Do not install N4.11 or 4.12 to a JACE-8000 or Edge 10 running 4.10U7 or later

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Do not install N4.11 or 4.12 to a JACE-8000 or Edge 10 running 4.10U7 or later
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
6893 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Do not install N4.11 or 4.12 to a JACE-8000 or Edge 10 running 4.10U7 or later

Guinan RandyDavis Guinan
‎2024-10-15 09:09 AM

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Issue

Upgrading a JACE-8000 or Edge-10 from 4.10U7 to 4.11 or 4.12 will prevent Niagara Daemon from starting.  You will be unable to connect via Workbench or Browser.

Product Line

TAC IA Series

Environment

  • I/A Series N4 Jace 8000
  • Tridium Edge 10

Cause

The software in builds 4.10u7 and later LTS builds (4.10u8, 4.10u9, 4.10u10) was released after 4.11 and 4.12 reached EOL.   4.10u7 contains a newer signing key that is not recognized by 4.11 and 4.12.

Resolution

When upgrading JACE-8000 and/or Edge 10 running 4.10 LTS builds 4.10u7 and later, please skip over 4.11 and 4.12 and instead upgrade to 4.13u3 or newer. Alternatively, you may apply the dist that reverts JACE-8000 to clean 4.9u1 state, or for Edge-10, the dist that reverts it to clean 4.7 state. You can then install 4.11u2 or 4.12u2, if that's the version you have to use. 

  • If you've already attempted the commissioning operation and bricked a device, and have backups, you can connect to the debug port and use the factory reset process per the documentation. 
    • For Edge 10, consult the section titled Factory Default Recovery  in the Niagara Edge 10 Install and Startup Guide. 
    • For JACE-8000, consult the section titled Restoring factory defaults  in the JACE-8000 Backup and Restore Guide.
  • If you are lacking any backups for the host, then before performing the factory reset, you should enable SSH/SFTP via the debug port, and then copy out the Station files using Filezilla or WinSCP or equivalent. 
    • Reach out to your support channel if you have difficulty finding the location of station files. Typically, the files will be in a subfolder of /home/niagara/stations. The config.bog file will be keyring encrypted, and you'll have to reset it using the Bog File Protection Tool. See Editing the .bog file passphrase offline in the Niagara Platform Guide  for details on using the Bog File Protection Tool. 
    • For details on using the debug port on JACE-8000, see Debug port  in the JACE-8000 Install and Startup Guide. 
    • For details on using the debug port on Edge-10, see Connecting to the debug system shell  in the Niagara Edge 10 Install and Startup Guide.
Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (1)
  • Find more articles tagged with:
  • RandyDavis24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of