade Considerations

Issue Tridium N4.11 Upgrade Considerations  Product Line TAC IA Series Environment I/A Series N4.11 Enterprise Server I/A Series N4.11 Jace 8000 Cause Detailed information about N4.11 upgrade prerequisites and best practices  Resolution The following details a set of upgrade considerations and known issues and their workarounds regarding Niagara 4.11. Please review prior to upgrading to Niagara 4.11. Niagara 4.11 and Default NRE Memory Changes: A change to the JACE-8000 file system has been introduced with the release of Niagara 4.11. The RAM disk was used to store alarm and history data. During station save, this data was copied from the RAM disk and zipped up into a single file that was stored on flash. In Niagara 4.11, the RAM disk has been removed entirely. This data is now written directly to the flash memory. This change has enabled ~384MB of RAM to be freed up to improve performance. Some of the space has been reallocated to code cache, metaspace, and heap space in the 4.11 NRE default settings. Any additional memory space is now available as general free memory. These changes should be transparent to most users and will provide moderate performance improvements on the JACE-8000. Prior to upgrading your JACE-8000, please review NRE default configuration changes and RAM disk removal In 4.11. Niagara 4.11 and Third-Party Modules Keeping your Niagara installations safe and secure is our highest priority. In Niagara 4.11, ALL third-party modules must be signed with either a trusted valid certificate or a self-signed certificate to successfully run on a station. This new policy greatly increases the security posture of Niagara installations by making administrators aware of any modules that may have been tampered with, compromised, or derived from untrustworthy sources. Niagara's new signature enforcement feature is being rolled out over multiple Niagara releases. The first iteration was built into release 4.8 to give developers adequate time to make the transition to always signing any third-party modules. Niagara 4.8 produced console and Security Dashboard warnings about unsigned modules but allowed them to run on a station. As of Niagara 4.11, unsigned modules will not execute. For more information, please review the Niagara documentation on Third-Party Module Signing Niagara 4.11 Updated Operating Systems, Browsers, and Databases For the latest information on supported operating systems, please refer to Supported OS and other software in the Niagara 4 Framework Installation Guide. Tridium remains focused on keeping pace with advancing IT infrastructure to enable more efficient, long-term support of each release version. This policy enhances the security posture of a Niagara installation by ensuring that only the most robust, secure operating systems and enterprise applications are compatible with the framework. The list below provides information on what we will be supporting with Niagara 4.11.   OS, Browser, Database Version Red Hat Enterprise Linux 8.1 (64 bit), 7.7 Ubuntu Linux 20.04 LTS – Desktop & Server Windows Server 2019 (64 bit), Server 2016 (64 bit), Windows 10 (64 bit) VMWare ESXi 6.7 Oracle Database 19.3, 18.3, ... 12.2/12.1 MySQL Database 8 MS SQL Database 2019, 2017, 2016 Browsers Chrome, FireFox, Microsoft Edge Mobile Browsers Safari (iOS 12, 13), Chrome (Android 8, 9, 10) As with all software products, we must also deprecate support for some operating systems and enterprise applications.  Nevertheless, you can be confident that the above list will handle your needs moving forward. Using Web Launcher with Niagara 4.11 Web Launcher 21.4.1 was recently revamped for Niagara 4.11 to include essential software dependencies updates along with critical defect fixes. This version of Web Launcher has Java version 8 update 311 and certificate management has been updated to work with Niagara 4.11 along with any legacy or prospective release. Prior to using Web Launcher with Niagara 4.11, customers should update Web Launcher accordingly (see steps below). How to update Web Launcher? Web Launcher has a feature to check for updates over the internet and prompts the user when a new version is available in the cloud. However, the existing version of Web Launcher has a bug that prevents a smooth update. Users will be required to perform a fresh install by downloading the latest version from the cloud via the station web Login page. Click on the Niagara Web Launcher Installer link on the station's Web Launcher Web Page, which can be reached via the link on the Login page itself. Once the download is successful, click on the msi file and follow the installation wizard. You do not have to uninstall the older version. The new installation will automatically update to the latest version. Niagara 4.11 Release Notes: The release notes for Niagara 4.11 are located here.
View full article
Guinan RandyDavis Guinan
‎2022-05-10 11:15 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:54 AM

Labels:
  • TAC IA Series
18763 Views

PID definitions for Plain English/Script AutoTune PIDs

Issue PID Definitions and definition for AutoTune PIDs. Product Line Andover Continuum, EcoStruxure Building Operation Environment Continuum 1.94 StruxureWare Building Operation 1.1 and higher Cause Argument for bPID in Continuum and StruxureWare Building Operation are: Arg 1 Ena Arg 2 Type Arg 3 Cv Arg 4 SP Arg 5 Kp Arg 6 LKi Arg 7 LKd Arg 8 Db Arg 9 OP Arg 10 Bias Arg 11 Isum Arg 12 err Arg 13 Ltim Arguments for AutoTuner PID Continuum and StruxureWare Building Operation are: Arg 1 Ena Tuning Enable Arg 2 Type type of control Arg 3 Cv Measured variable Arg 4 SP Setpoint Arg 5 Kp Proportional gain constant Arg 6 Ki Integral gain constant Arg 7 Kd Derivative gain constant Arg 8 Db Deadband Arg 9 OP Output Arg 10 Lag Output Device Lag time Arg 11 Dev Deviation from setpoint allowed Arg 12 Pd Passed Data Array of 17 Numerics Arg 13 Ta Time Date Array of 3 Variables Resolution For AutoTunerPID Wizard keep in mind that it is different than PID or often referred to as BPID. There are 3 types of PIDs bPID (normal PID) Simple PID (which was used for less memory available in controllers and had 9 Arguments) AutoTunerPID (designed to be run once on a system to ascertain the required values of Proportional, Integral and Derivative factors (Kp, Ki, Kd), when complete the function is normally to be replaced by the standard PID function as it will run faster with less system overhead. However when tuning is complete the PID tuning function will continue to control the plant using the standard PID function.) Please note that PIDs are no longer autoconfig and there is no generic PID functionality with Continuum 1.94 and StruxureWare Building Operation 1.1 and higher, but custom solutions instead.  bPID information on page 101 available in PID Function.pdf Simple PID is on page 90 of the above link AutoTunerPID information available in PID AutoTuner.pdf
View full article
Picard Product_Support
‎2018-09-06 03:28 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:49 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
18274 Views

What cable type should be used for BACnet MS/TP communications?

Issue What specification should BACnet MS/TP cable meet? Product Line Andover Continuum, EcoStruxure Building Operation Environment MS/TP BACnet devices Cause Often an incorrect cable type is used when wiring MS/TP devices causing unreliable communications. Resolution The BACnet Controller Technical Reference defines the following cable specification for a MS/TP cable: RS-485 Cable Specifications: Cables used to form the RS-485 network should conform to the following specifications: Wire Size: 22-24 AWG Cable Type: Twisted-pair, copper wire, tinned Shield: Braid Nominal Impedance: 100-120 Ohms Velocity of propagation: 78% Capacitance: <12.5 pF/ft (~ 41pF/M) between conductors and < 22 pF/ft (~72pF/M) between the conductor connected to ground and the next conductor. An example of a cable that meets this specification is Belden 3105A. Also check out the SmartStruxure-RS485-Network Installation Quick-Help video on the Exchange.
View full article
Picard Product_Support
‎2018-09-07 02:08 PM

Last Updated: Crewman ContentModerator ‎2025-10-15 03:41 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
17554 Views

How to read individual bits from a Modbus Holding Register

Issue How to read individual bits from a Modbus Holding Register that holds a 16-Bit Word and represent each Bit as a separate Digital point Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server (AS, AS-P, AS-B) Modbus TCP/IP Modbus RTU (RS485) Cause There is a requirement for a Modbus Holding Register that is a 16-bit unsigned value, each bit represents a digital state in the Modbus device and to replicate this as 16 separate digital states in EBO. The 16-bit unsigned value is an integer with a range of 0 to 65,535 and needs to be converted into 16 digital values. Resolution Use a Modbus Digital Input point for each bit required. Each object will be configured to read the same Modbus register address, but with a different bitmask value applied prior to evaluating the value. For example: Read Modbus Holding Register 40123 with a value of 32769 (16-bit unsigned) and decode bits 0, 8, and 15 as three separate Digital points Since the actual Value of 32769 being read at address 40123 is shown in Binary as 1000000000000001 it can be seen that Bit 0 and Bit 15 should return TRUE while Bit 8 should return FALSE Configure each point as follows: Modbus Digital Input Point 40123 bit 0 Register number 123 Register type 16 bit unsigned Read function code 03 Bit mask - enable only Bit 0   Modbus Digital Input Point 40123 bit 8 Register number 123 Register type 16 bit unsigned Read function code 03 Bit mask - enable only Bit 8   Modbus Digital Input Point 40123 bit 15 Register number 123 Register type 16 bit unsigned Read function code 03 Bit mask - enable only Bit 15   Additional information can be found in the EcoStruxure Building Operation - Technical Reference Guide - Search for Bitmask.   If you need to break this bit information out for programming this can be done with a FB application and just binding the full 16 bits to the FB as shown here.
View full article
Picard Product_Support
‎2018-09-07 02:33 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:45 AM

Labels:
  • EcoStruxure Building Operation
17462 Views

WorkPlace Tech 5.8.x, 5.9.x, 5.10.x, and 5.11.x Operating System and Microsoft Visio Compatibility

Issue WorkPlace Tech 5.8.x, 5.9.x, 5.10.x, and 5.11.x Operating System and Microsoft Visio Compatibility Product Line TAC IA Series Environment WorkPlace Tech Tool Software release 5.8.x, 5.9.x, 5.10x, and 5.11.x Microsoft Windows and Microsoft Office Visio requirements, see the "Resolution" section, below. Visio 2010, 2013, 2016, 2019, 2021(.msi install)  Visio 2013, 2016, 2019, 2021 (subscription "Click to Run", Plan 2) Office 2010, 2013, 2016 (.msi install) Office 2013, 2016, 365 (subscription "Click to Run", Plan 2) Support for Workplace Tech 5.10 / previous and Workplace Tech Editor Note: Visio 2019 and Visio 2021 are not supported in 5.9.4 or EBO versions before EBO 2022.  Visio 2019 and Visio 2021 are supported when using Workplace Tech 5.10.x and EBO 2022. Cause What Microsoft Windows operating systems and what versions of Microsoft Visio are compatible with the WorkPlace Tech Tool version 5.8.x, 5.9.x, 5.10.x, and 5.11.x? Resolution Microsoft Windows WorkPlace Tech Tool releases 5.8 through 5.8.6 are certified to run on the following versions of Microsoft Windows: Microsoft Windows XP Professional with Service Pack 2 or Service Pack 3 Microsoft Windows Vista 32-bit Business, Ultimate or Enterprise Microsoft Windows 7 32-bit Professional Microsoft Windows 7 64-bit Professional WorkPlace Tech Tool release 5.8.7 is certified to run on the following versions of Microsoft Windows: Microsoft Windows 7 32-bit Professional Microsoft Windows 7 64-bit Professional Microsoft Windows 8.1 32-bit Pro or Enterprise Microsoft Windows 8.1 64-bit Pro or Enterprise Microsoft Windows Server 2012 64-bit WorkPlace Tech Tool releases 5.9.1 to 5.9.4 are certified to run on the following versions of Microsoft Windows: Microsoft Windows 7   32-bit Professional Microsoft Windows 7   64-bit Professional Microsoft Windows 8.1   32-bit Pro or Enterprise Microsoft Windows 8.1   64-bit Pro or Enterprise Microsoft Windows 10    32-bit Professional Microsoft Windows 10    64-bit Professional Microsoft Windows Server 2012   64-bit WorkPlace Tech Tool release 5.10.0 to 5.10.x is certified to run on the same as WorkPlace Tech 5.9.x and the following versions of Microsoft Windows: Microsoft Windows Server 2016 64-bit Microsoft Windows Server 2019 64-bit Microsoft Windows Server 2022 64-bit Microsoft Windows 11 Professional (Workplace Tech 5.10.4 only) WorkPlace Tech Tool release 5.11.0 is certified to run on the following versions of Microsoft Windows: Microsoft Windows 10 64-bit Professional Microsoft Windows Server 2022 64-bit Microsoft Windows 11 Professional Microsoft Visio Microsoft Windows 7 32-bit Professional Microsoft Windows 7 64-bit Professional Microsoft Windows 8 32-bit Pro or Enterprise Microsoft Windows 8 64-bit Pro or Enterprise Microsoft Windows 8.1 32-bit Pro or Enterprise Microsoft Windows 8.1 64-bit Pro or Enterprise Microsoft Windows Server 2012 64-bit WorkPlace Tech Tool releases 5.8 through 5.8.6 require one of the following versions of Microsoft Visio (32-bit version ONLY) Microsoft Office Visio 2003 with Service Pack 3 (officially supported for WPT 5.8.0, WPT 5.8.1, no known issues with WPT 5.8.2 through 5.8.5) Microsoft Office Visio 2007 with Service Pack 1 or Service Pack 2 Microsoft Office Visio 2010 with or without Service Pack 1 NOTE: Standard or Professional edition of Microsoft Visio may be used. WorkPlace Tech Tool release 5.8.7 requires one of the following versions of Microsoft Visio (32-bit version ONLY) Microsoft Office Visio 2007 with Service Pack 3 Microsoft Office Visio 2010 with Service Pack 2 NOTE: Standard or Professional edition of Microsoft Visio may be used. WorkPlace Tech Tool release 5.9.1 through 5.9.4 requires one of the following versions of Microsoft Visio (32-bit version ONLY) Microsoft Office Visio 2010 with Service Pack 2 Microsoft Office Visio 2013 with Service Pack 1 Microsoft Office Visio 2016 NOTE: Standard or Professional edition of Microsoft Visio may be used. WorkPlace Tech Tool releases 5.10.0 through 5.10.x requires one of the following versions of Microsoft Visio (32-bit version ONLY) Microsoft Office Visio 2016 Microsoft Office Visio 2019 Microsoft Office Visio 2021 Microsoft Office Visio Office 365 Subscription Plans 2 WorkPlace Tech Tool releases 5.11.x requires one of the following versions of Microsoft Visio (64-bit version ONLY) Microsoft Office Visio 2019 64-bit Microsoft Office Visio 2021 64-bit Microsoft Office Visio Office 365 Subscription 64-bit Plans 2 Warning: WorkPlace Tech 5.11 is not compatible with EBO WorkPlace Tech Editor. Do not install WP Tech 5.11 on a PC that has EBO WorkPlace Tech Editor installed. Continue to use WP Tech 5.10 on PCs where EBO WorkPlace Tech Editor is required.   Note: Workplace Tech Tool 5.10.0 and later releases require .NET Framework 4.8 to support Open LDV 5.1 which is included in the installer.  .NET Framework 3.5 Sp1 is no longer required.   Follow the instructions in the article link for the security updates required. Workplace Tech 5.10.x and previous / Workplace Tech Editor (EBO) Microsoft Security Updates required for Visio and Office For the Visio requirements for earlier versions of the WorkPlace Tech Tool software, see What versions of Visio are required for WorkPlace Tech?.
View full article
Picard Product_Support
‎2020-12-15 10:46 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • TAC IA Series
17430 Views

Replacement of Satchwell "AM" series Rotary Actuator by S-E MV15B-230 Linear Actuator due to obsolescence.

Issue Satchwell "AM" series Rotary Actuator requires replacement Environment Satchwell “AM” series Rotary Actuator installed on Satchwell MJF, MZ, MZF, VJF, VSF, VZ or VZF series Plug and Seat Valve Body.   N.B. Where a Satchwell “AM” series Rotary Actuator is installed on a Satchwell VV Butterfly Valve Body then NO simple Actuator replacement is available. In addition to replacing the AMS Actuator it will also be necessary to replace the VV Butterfly Valve Body. The replacement Actuator is S-E type MF type. Please check the latest catalog for current equipment. The Satchwell VV Butterfly Valve Body should be replaced by a S-E Butterfly Valve Body selected from the VF208W series of Butterfly Valve Bodies. It should be noted however that significant pipe work modifications will also be necessary in order to accommodate any selected VF208W series Butterfly Valve Body due to the differing construction of the VF208W Butterfly Valve Body. Please check the latest catalog for current equipment. Cause Obsolescence of Satchwell AM series Rotary Actuator. Resolution Replace Satchwell AM series Rotary Actuator with MV15B-230 Linear Actuator and Linkage Kit :- AM = MV15B-230 + L7SV (880-0126-000) Linkage Kit. N.B. Should the Satchwell AM series Actuator include a wired Auxiliary Switch then the following Auxiliary Switch Pack S2 (880-0469-000) - two independent 250 volt 10 amp (inductive) 3 amp (resistive) rated SPDT Auxiliary End Point Switches - may be purchased separately permitting local installation.   Please check the latest catalog for current equipment.
View full article
Picard Product_Support
‎2018-09-06 01:43 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:07 AM

Labels:
  • Field Devices
17285 Views

Enabling / Disabling the WoW64 optional feature in Windows Server 2008 R2 - R4 (Windows 32-bit on Windows 64-bit)

Issue Even though Windows Server 2008 R2 is exclusively a 64-bit operating system, 32-bit applications are supported by enabling the WoW64 optional feature. NOTE: These are general instructions for utilizing the WoW64 function. Not all Schneider Software will be able to run in an emulated environment. If uncertain, please check with Product Support Services to ensure proper installation. Product Line Andover Continuum, Field Devices, Other, Satchwell MicroNet, Satchwell Sigma, TAC INET, TAC Vista Environment Windows Server 2008 R2 WoW64 feature. All 64bit OS Cause If the WoW64 feature is not enabled and you try to run a 32-bit application, the application will fail to execute. WoW64 option in in undesired state. Resolution If the WoW64 feature is not enabled and you try to run a 32-bit application, the application will fail to execute. The WoW64 execution layer is an optional component that is installed by default on R2 releases. You can save resources by removing the feature if you are not going to be running 32-bit applications on your Server Core install. Install the WoW64 Execution Layer using the following command: dism /online /enable-feature /featurename:ServerCore-WOW64 If your solution has a .NET 32-bit dependency, then also invoke the following sequence: dism /online /enable-feature /featurename:NetFx2-ServerCore dism /online /enable-feature /featurename:NetFx2-ServerCore-WOW64 Note: In Windows Server 2008 R2 RC1, WoW64 is enabled by default. If you don't want WoW64 enabled, just disable the feature as follows:  dism /online /disable-feature /featurename:ServerCore-WOW64
View full article
Picard Product_Support
‎2018-09-06 01:14 PM

Labels:
  • Andover Continuum
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
16974 Views
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore