Tridium N4.11 Upgrade Considerations

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Tridium N4.11 Upgrade Considerations
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
18671 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Tridium N4.11 Upgrade Considerations

Guinan RandyDavis Guinan
‎2022-05-10 11:15 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:54 AM

Issue

Tridium N4.11 Upgrade Considerations 

Product Line

TAC IA Series

Environment

  • I/A Series N4.11 Enterprise Server
  • I/A Series N4.11 Jace 8000

Cause

Detailed information about N4.11 upgrade prerequisites and best practices 

Resolution

The following details a set of upgrade considerations and known issues and their workarounds regarding Niagara 4.11. Please review prior to upgrading to Niagara 4.11.

Niagara 4.11 and Default NRE Memory Changes:
A change to the JACE-8000 file system has been introduced with the release of Niagara 4.11. The RAM disk was used to store alarm and history data. During station save, this data was copied from the RAM disk and zipped up into a single file that was stored on flash. In Niagara 4.11, the RAM disk has been removed entirely. This data is now written directly to the flash memory.
This change has enabled ~384MB of RAM to be freed up to improve performance. Some of the space has been reallocated to code cache, metaspace, and heap space in the 4.11 NRE default settings. Any additional memory space is now available as general free memory. These changes should be transparent to most users and will provide moderate performance improvements on the JACE-8000. Prior to upgrading your JACE-8000, please review NRE default configuration changes and RAM disk removal In 4.11.

Niagara 4.11 and Third-Party Modules
Keeping your Niagara installations safe and secure is our highest priority. In Niagara 4.11, ALL third-party modules must be signed with either a trusted valid certificate or a self-signed certificate to successfully run on a station. This new policy greatly increases the security posture of Niagara installations by making administrators aware of any modules that may have been tampered with, compromised, or derived from untrustworthy sources. Niagara's new signature enforcement feature is being rolled out over multiple Niagara releases. The first iteration was built into release 4.8 to give developers adequate time to make the transition to always signing any third-party modules. Niagara 4.8 produced console and Security Dashboard warnings about unsigned modules but allowed them to run on a station. As of Niagara 4.11, unsigned modules will not execute.
For more information, please review the Niagara documentation on Third-Party Module Signing


Niagara 4.11 Updated Operating Systems, Browsers, and Databases
For the latest information on supported operating systems, please refer to Supported OS and other software in the Niagara 4 Framework Installation Guide.
Tridium remains focused on keeping pace with advancing IT infrastructure to enable more efficient, long-term support of each release version. This policy enhances the security posture of a Niagara installation by ensuring that only the most robust, secure operating systems and enterprise applications are compatible with the framework. The list below provides information on what we will be supporting with Niagara 4.11.

 

OS, Browser, Database Version
Red Hat Enterprise Linux 8.1 (64 bit), 7.7
Ubuntu Linux 20.04 LTS – Desktop & Server
Windows Server 2019 (64 bit), Server 2016 (64 bit), Windows 10 (64 bit)
VMWare ESXi 6.7
Oracle Database 19.3, 18.3, ... 12.2/12.1
MySQL Database 8
MS SQL Database 2019, 2017, 2016
Browsers Chrome, FireFox, Microsoft Edge
Mobile Browsers Safari (iOS 12, 13), Chrome (Android 8, 9, 10)


As with all software products, we must also deprecate support for some operating systems and enterprise applications.  Nevertheless, you can be confident that the above list will handle your needs moving forward.

Using Web Launcher with Niagara 4.11
Web Launcher 21.4.1 was recently revamped for Niagara 4.11 to include essential software dependencies updates along with critical defect fixes. This version of Web Launcher has Java version 8 update 311 and certificate management has been updated to work with Niagara 4.11 along with any legacy or prospective release. Prior to using Web Launcher with Niagara 4.11, customers should update Web Launcher accordingly (see steps below).

How to update Web Launcher?
Web Launcher has a feature to check for updates over the internet and prompts the user when a new version is available in the cloud. However, the existing version of Web Launcher has a bug that prevents a smooth update. Users will be required to perform a fresh install by downloading the latest version from the cloud via the station web Login page. Click on the Niagara Web Launcher Installer link on the station's Web Launcher Web Page, which can be reached via the link on the Login page itself. Once the download is successful, click on the msi file and follow the installation wizard. You do not have to uninstall the older version. The new installation will automatically update to the latest version.

Niagara 4.11 Release Notes:

The release notes for Niagara 4.11 are located here.

Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (1)
  • Find more articles tagged with:
  • RandyDavis22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore