Time Synchronization of the ES and AS

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Time Synchronization of the ES and AS
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
4 Likes
21554 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Time Synchronization of the ES and AS

Picard Product_Support
‎2018-09-10 06:31 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:50 AM

Issue

Trouble synchronizing the time of the Automation Server or Enterprise Server to a NTP server or between each other

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation Enterprise Server
  • EcoStruxure Building Operation Automation Server

Cause

The Enterprise Server and the Automation Server (ASP/ASB) do not synchronize time to each other, they must use an NTP server for synchronization

Resolution

The information below is mainly concerned with synchronizing the time setting but not the actual time.

 

Overview
  • To synchronize the server times an NTP Server will be required, they do not synchronize time with each other. A common misconception is that the Automation Servers sync time with the Enterprise Server via server-to-server communications.
  • To find an external NTP server consult support.ntp.org . Alternatively, an existing internal NTP server can be used or consult Setting up a Local / Internal NTP Server to configure the Enterprise Server computer as a time server
  • The time settings on the Enterprise Server are configured through the operating system settings on the computer where Enterprise Central is installed.  EcoStruxure Building Operation cannot be used to configure the NTP server for the Enterprise Server. Please refer to Network Time on WorkStation, Enterprise Server, and Enterprise Central
  • To find the Network Time Protocol (NTP) configured on a WorkStation, Enterprise Server, or Enterprise Central computer open a command prompt and enter w32tm /query /peers. If configured the peer NTP server(s) will be listed

    1.Modbus.png

  • If you need to ensure an NTP server is actually running on certain IP or DNS address, please reference Ensure IP or DNS address is valid NTP server
  • The time settings on the Automation Servers can only be configured via the Workstation. As per the image they can be configured to look at an NTP server (1) or set manually (2). For synchronization, they must use an NTP Server. Please refer to  Network Time Server on an Automation Server on Webhelp

    2.ASP Time Settings.png

  • Starting in version 1.5, the time adjustment depends on how much the Automation Server drifts from the NTP server. The faster the Automation Server drifts, the more frequently the time is updated.  Please refer to How often will an Automation Server ask the NTP server for the time? 
  • If the time server is a URL, such as time.nist.gov, then it is critical that a Primary DNS is set for each Automation Server, and possibly a Secondary DNS via Device Administrator. Without a DNS, the Automation Server will be unable to resolve the URL to an IP address. Please refer to Configuring the Automation Server IP Address on Webhelp
  • The time displayed for a server in Workstation (Properties -> Basic) will reflect the time zone of the local computer that Workstation is installed on. All events and alarms will be automatically modified to match the time of the workstation that was used to log into the server. The "Server time" will represent the date and time of the server adjusted to client local time zone, while the fields below "Server time" represent the settings of the Automation Server.  

    3. ASP Local Settings.png


How to synchronize date and time settings on multiple Automation Servers

 

IMPORTANT: Only the time settings are synchronized via the Lead/Shadow configuration, the time itself IS NOT synchronized via the Lead/Shadow but rather by all servers synchronizing with the configured timer server.

 

The synchronizing of multiple Automation servers can be achieved with a lead/shadow relationship. The primary and secondary network time server settings for connected shadow Automation servers are defined on the Enterprise server. Setting up the Primary and secondary time servers in the Enterprise Server only passes those configuration settings to the AS controllers, it does not send the actual time and date value.

 

  1. Select the Enterprise server (1), click the Date & Time tab (2), select Enable (3) and enter the Primary time server (4) and, if used, the Secondary time server (5) the Automations Servers will use. Ensutre the time zone for the Enterprise Server is set correctly (6).   Save the settings 

    4. ES NTP Settings.png

  2. From EBO version 2.0 all Automations Servers are automatically configured to shadow the date and time settings configured in the Enterprise Server. To verify this expand the System folder of an Automation Server and select Time Settings -> Date and Time (1). Observe the Date and Time are Shadow-Read only (2), replicating the Enterprise Server settings. Attempting to change any of the settings, other than the Lead object (3), will result in an error. All the Automation Servers will be 'looking' to the same Primary (4) and Secondary time servers, i.e. they will all receive the same time and be synchronized

    5a. Date Time Shadow.png

  3. Similarly, select the Time Zone (1) of the Automation Server in the System Tree; this will also be shadow-read only (2). The lead object is set to the Time Zone on the Enterprise Server (3)

    5b.  Time Zone Shadow.png

  4. Before EBO version 2.0 the Automation Servers were not automatically set to shadow the Enterprise Server settings but this could easily be achieved en masse using Search . In the Search box in the top right corner of the Workstation, type "Date and Time" and click Search (1) to find the date and time object of all connected servers. In the Search view select the servers (2) that require their Date and Time settings synchronized to the Enterprise Server, the Enterprise Server does not need selecting. Select the Time tab (3) and then click the triple dots (4) to navigate to and select the Date and Time object on the Enterprise Server (5)  6. Date Time Search.png
  5. You may need to stop and start the Enterprise server to get the configuration settings to pass down to the shadow Automation servers

Note: To set up synchronization of the time zone settings follow the above search steps for date and time but search on Time Zone


Tip/Tricks

  1. To see the time of on the Enterprise Server and multiple Automation Servers use the Search to find the Date and Time object (1). Individually select each server (2) and then drag the Date and Time object (3) into the Watch Window (4)

    7. Time View Tip.png

  2. It is the Automation Server that initiates the synchronization. To check the Automation Server communication settings select the Automation Server (1) and in the Communication tab (2) select the Enterprise Server (3) and make sure the Automation Server has the correct IP address (4)

    8. AS Comunication Tab.png

  3. To check the Enterprise Server communication settings select the Enterprise Server (1) and in the Communication tab (2) select each Automation Server (3) and make sure the correct IP address is specified for each Automation Server (4). 

    9. ES Communication Tab.png

  4. If a firewall exists ensure that the ports are open so the Automation Server can connect to the Enterprise Server. Please search for the EcoStruxure Building Operation IT Reference Guide on Exchange for details

Further Information Release 1.2.0 and higher

  1. Until the time is set, b3 data will not update in the Watch Window
  2. Until the time is set, BACnet COV will not be functional
  3. Automation Server time does not synchronize directly with the Enterprise Server. Instead, all servers can synchronize to the same accessible time server
  4. To adjust the Automation Server time, time zone, and DST, access to the Automation Server is through a WorkStation
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 7803
  • DavidPurser22
  • DavidShore20
  • GavinHeward22
Was this article helpful? Yes No
85% helpful (11/13)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore